White plastic EMT insulators - Electrician Talk - Professional Electrical Contractors Forum
Old 02-17-2012, 11:47 PM   #1
Rewards Points: 284
Default White plastic EMT insulators
Up to this point, I used those Arlington white plastic insulators on the ends of my EMT if I am shoving Romex down an exposed cinderblock wall or the side of a furnace into a 4 square box (using an EMT set-screw connector w/ plastic bushing to connect to the 4 sq.)
I guess that I just went for the cheapest thing rather than using those Bridgeport EMT to Romex fittings or possibly having to install a junction box to transition from Romex to THHN.
In my own mind, I figured that as long as the Romex was attached within 12" of the white insulator, it was legal.
Then, today the supply house dropped off a replacement bag of these white insulators and I read the label. "For low voltage use only".
Every trade magazine that I have ever read has a picture of these white insulators on the Arlington product page with Romex going into EMT.
My AHJ has never commented on using the white insulators with Romex, but that manufacturer label does not leave any leeway.
Do you use white insulators, EMT connectors with plastic bushings or those EMT-to-Romex fittings?
If you do use those fittings, do you strip the jacket off the Romex before you shove it down the EMT?
Thanks,
Rick
subelect is offline   Reply With Quote
Old 02-17-2012, 11:50 PM   #2
I own stock in FotoMat!
Rewards Points: 6,520
Originally Posted by subelect View Post
........ do you strip the jacket off the Romex before you shove it down the EMT?.........
Doing so is a violation.
subelect (02-18-2012)
Old 02-17-2012, 11:53 PM   #3
Rewards Points: 6,421
I see no special requirement that you use a bushing at all when you're sleeving for protection. If you go one step better and install a bang on bushing (like probably most of us do), then good for you.
Old 02-18-2012, 12:10 AM   #4
Rewards Points: 256
http://www.aifittings.com/products/s...eets/emt50.pdf
Techy is offline   Reply With Quote
The Following User Says Thank You to Techy For This Useful Post:
guest (02-18-2012)
Old 02-18-2012, 12:39 AM   #5
mattsilkwood's Avatar
Rewards Points: 2,006
By all rights romex is low voltage.
A man that will not read has no advantage over a man that can not read.-Mark Twain
Old 02-18-2012, 01:31 AM   #6
Rewards Points: 2,000
Only issue I can see is does the EMT get bonded?
Old 02-18-2012, 01:33 AM   #7
You're going on the assumption that it needs to be. Sleeving for protection is not a conduit system.
Old 02-18-2012, 01:45 AM   #8
But likely to be energized comes into play..
Old 02-18-2012, 08:39 AM   #9
mbednarik's Avatar
Rewards Points: 1,126
334.15 (C). It needs a bushing. I use those bang-on's all of the time, an inspector told me to use those rather than the romex to emt fitting. I always ground the emt/box with a ground screw. If the emt is just a sleeve without any box or device, it does not need to be grounded per 250.86 ex 2
Old 02-18-2012, 10:22 AM   #10
You can't use Ex. 2 alone. It must comply with 1, 3 and 4 as well. It also applies only to existing circuits.
If you install the circuit and it is has a grounding conductor, you must ground the raceway.
Old 02-18-2012, 11:09 AM   #11
rexowner's Avatar
Rewards Points: 518
Sure you can use Exception 2 alone. Exception 1 and Exception 3
have nothing to do with Exception 2.
You seem to be conflating the 4 parts necessary to use Exception 1 with
the completely separate Exception 2.
Exception No. 1: Metal enclosures and raceways for conductors added to existing installations of open wire, knob-and-tube wiring, and nonmetallic-sheathed cable shall not be required to be connected to the equipment grounding conductor where these enclosures or wiring methods comply with (1) through (4) as follows:
(1) Do not provide an equipment ground
(2) Are in runs of less than 7.5 m (25 ft)
(3) Are free from probable contact with ground, grounded metal, metal lath, or other conductive material
(4) Are guarded against contact by persons
Exception No. 2: Short sections of metal enclosures or raceways used to provide support or protection of cable assemblies from physical damage shall not be required to be connected to the equipment grounding conductor. See related ROP
Exception No. 3: A metal elbow shall not be required to be connected to the equipment grounding conductor where it is installed in a nonmetallic raceway and is isolated from possible contact by a minimum cover of 450 mm (18 in.) to any part of the elbow or is encased in not less than 50 mm (2 in.) of concrete.
rexowner is offline   Reply With Quote
Old 02-18-2012, 11:27 AM   #12
Uh, try again.
.... comply with (1) through (4) as follows: ...
Not any or some or one of them, all of them.
Old 02-18-2012, 11:57 AM   #13
buzzbar's Avatar
Rewards Points: 25
Uh, try again.
Items 1 THROUGH 4 refer to exception 1 only. Exception 2 is a stand alone rule.
buzzbar is offline   Reply With Quote
Old 02-18-2012, 12:01 PM   #14
rexowner's Avatar
Rewards Points: 518
Uh, try again.
OK, I'll try again.
The following:
is part of Exception 1. It is not part of Exception 2.
Exception 2 stands on its own independent of Exception 1.
Old 02-18-2012, 12:07 PM   #15
OK, I'll try again.
The following:
Now I see the confusion. I'm referring to 250.86 Ex 1 (2), and you're referring to 250.86 Ex. 2.
guest (02-18-2012), rexowner (02-18-2012)
Old 02-18-2012, 12:28 PM   #16
Rewards Points: 1,360
I wouldn't lose any sleep over it.
Old 02-18-2012, 01:23 PM   #17
Rewards Points: 284
I usually run 3/4" EMT into a 4 square, with an RS cover that meets the requirements of 250, then I bond to the outlet/switch/GFCI ground screw.
I used to also bond the Romex's grd wire to a green screw in the 4 square, but you don't gain anything by double bonding and it wastes time/labor.
Thanks for the replies,
Rick
Old 02-18-2012, 03:31 PM   #18
From the PDF in Techy's link: (Bold underline added by me.)
Uses include power, computer data lines, cable TV, audio/video cable, phone/modem or alarm/security systems. (AND) Meets 2008 NEC requirements for 300-15(c) protection.
So I see no problem at all using them on conduit used to protect Romex. No violation.
And 480, I agree with rexowners' interpretation. Unless the Code states specifically that EXCEPTIONS 1-3 ALL must be complied with, each exception stands alone. But you are right in that if you are trying to apply Exception 1 only, then all four conditions that follow MUST be met. Edit: Whoops, just saw post #15..so I have restated what you already said. My bad.
Plastic boxes Vintage Sounds Canadian Electrical Forum 10 05-09-2012 09:19 PM
2x2 plastic Lenses dronai General Electrical Discussion 18 07-02-2011 11:53 AM
plastic Chris1971 Off Topic (Non Trade) 13 04-19-2011 01:34 PM
plastic shelving.. captkirk Off Topic (Non Trade) 21 04-07-2011 06:06 AM
!)@#$*(%&* Insulators! 480sparky Code Violation Discussion 34 01-02-2011 10:25 AM