Violation or ??? - Electrician Talk - Professional Electrical Contractors Forum
Old 12-15-2017, 12:52 PM   #1
zap
tates1882's Avatar
Rewards Points: 1,072
Default Violation or ???
Iím hooking up some equipment sent by others and came across a funky control drawing. IMO its a violation of ul508a but I thought I would see what everyoneís consensus was. the 5 devices shown in the drawing are all in separate enclosures.
Old 12-15-2017, 02:01 PM   #2
Ax grinder
raider1's Avatar
Rewards Points: 1,162
Is each enclosure listed separately as a UL508A Industrial Control Panel? How is the equipment Marked?
Chris
The Following User Says Thank You to raider1 For This Useful Post:
tates1882 (12-17-2017)
Old 12-15-2017, 03:25 PM   #3
zap
tates1882's Avatar
Chris
Marked as ul508 compliant, but being a panel shop myself, I say that having no overcurrent protection for the control circuit leaving the enclosures is a violation. Along with not having a disconnecting means for the control circuit when it enters the 2nd starter. Also just not a fan a taking one leg from starter 1 and 1 leg from starter 2 to make the control circuit.
Old 12-16-2017, 02:29 PM   #4
Rewards Points: 320
Your points are valid even as an NEC issue.
But UL508 and UL508a are different things. 508 alone just means the components are UL listed. 508a means the ASSEMBLY as a whole is listed. Sometimes OEMs try to get away with not having to pay a UL508a panel shop by using separate UL listed enclosed parts and wiring them together, then taking advantage of the semantics of saying "UL 508 listed controls". In reality it's a dodge and in this case, puts the burden of making the system NEC compliant on the installer. No bueno.
Old 12-17-2017, 12:18 AM   #5
zap
tates1882's Avatar
Marked as 508a compliant, even has the file number.