I have two 208V appliances in a restaurant (recent build) on 30 amp breakers. Both breakers tripped a couple of times over the last couple of weeks. Yesterday they tripped five times.
I am getting 22.5 amps on each with a clamp meter. I have been here for an hour and nothing has changed. What now, gurus?
Old 04-25-2019, 09:14 AM   #2
Rewards Points: 427
More info needed.
What are the appliances?
Did you check to make sure that there are no bastard splices between the two circuits?
Both breakers trip together every time?
When the breakers trip, are both appliances always running?
Old 04-25-2019, 09:22 AM   #3
More info needed.
Shawarmas.
They will trip independently.
Both are running at the same time when tripping occurs.
Old 04-25-2019, 09:26 AM   #4
Rewards Points: 880
Just a hunch, but both those breakers were bought at the same time and same place, could be a batch of defective breakers and lucky you, you got em IDK. I check easy first.
J F Go is offline   Reply With Quote
Old 04-25-2019, 09:36 AM   #5
Could be a breaker issue. There was a dummy (me) who shorted them out during finishing. Maybe weakened the breakers?
stiffneck likes this.
Old 04-25-2019, 09:41 AM   #6
Rewards Points: 427
Shorted both breakers out? How did you do that?
And yeah, replacing breakers is a good idea in these situations, especially after you had an issue with them.
Old 04-25-2019, 09:42 AM   #7
Vacated
Wiresmith's Avatar
Rewards Points: 2,844
are the breakers side by side? if so it could be the ambient temp at the breakers. whats your measured voltage?
sbrn33 and samgregger like this.
Think like a man of action, act like a man of thought. ~Henri Louis Bergson
Old 04-25-2019, 09:53 AM   #8
Fast track job, working nights, things happen.
Old 04-25-2019, 09:55 AM   #9
Not side by side, voltage is good.
Breakers are warm to the touch compared to the others.
Old 04-25-2019, 10:11 AM   #10
wcord's Avatar
Rewards Points: 1,524
IF, i were to short out a breaker, I wouldn't short across the phases. Only short 1 phase to ground.
Like i said, IF lol
bill39 and 99cents like this.
Old 04-25-2019, 10:13 AM   #11
Rewards Points: 1,574
At a 22.5 amp continuos load, on a 30 amp breaker, the breakers will probably be a little warm. Do you have a amp meter with peak capture? If everything else is working fine, the two options are the equipment is defective or the breakers trip is off a little.
Do a "fall of potential test" across the breakers to see if one or more poles has a higher resistance than the other. I would be concerned if the FOP test showed more than a 50 milivolt reading.
Probably replace the breakers and see if anything changes. If not, probably an equipment problem.
Also, do the FOP test between the panel incoming line terminals and the problem breakers load terminals. This would verify the panel buss connections and the breaker contacts.
acro and 99cents like this.
Old 04-25-2019, 11:22 AM   #12
Bird dog's Avatar
Rewards Points: 1,338
Shawarmas.
So, same manufacturer? Any way to find out if this equipment causes these problems? Is this new equipment? Are they hardwired? If not what do the plug & receptacle look like?
Old 04-25-2019, 12:04 PM   #13
Rewards Points: 68
Any chance that the 2 sets of wires got mixed (same pipe same colors)???
tmessner and sparkiez like this.
AU Facilities is offline   Reply With Quote
Old 04-25-2019, 12:09 PM   #14
Vacated
Wiresmith's Avatar
are they cutting meat and in turn loading the motor when it trips?
Old 04-25-2019, 12:12 PM   #15
canbug's Avatar
Rewards Points: 1,510
What's your incoming voltage when the Donair place is hopping. Could the voltage be dropping just enough to raise the current close to the trip level?
Tim.
samgregger likes this.
Old 04-25-2019, 12:21 PM   #16
Possible but unlikely. I will verify before I go back with the new breakers.
Used machines with factory cords (maybe). Normal 30 amp dryer receptacle.
One tripped just before I left so nobody was cutting meat at the time.
Old 04-25-2019, 02:39 PM   #17
Rewards Points: 44
Just a hunch, so it’s a commercial kitchen, cord and plug.
Maybe not a current issue, assuming they are gfi as required by code, my bet is it’s in the equipment,and it’s tripping out on the GFCI function. probably from moisture from cleaning or steam from cooking.
FF301 is offline   Reply With Quote
Old 04-25-2019, 02:56 PM   #18
Rewards Points: 1,514
That’s a good thought. The receptacle box might be filled up w/water or goo is built up btw plug blades, etc.
Old 04-25-2019, 03:13 PM   #19
Rewards Points: 1,494
As noted do an FOP
This load is resistive with a motor after start up the current should be fairly constant
Tt 22.5 amps you are close to the magic number of 24 WHICH might put you close to the longtime trip.
Not tripping now because the cover is off?
Put a cover on and put a fan in front of them see what happens
OR replace the CB's
Old 04-25-2019, 03:22 PM   #20
MikeFL's Avatar
Rewards Points: 2,694
I've seen thermal magnetic breakers trip after a restive load runs for a while because the load is approaching the threshold and the breaker warms up, eventually opening. If you have a means to monitor the temperature of that breaker as the load is started and as it continues until it trips, that may give you some indication.
Maybe lift the breaker and make sure it's seating on the bus well.
Old grease saturated junk like is common in an old restaurant? Or is this new work?
Michael Gookin, President
GPS Timers
(833) GPS-TIME
weird troubleshoot black-neutral 120v n black-black 0v [email protected] Residential Electrical Forum 13 09-25-2018 12:24 PM
Troubleshoot question (Ohm's law?) JasonCo General Electrical Discussion 17 09-20-2018 09:00 AM
Troubleshoot question (Odd problem...) JasonCo General Electrical Discussion 17 09-14-2018 04:43 PM
Troubleshoot this 220/221 General Electrical Discussion 14 06-01-2018 02:20 PM
Troubleshoot WronGun Residential Electrical Forum 25 05-09-2017 08:30 PM