The other day we lost power in one of the building we work the main breaker trip in switchgear we have a specialist. The guy came open the rest of breakers crank a handle in the switchgear push a button the switchgear came back on and close all breaker again. My question is is there a specific training about switchgear out there?
Morales95 is offline   Reply With Quote
Old 01-15-2015, 05:46 PM   #2
butcher733's Avatar
Rewards Points: 798
That hurts to read.
I'll take therapists for $400.
butcher733 is offline   Reply With Quote
The Following 6 Users Say Thank You to butcher733 For This Useful Post:
amigi968 (01-17-2015), BuzzKill (01-15-2015), glen1971 (01-15-2015), meadow (01-15-2015), Moonshot180 (02-03-2015), Sparky J (01-17-2015)
Old 01-15-2015, 05:49 PM   #3
Rewards Points: 1,464
First,did he suit up with the correct level of P.P.E.?
Next, did he determine why the main tripped?
And why were you there watching?
To me, some specialist...
The Following 7 Users Say Thank You to bobelectric For This Useful Post:
Bad Electrician (01-15-2015), dronai (01-15-2015), glen1971 (01-15-2015), guest (01-18-2015), meadow (01-15-2015), Sparky J (01-17-2015), The_Modifier (01-16-2015)
Old 01-15-2015, 06:17 PM   #4
Experience Member
Rewards Points: 26
We both suit up arc flash suit 40 cal/cm2 we deal with panel and transformers and for switchgear they call other company
Old 01-15-2015, 06:42 PM   #5
Anytime that goes down, 1 dude is the hero, the other waits outside the zone , Justin Case. You need more 70 E training.
Old 01-15-2015, 06:46 PM   #6
Rewards Points: 684
Originally Posted by Morales95 View Post
... My question is is there a specific training about switchgear out there?
Yes there is, it's called "becoming a licensed electrician" available in all states through a process of apprenticeship and extensive experience working with a qualified Journeyman electrician.
Seriously, walking in and re-closing a tripped main breaker is not a special skill, and in fact is really dangerous and exhibits poor judgement on the part of your technician. Breakers never trip without reason. When the MAIN breaker in a large piece of switchgear trips (I know it is large, because you said it has a crank handle), there was/is some kind of very serious situation somewhere down stream, and the main breaker breaker tripped as a latch ditch effort to prevent it from becoming a fire. Re-closing it without finding the cause is not the first course of action, that is just inviting more trouble, SERIOUS trouble.
IBTL
Is it weird how saying sentences backwards creates backwards sentences saying how weird it is?
The Following 7 Users Say Thank You to JRaef For This Useful Post:
51360 (01-16-2015), BuzzKill (01-15-2015), glen1971 (01-15-2015), guest (01-18-2015), Moonshot180 (02-03-2015), Rollie73 (01-17-2015), The_Modifier (01-16-2015)
Old 01-15-2015, 06:58 PM   #7
Experience Member
Rewards Points: 26
Jajaja I have 10 years in the field 4 of those apprenticeship I never had to deal with a trip breaker in a switchgear. I install them and we have a guy do the splicing but I would like to get that knowledge
Old 01-15-2015, 07:39 PM   #8
dronai's Avatar
Rewards Points: 441
I had to hold my breath through that whole paragraph
Old 01-15-2015, 07:41 PM   #9
Experience Member
Rewards Points: 26
Originally Posted by dronai View Post
I had to hold my breath through that whole paragraph, because there are no commas, and only one period.
Actually two periods
The Following User Says Thank You to Morales95 For This Useful Post:
dronai (01-15-2015)
Old 01-15-2015, 07:44 PM   #10
dronai's Avatar
Rewards Points: 441
Are you in maintenance, or construction ?
Old 01-15-2015, 07:48 PM   #11
A crank handle tells me it's 480 switchgear and why would you rack it out and in again to reset it?
Old 01-15-2015, 07:50 PM   #12
Experience Member
Rewards Points: 26
I'm a maintenance electrician now my first 6 construction
Old 01-15-2015, 08:06 PM   #13
Experience Member
Rewards Points: 26
I didn't do anything; my instructions were wait for the guy who deals with switchgear, and make sure the power is back
Old 01-15-2015, 08:11 PM   #14
Rewards Points: 4,138
It may not have had to be racked out and back in.. I work on a couple of older FPE 800 amp breakers that need the handle to recharge the spring, if the charging motor quits working... Then the other end of the ratchet handle has a pin that is inserted to close the breaker. If memory serves there is also a pushbutton, but if the charging motor isn't working, OR if there is another reason electrically it won't operate...
As stated above it is VERY foolish to close a tripped MAIN breaker without first finding out why it tripped...
guest (01-18-2015)
Old 01-15-2015, 08:16 PM   #15
Experience Member
Rewards Points: 26
I agree with you with the foolish part. The next day I did my report but the boss didn't explain why we have to turned back on.
Old 01-15-2015, 08:21 PM   #16
Very Long Vacation
Rewards Points: 5,262
If this tripped because of GFP not set correctly when a fault occurred on a 20amp branch circuit I guess its none to bad. But if that breaker is closing into a bolted fault within the gear itself or anywhere else for that matter be prepared to have regrets.
Even at the 120/240 branch circuit level a megger is a good idea before reengaging something.
guest (01-18-2015)
Old 01-15-2015, 11:53 PM   #17
EB Electric's Avatar
Rewards Points: 268
I don't mean to bust your balls, but how do you gather the system voltage is 480 from the description of a crank handle? Maybe in one plant that is the setup, but that is no way to identify system voltage. Nothing saying the breaker was racked in or out, the original poster doesn't make it very clear, but I would bet more likely the guy charged the closing spring on the breaker.
"If a man made it, a man can fix it"
EB Electric is offline   Reply With Quote
The Following User Says Thank You to EB Electric For This Useful Post:
Old 01-16-2015, 12:37 AM   #18
More than lead and elbows
JW Splicer's Avatar
Rewards Points: 1,130
Sounds like it might be at least 4160V considering someone has to "splice" cable? Anyway, AVO, and a few others offer some good courses on medium voltage distribution which includes switchgear work, also Zog can probably get you what you want. Contact the manufacturer as well and ask for a rep to give you a maintenance course...
JW Splicer is offline   Reply With Quote
Old 01-16-2015, 04:24 AM   #19
Dig it, EB. All the switchgear I dealt with to recharge for a reset, you pumped the handle to recharge the springs if necessary. The crank was for removing the breaker. Maybe that's older than me. Plus, a lot of places I went to, the breaker had a rachet cable on a trolley support to the breaker when you racked it open. Most of these went home to someones garage.
Old 01-16-2015, 11:31 AM   #20
Zog
Zog's Avatar
Rewards Points: 1,096
And a direct violation of OSHA
1910.334 (b)(2) "Reclosing circuits after protective device operation." After a circuit is deenergized by a circuit protective device, the circuit protective device, the circuit may not be manually reenergized until it has been determined that the equipment and circuit can be safely energized. The repetitive manual reclosing of circuit breakers or reenergizing circuits through replaced fuses is prohibited.
Note: When it can be determined from the design of the circuit and the overcurrent devices involved that the automatic operation of a device was caused by an overload rather than a fault condition, no examination of the circuit or connected equipment is needed before the circuit is reenergized.
No trees were killed in the sending of this message, but a large number of electrons were terribly inconvenienced.
The Following User Says Thank You to Zog For This Useful Post:
guest (01-18-2015)
Magnetic trip breaker martindag General Electrical Discussion 7 06-20-2014 06:41 PM
What happens when a breaker goes trip free Lone Crapshooter Commercial Electrical Forum 14 12-17-2013 09:24 AM
Circuit breaker will not trip harlymang General Electrical Discussion 22 04-11-2013 10:56 PM
Why didn't breaker trip? knothole General Electrical Discussion 63 12-13-2011 10:58 PM
shunt trip breaker spider General Electrical Discussion 26 04-06-2011 12:44 PM