But I will when I rest up some. So...... go to service call the other day at really old peoples house on the Bayfront. Nice place. Real nice. Problem- lights not working in downstairs office room- there is more than one set of fixtures not working so I start heading for the panel. There was a Cutler Hammer Br 40 circuit single phase load center for the house. When I opened the panel door - holy crap look at all the twins and quadraplex breakers in that thing. Now for starters the old 40 circuit Cuttler Hammer load centers lug only would not accept any twins or quads - full size breakers only so cut that crap out. I count 57 circuit breakers all together. And then after pulling the cover off , there is also maybe 6 double lugged breakers in addition to the twins and quads. I find the breaker in question with no power going thru it right away and pull it out- yep carbon pitted bus stab. Shut off panel power, go to work on stab with a flat file, make it pretty good , put oxiban on it and a new full size single pole and am about to close up and go when I hear fizzle fizzle fizzle sounds , Start checking the quads and find the asshole beat the rejection bars out with a screwdriver and hammer. All the twins and all the quads except for a few that were the replacement non CTL type that clearly state on the lable on the side of the breakers - for replacement only in listed panels. Do not install in newer panel boards made after 1965.

I went back today and put in a sub panel on the adjacent wall, transferred 20 circuits over to it and fed it with #2 ser in flex conduit on an 80 amp breaker. Then I slowly remade the whole crackhead thing work right, while making sure the right neutrals were used with the right hot wires so I wouldn't screw anything up worse than it was to begin with. I hate people that break a circuit breaker just to fit into a panel that don't want a twin or a quad breaker in the first place. Dip shirts. rant over.
__________________
Thought for the Day: President Trump is the first sitting U.S. president to EVER step foot in North Korea... Obama got a Nobel Peace Prize for being black.
macmikeman is online now   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 09-12-2018, 02:52 AM   #2
Can't sign em..forget em
 
lighterup's Avatar
 
Join Date: Jun 2013
Location: Ohio
Posts: 7,361
Rewards Points: 10,046
Default

The guy must not have had a rotozip
99cents likes this.
lighterup is offline   Reply With Quote
Old 09-12-2018, 06:42 AM   #3
Petulant Amateur
 
99cents's Avatar
 
Join Date: Aug 2012
Location: Perky Nipples, Canada
Posts: 20,280
Rewards Points: 10,925
Default

I think I know how you feel, mac. I would be happy that I made things pretty and safe for the customer but the guy who did that, I would want to put his ballz in a vice and run over his head with my monster van. It pi$$es me off bad.
tmessner likes this.
99cents is online now   Reply With Quote
Sponsored Links
Advertisement
 
Old 09-12-2018, 07:32 AM   #4
animal lover /rat bastard
 
wildleg's Avatar
 
Join Date: Apr 2009
Location: somewhere in FL
Posts: 13,519
Rewards Points: 982
Default

yeah, but did you get paid ?

BTW, I thought you only worked 5 hrs a day so you could either surf or watch hula girls ? what gives ?
__________________
this message was sent from a dental floss farm using ZappaTalk and a pair of zirconium encrusted tweasers
wildleg is offline   Reply With Quote
Old 09-12-2018, 07:33 AM   #5
86 45 20
 
Southeast Power's Avatar
 
Join Date: Jan 2009
Location: Florida
Posts: 17,515
Rewards Points: 7,698
Default

Nice save.
Im thinking I would have done a gut swap on the original loadcenter and also add an additional loadcenter the way you did.
samgregger likes this.
Southeast Power is online now   Reply With Quote
Old 09-12-2018, 08:12 AM   #6
Petulant Amateur
 
99cents's Avatar
 
Join Date: Aug 2012
Location: Perky Nipples, Canada
Posts: 20,280
Rewards Points: 10,925
Default

Quote:
Originally Posted by wildleg View Post
yeah, but did you get paid ?

BTW, I thought you only worked 5 hrs a day so you could either surf or watch hula girls ? what gives ?
Mac always gets paid. His van is actually an armored car .
99cents is online now   Reply With Quote
Old 09-12-2018, 08:27 AM   #7
Senior Member
 
HackWork's Avatar
 
Join Date: Oct 2009
Location: -
Posts: 32,098
Rewards Points: 1,339
Default

I don't know why people always try to jam more breakers into a panel.

Just combine circuits. Most of those 57 circuits will never see more than 5 amps, and definitely not at the same time as another random circuit.

If the main can handle the load, then 40 breakers is MORE than enough to spread that load out across.
HackWork is online now   Reply With Quote
The Following User Says Thank You to HackWork For This Useful Post:
TGGT (09-12-2018)
Old 09-12-2018, 11:15 AM   #8
Senile Member
 
macmikeman's Avatar
 
Join Date: Jan 2007
Location: Honolulu
Posts: 26,498
Rewards Points: 15,343
Default

Quote:
Originally Posted by HackWork View Post
I don't know why people always try to jam more breakers into a panel.

Just combine circuits. Most of those 57 circuits will never see more than 5 amps, and definitely not at the same time as another random circuit.

If the main can handle the load, then 40 breakers is MORE than enough to spread that load out across.
I think we have two culprits. Well three. First and least guilty is the original installer. Filled the 40 up no spaces free. Second and now bad guy is the pv pirates showed up and needed a 2 pole pv main so out comes the screwdriver to break some rejection tabs out , or maybe he was the double lugger which is nothing more than a technical violation in my book. The really big bad naughty came when they decided to put in split ac's for the whole place. I lost count of how many compressors, but there is at least six of them. The electrician (loosely termed I might add, but they are licensed....) that installed the wiring could have easily used Hax"s method to put in a main for a ac panel right where I put my new one and fed all the ac loads off of that. He's the guy I'd like to run over with my van. I didn't even finish after ten hours on that thing, but the proposal was for 2,500 dollars to make this repairs so off I go in an hour or so to complete. That ten hours was double hard cause the old man turns on CNN on the nearby tv and turns it up loud and sits in front of it the whole ten hours I was there.
My head almost exploded . It's going to take me a few more hours to finish, there is no labels on that are reliable on any of the breakers for the most part so I get to hunt and peck now. Ten hours standing in one spot is a lot for a geezer like me.
__________________
Thought for the Day: President Trump is the first sitting U.S. president to EVER step foot in North Korea... Obama got a Nobel Peace Prize for being black.
macmikeman is online now   Reply With Quote
Old 09-12-2018, 08:55 PM   #9
Magic Smoke Remover
 
Join Date: Aug 2011
Location: Oklahoma
Posts: 1,004
Rewards Points: 1,966
Default

OK first of all, the non CTL thing... They obviously know we are using them in panels that are full. How many pre-'65 panelboards are there that they need sleeves and sleeves of non-CTL breakers at Lowe's.

Eaton tech line even told me they don't care anymore since they 42 rule went away, I asked how to determine max circuits since they used to be BR3040B200 and now are just labeled at BR30B200 or similar.

Secondly, do guys not carry breakers without rejection tabs on the trucks? They even make them in quads. Why bother keeping both?
matt1124 is offline   Reply With Quote
Old 09-12-2018, 09:01 PM   #10
Can't sign em..forget em
 
lighterup's Avatar
 
Join Date: Jun 2013
Location: Ohio
Posts: 7,361
Rewards Points: 10,046
Default

Quote:
Originally Posted by macmikeman View Post
I think we have two culprits. Well three. First and least guilty is the original installer. Filled the 40 up no spaces free. Second and now bad guy is the pv pirates showed up and needed a 2 pole pv main so out comes the screwdriver to break some rejection tabs out , or maybe he was the double lugger which is nothing more than a technical violation in my book. The really big bad naughty came when they decided to put in split ac's for the whole place. I lost count of how many compressors, but there is at least six of them. The electrician (loosely termed I might add, but they are licensed....) that installed the wiring could have easily used Hax"s method to put in a main for a ac panel right where I put my new one and fed all the ac loads off of that. He's the guy I'd like to run over with my van. I didn't even finish after ten hours on that thing, but the proposal was for 2,500 dollars to make this repairs so off I go in an hour or so to complete. That ten hours was double hard cause the old man turns on CNN on the nearby tv and turns it up loud and sits in front of it the whole ten hours I was there.
My head almost exploded . It's going to take me a few more hours to finish, there is no labels on that are reliable on any of the breakers for the most part so I get to hunt and peck now. Ten hours standing in one spot is a lot for a geezer like me.

You are in the Land of Goshen my friend...
Surrounded on all sides by the Philistines...
You have my moral support.
lighterup is offline   Reply With Quote
Old 09-12-2018, 09:04 PM   #11
Can't sign em..forget em
 
lighterup's Avatar
 
Join Date: Jun 2013
Location: Ohio
Posts: 7,361
Rewards Points: 10,046
Default

Quote:
Originally Posted by matt1124 View Post
OK first of all, the non CTL thing... They obviously know we are using them in panels that are full. How many pre-'65 panelboards are there that they need sleeves and sleeves of non-CTL breakers at Lowe's.

Eaton tech line even told me they don't care anymore since they 42 rule went away, I asked how to determine max circuits since they used to be BR3040B200 and now are just labeled at BR30B200 or similar.

Secondly, do guys not carry breakers without rejection tabs on the trucks? They even make them in quads. Why bother keeping both?
Eaton Br is now selling 40-54 space main breaker 200 amp panels
(single phase). I believe damn near all the busses are mini rated now.
(well not quite all , but you get my point)
lighterup is offline   Reply With Quote
Old 09-12-2018, 10:26 PM   #12
Senior Member
 
Jlarson's Avatar
 
Join Date: Jun 2009
Location: AZ
Posts: 14,105
Rewards Points: 3,906
Default

Only 10 hours? eh that's a regular day for me.







Quote:
Originally Posted by HackWork View Post
I don't know why people always try to jam more breakers into a panel.

Just combine circuits. Most of those 57 circuits will never see more than 5 amps, and definitely not at the same time as another random circuit.

If the main can handle the load, then 40 breakers is MORE than enough to spread that load out across.

Yep, have wirenuts, will pigtail.
frenchelectrican and HackWork like this.
__________________
Everything has user serviceable parts inside.
Jlarson is offline   Reply With Quote
Old 09-12-2018, 10:45 PM   #13
Senior Member
 
Join Date: Mar 2010
Location: NH
Posts: 571
Rewards Points: 1,079
Default

My new go to panel for new construction is a siemens 40/80 mcb panel. Full length neutral bars, 80 circuits and almost the same price as a 40.

https://www.amazon.com/Siemens-S4080.../dp/B01BD87I98
JoeSparky is offline   Reply With Quote
Old 09-12-2018, 10:58 PM   #14
Magic Smoke Remover
 
Join Date: Aug 2011
Location: Oklahoma
Posts: 1,004
Rewards Points: 1,966
Default

I hate when they are jammed up like that. Small house gets CH22B100, Medium CH42B200, bigger gets a 320 amp can and 2x Eaton CH42B200. No tandems. Subs from there as required.

There's no need for this 42/84 baloney. The gutters are so packed you can't do anything and sometimes you have to leave the middle screws out or they'll short out.
macmikeman likes this.
matt1124 is offline   Reply With Quote
Old 09-12-2018, 11:08 PM   #15
Senior Member
 
360max's Avatar
 
Join Date: Jun 2011
Location: NY
Posts: 11,433
Rewards Points: 1,234
Default

Quote:
Originally Posted by macmikeman View Post
Quote:
Originally Posted by HackWork View Post
I don't know why people always try to jam more breakers into a panel.

Just combine circuits. Most of those 57 circuits will never see more than 5 amps, and definitely not at the same time as another random circuit.

If the main can handle the load, then 40 breakers is MORE than enough to spread that load out across.
I think we have two culprits. Well three. First and least guilty is the original installer. Filled the 40 up no spaces free. Second and now bad guy is the pv pirates showed up and needed a 2 pole pv main so out comes the screwdriver to break some rejection tabs out , or maybe he was the double lugger which is nothing more than a technical violation in my book. The really big bad naughty came when they decided to put in split ac's for the whole place. I lost count of how many compressors, but there is at least six of them. The electrician (loosely termed I might add, but they are licensed....) that installed the wiring could have easily used Hax"s method to put in a main for a ac panel right where I put my new one and fed all the ac loads off of that. He's the guy I'd like to run over with my van. I didn't even finish after ten hours on that thing, but the proposal was for 2,500 dollars to make this repairs so off I go in an hour or so to complete. That ten hours was double hard cause the old man turns on CNN on the nearby tv and turns it up loud and sits in front of it the whole ten hours I was there.
My head almost exploded . It's going to take me a few more hours to finish, there is no labels on that are reliable on any of the breakers for the most part so I get to hunt and peck now. Ten hours standing in one spot is a lot for a geezer like me.
i spit my coffee out over the old man watching CNN for the 10 hours and you had to listen
99cents likes this.
360max is offline   Reply With Quote
Old 09-13-2018, 05:22 AM   #16
Senior Member
 
HackWork's Avatar
 
Join Date: Oct 2009
Location: -
Posts: 32,098
Rewards Points: 1,339
Default

Quote:
Originally Posted by matt1124 View Post
OK first of all, the non CTL thing... They obviously know we are using them in panels that are full. How many pre-'65 panelboards are there that they need sleeves and sleeves of non-CTL breakers at Lowe's.

Eaton tech line even told me they don't care anymore since they 42 rule went away, I asked how to determine max circuits since they used to be BR3040B200 and now are just labeled at BR30B200 or similar.

Secondly, do guys not carry breakers without rejection tabs on the trucks? They even make them in quads. Why bother keeping both?
I carry both because the price is significantly higher in many brands. Why throw out profit?

As far as being allowed to use them, from a code standpoint that won’t work. You will not be able to get what the guy on the phone told you certified in writing. If a panel says 42 circuits max, that’s what we have to go by even if it was compelled by the code at the time which has changed.

Last edited by HackWork; 09-13-2018 at 05:29 AM.
HackWork is online now   Reply With Quote
Old 09-13-2018, 05:26 AM   #17
Senior Member
 
HackWork's Avatar
 
Join Date: Oct 2009
Location: -
Posts: 32,098
Rewards Points: 1,339
Default

Quote:
Originally Posted by matt1124 View Post
I hate when they are jammed up like that. Small house gets CH22B100, Medium CH42B200, bigger gets a 320 amp can and 2x Eaton CH42B200. No tandems. Subs from there as required.

There's no need for this 42/84 baloney. The gutters are so packed you can't do anything and sometimes you have to leave the middle screws out or they'll short out.
I agree. I think 40 circuits in a panel is too much, I definitely donít want more than that. I would rather split 40 circuits up into 2 30 space panels.
frenchelectrican likes this.
HackWork is online now   Reply With Quote
Old 09-13-2018, 09:57 AM   #18
Magic Smoke Remover
 
Join Date: Aug 2011
Location: Oklahoma
Posts: 1,004
Rewards Points: 1,966
Default

Quote:
Originally Posted by HackWork View Post
I carry both because the price is significantly higher in many brands. Why throw out profit?

As far as being allowed to use them, from a code standpoint that won’t work. You will not be able to get what the guy on the phone told you certified in writing. If a panel says 42 circuits max, that’s what we have to go by even if it was compelled by the code at the time which has changed.
You're probably right but I just don't carry both, someone buying one or two breakers at $10 more each probably isn't going to be a big deal, vs being out of those without rejection clips because I didn't pay close attention to what needed refilled on the truck.

I know I'd never see it in writing, and looks like the BR series still has a circuit limit, but the CH is sold as "number of poles" instead of "number of circuits" without a circuit number spec, that's why I called them.
matt1124 is offline   Reply With Quote
Old 09-13-2018, 11:06 AM   #19
Senior Member
 
HackWork's Avatar
 
Join Date: Oct 2009
Location: -
Posts: 32,098
Rewards Points: 1,339
Default

Quote:
Originally Posted by matt1124 View Post
You're probably right but I just don't carry both, someone buying one or two breakers at $10 more each probably isn't going to be a big deal, vs being out of those without rejection clips because I didn't pay close attention to what needed refilled on the truck.
You would bend over to pickup a $10 bill, right? Writing "CTL" or "non-CTL" next to the breaker brand and size on your material list is far less work.

A lot of the times that I use tandems it is to make room for a 2-pole breaker, so 2 non-cheater tandems saves me $20-30.

Quote:
I know I'd never see it in writing, and looks like the BR series still has a circuit limit, but the CH is sold as "number of poles" instead of "number of circuits" without a circuit number spec, that's why I called them.
I haven't seen that, but I never specifically looked. However, even if the panel doesn't specify a maximum number of circuits somewhere on the label, those breakers still specify that they aren't to be used.

I am not saying that I wouldn't do it, I am just saying that if you are getting inspected that it might not pass if the inspector looks at that.
HackWork is online now   Reply With Quote
Old 09-13-2018, 11:39 AM   #20
Senior Member
 
Join Date: Apr 2013
Location: rural mn
Posts: 368
Rewards Points: 744
Default

Quote:
Originally Posted by macmikeman View Post
I think we have two culprits. Well three. First and least guilty is the original installer. Filled the 40 up no spaces free. Second and now bad guy is the pv pirates showed up and needed a 2 pole pv main so out comes the screwdriver to break some rejection tabs out , or maybe he was the double lugger which is nothing more than a technical violation in my book. The really big bad naughty came when they decided to put in split ac's for the whole place. I lost count of how many compressors, but there is at least six of them. The electrician (loosely termed I might add, but they are licensed....) that installed the wiring could have easily used Hax"s method to put in a main for a ac panel right where I put my new one and fed all the ac loads off of that. He's the guy I'd like to run over with my van. I didn't even finish after ten hours on that thing, but the proposal was for 2,500 dollars to make this repairs so off I go in an hour or so to complete. That ten hours was double hard cause the old man turns on CNN on the nearby tv and turns it up loud and sits in front of it the whole ten hours I was there.
My head almost exploded . It's going to take me a few more hours to finish, there is no labels on that are reliable on any of the breakers for the most part so I get to hunt and peck now. Ten hours standing in one spot is a lot for a geezer like me.
I have been known to have to "work on that circuit for an extended period of time" to control the heat as the the old man may want it at 76 in the winter and i have on long johns.
tmessner is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
14 hours on site bending and strapping macmikeman Off Topic (Non Trade) 23 09-02-2016 12:18 PM
Pros and cons of this site! Borgi Off Topic (Non Trade) 58 07-17-2016 12:10 AM
Guidelines For Referencing Articles From Another Site Cricket Getting Started With Electrician Talk 0 04-27-2016 09:43 AM
Reporting A Post Cricket Getting Started With Electrician Talk 0 07-25-2014 11:27 AM


All times are GMT -4. The time now is 07:15 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com