How much overloading we can do 167KVA,4.8KV/240V 1-phase transformer.
I seen that in town homes utilities feds twelve 100A services from only 50kVA transformer. Which is way bigger than it's capacity. Do anyone have idea how much capacity or services we can fed from 167kVA transformer.
hiren.munjani1994 is offline   Reply With Quote
Old 03-26-2019, 05:40 PM   #2
Rewards Points: 21,898
It depending on if customer own that or POCO own that if the POCO own that and they are typically oil cooled unit and they can handle a bit of overloading before it get overheat on tempture rise.
but to know the actual number that you need to look at the nameplate on the transformer and concant the manufacter they will have the info what you are looking for.
Old 03-26-2019, 10:37 PM   #3
Rewards Points: 718
well if i calculated it right its rated for 695 amps @240 volts.how much overload is a good question. but 695 amps is an awful lot!
circuitman1 is offline   Reply With Quote
Old 03-27-2019, 01:11 AM   #4
Rewards Points: 8,273
When it starts smoking, you've hit the limit. Why would you want to overload a transformer? That isn't a safe practice, and wastes energy.
Bird dog likes this.
joebanana is online now   Reply With Quote
Old 03-27-2019, 08:36 AM   #5
Light Bender
eddy current's Avatar
Rewards Points: 8,168
50 kVA seems small but 167kVA is pretty normal.
What are the chances that all twelve of those services use more than 60 amps all at the same time?
brian john and glen1971 like this.
Old 03-27-2019, 09:38 AM   #6
just the cowboy's Avatar
Rewards Points: 822
POCO do what they want to their own codes, so you can't compare what they do.
Are you talking short term overload like starting a motor?
"DID THIS FIX IT??"
Old 03-27-2019, 09:46 AM   #7
Rewards Points: 3,816
Utilities look at the chances (as noted above) that all these services are running at capacity. Fact is none of them will ever run at full capacity. Even in an all-electric house, it is rare to never that the water heater, furnace, stove with all the burners and all the lighting load will be at full load and that the number of houses served are in the same operational mode of 100% loaded.
This is not the utility's first job, this is based on years and years of data and if anything is happening it is loads in a typical residence are lower than in years past.
Old 03-27-2019, 01:22 PM   #8
Bird dog's Avatar
Rewards Points: 862
Years ago an engineer told me they'd rather send out a truck to change a fuse than change a xfmr.