Transformers - Electrician Talk - Professional Electrical Contractors Forum
Like Tree5Likes
  • 2 Post By varmit
  • 3 Post By brian john
Old 03-02-2019, 01:40 AM   #1
Default Transformers
I recently found out on a transformer even one you mount in a box? 347 to 120 you need to ground one leg of the 120 volt side. Can someone explain?
Bigbilly is offline   Reply With Quote
Old 03-02-2019, 05:46 AM   #2
CoolWill's Avatar
Rewards Points: 2,012
So that there is a complete circuit path for current to flow if there is a ground fault downstream.
I'm With Her! Hillary 2016
Old 03-02-2019, 07:33 AM   #3
Rewards Points: 1,574
The transformer secondary needs the "neutral" grounded so the over current protection will work on a short to ground on the "hot" secondary conductor(s).
Grounding the "neutral" also makes searching for problems much easier, as you can check voltage, from the energized conductors, to any available ground.
Old 03-02-2019, 09:30 AM   #4
Rewards Points: 7,520
Assuming your in Canada with the 347 volts, yes you must ground the secondary. Even if the secondary is lower than 50 volts, if the primary is over 150 volts to ground you must ground it.
Old 03-02-2019, 09:35 AM   #5
Rewards Points: 1,486
a grounded conductor (most often the neutral) so the over current protection will work on a short to ground on the "hot" secondary conductor(s).
Grounding a conductor also makes searching for problems much easier, as you can check voltage, from the energized conductors to any available ground.
Fixed it for you.
glen1971, telsa and MCasey like this.
Old 03-02-2019, 02:37 PM   #6
Rewards Points: 25,612
Electric circuit 600Y347 (primary windings )
Magnetic circuit ( the flux inside the three-phase transformer )
Electric circuit 208Y120 (secondary windings )
Until you've grounded the secondary winding circuit it is ELECTRICALLY isolated -- via the magnetic circuit. Re-stated, it has no point of reference. This means that -- until it's grounded -- the secondary is an un-grounded system.
Check out the threads on un-grounded Services. They are 'floaters.'
( 600 3-phase or 480 3-phase -- it makes little difference diagnostically. )
Review post #5.
Old 03-02-2019, 08:24 PM   #7
Rewards Points: 2,744
Welcome to Electrician Talk.
Please take a few minutes and fill out your profile.
Old 03-02-2019, 09:13 PM   #8
Fixed it for you.
Old habits are difficult to change.
Old 03-02-2019, 09:34 PM   #9
Bird dog's Avatar
Rewards Points: 1,324
Does the CEC differentiate between a grounded & a grounding conductor?
Old 03-02-2019, 09:52 PM   #10
Yes.
Old 03-04-2019, 12:47 PM   #11
Rewards Points: 1,990
good to know i've seen some 600--24v xfmer install and the 24v was floating
Old 03-04-2019, 01:14 PM   #12
Also, depending on the voltage and va, you might have to fuse the secondary.
16-104 for class 1 transformers
16-200 for class 2
How to plan for Pad Mounted Transformers boot Services and Service Equipment 21 08-20-2017 01:01 PM
3-Phase transformers (bonding & distribution) meggerman Canadian Electrical Forum 3 01-25-2017 12:04 AM
Grounding of transformers skachur Commercial Electrical Forum 3 01-12-2017 11:07 PM
Isolation Transformers/ Auto-Transformers DerekS General Electrical Discussion 10 12-21-2016 03:37 PM
Three Phase Transformers - Primary/Secondary Calculations JasonCo General Electrical Discussion 33 03-08-2016 09:55 PM