When 2 different phases touch? - Page 2 - Electrician Talk - Professional Electrical Contractors Forum
Like Tree43Likes
Old 03-21-2017, 02:24 AM   #21
triden's Avatar
Rewards Points: 382
In the simplest terms, you're essentially shorting (bolted fault) the secondary of the transformer together through the breaker. That's why the breaker trips.
telsa and RePhase277 like this.
Old 03-21-2017, 02:26 AM   #22
triden's Avatar
Rewards Points: 382
Originally Posted by sparkiez View Post
http://www.annsgarden.com/poles/JP0-PS-Schematic.jpg
That image shows the two Line taps on a standard pole transformer. If you look, you will see that one is +120V and the other is -120V relative to the neutral on the transformer's secondary. That is how you get 240V potential between L1 and L2.
You have a 240v secondary across L1 and L2. Don't worry about the neutral - it confuses most people. It's just a reference.
telsa likes this.
Old 03-21-2017, 02:30 AM   #23
triden's Avatar
Rewards Points: 382
Depending on the voltage the exact thing does not happen with a ground fault, at higher voltages a ground fault can become an arcing ground fault which will not generate sufficient current to operate SOME Over current protection devices. This fault can be a long term event with devastating results
This was today's job. 5kv cable fault. Probably was arcing for a period of time based on the condition of the cable.
frenchelectrican and telsa like this.
Old 03-21-2017, 08:51 AM   #24
Retired Account
Rewards Points: 14,650
Default Theory Query
If i may, i'd like to throw the theoretical monkey wrench in, a real stumper that an EE presented in an effort to enlighten the great unwashed....
What if on tied all three legs of a perfectly balanced 3 phase system together? perfectly vectored, if you will....
Think something low enough in terms of R value here.
Wouldn't said perfect balance simply cancel each other out?
Flyingsod likes this.
Flyingsod (03-21-2017)
Old 03-21-2017, 10:30 AM   #25
Rewards Points: 114
I don't see how. Phases are not diametrically opposed. Unless said conductors happened to be laying in a coil I don't think there would be enough induction forces to reread ****** electron flow. Thought experiments rule btw, thanks.
Old 03-21-2017, 10:34 AM   #26
Rewards Points: 938
This is dead on. If you put the three separate phases completely in phase, their magnitudes would combine.
Old 03-21-2017, 10:36 AM   #27
Rewards Points: 114
Omg political correctness should not override real words. "Reread *******" should of course be re. Tard
telsa and splatz like this.
The Following User Says Thank You to Flyingsod For This Useful Post:
telsa (03-22-2017)
Old 03-21-2017, 11:08 AM   #28
Rewards Points: 928
I don't even get it. I thought it would be either tie them together in a star or a triangle.
Old 03-21-2017, 12:28 PM   #29
Rewards Points: 3,060
What if on tied all three legs of a perfectly balanced 3 phase system together? ~CS~
It would blow up.
telsa likes this.
Old 03-21-2017, 01:07 PM   #30
Rewards Points: 284
I think you are conflating the effect of magnetic fields cancelling each other out, and current flow, which does not. They are apples and tractors (as in not apples and oranges, which at least are both fruits). With current flow, all you need is a path from one source to return to that source or to earth. With your perfect bolted fault on all three phases the paths from one phase to the next are going to exist and current flow in each phase will immediately jump to being all of the available fault current in the system at that point.
The only difference is that if this bolting of all three phases took place at EXACTLY the same moment and was a PERFECT connection between phases (meaning exactly the same resistance), the fault current wave forms would be symmetrical, not asymmetrical. In the past, things like breakers would have a rating for asymmetrical vs symmetrical fault current because the amount of current relates to the physical stresses exerted on the breaker when trying to open under a fault. The symmetrical rating was always a higher value, but of course was something that never happened in real life. Yet people got confused with that and would use the higher ratings by mistake, so they stopped providing that information. Fault interrupting ratings are now always asymmetrical.
chicken steve and cuba_pete like this.
Old 03-21-2017, 01:54 PM   #31
cuba_pete's Avatar
Rewards Points: 2,945
Default Don't mind me...just trolling for ET junkies
Wha?
Yeah…that’s pretty fücking rich.
I like to see when people try to explain something by posting to someone else’s interpretation as well…
...this interpretation brought to you by the Society of Broadcast Engineers, courtesy of the Ann's Garden...wth??? What kind of a reference is that?
oh my...oh my my my my my...
JRaef...you're one of my heroes.
Troll in Training
Last edited by cuba_pete; 03-21-2017 at 02:14 PM. Reason: more self loathing needed
Old 03-21-2017, 08:18 PM   #32
Rewards Points: 1,922
The OP mentioned touching the conductors together, in terms of fault current this MAY BE somewhat different that a true bolted fault.
Old 03-22-2017, 01:54 AM   #33
triden's Avatar
Rewards Points: 382
I guess it's possible fault current could be worse upstream closer to the transformer. Also, if we are talking arc flash, the location of the actual bolted fault may not have the worst incident energy.
Old 03-22-2017, 07:58 AM   #34
Retired Account
Perhaps a lame Q , but does the definition of 'bolted fault' mean actual bolted parts, ocpd's, etc....?
Old 03-22-2017, 09:08 AM   #35
Rewards Points: 1,360
Bolted means the conductors in the fault are connected with a mechanical strength greater than the fault's ability to seperate them through explosive or magnetic force.
Portable label maker 99cents General Electrical Discussion 42 12-25-2019 11:25 AM
Ipad Pro, surface pro or laptop with touch screen jsmart84 Business, Marketing, and Sales 4 03-13-2017 10:03 PM
Continuity Between 2 Phases of 240V Plug Azachi Canadian Electrical Forum 13 02-16-2017 10:00 AM
Touch Lamp Circuit Microcuts Lighting Design 1 11-21-2016 01:10 PM
why 3 phases system lose one phase and the lights of the lost phase dim? mike883 General Electrical Discussion 12 08-02-2016 12:46 PM