Whole house generator question - Electrician Talk - Professional Electrical Contractors Forum
Like Tree19Likes
  • 4 Post By B-Nabs
  • 3 Post By emtnut
  • 2 Post By HackWork
  • 5 Post By emtnut
  • 3 Post By HackWork
  • 1 Post By emtnut
  • 1 Post By trentonmakes
Old 01-19-2019, 02:30 PM   #1
Rewards Points: 6
Default Whole house generator question
I went to a house that had an ATS for a generator that controlled all of the circuits in the house. It all looked pretty standard but for some reason they had the range circuit controlled by a contactor in a large jbox. I've never seen that before. Any idea on why someone would have done that?
ZPelectric is offline   Reply With Quote
Old 01-19-2019, 02:40 PM   #2
Watt Pusher
B-Nabs's Avatar
Rewards Points: 466
Probably the contactor drops out on generator power to prevent overloading the generator.
Old 01-19-2019, 02:41 PM   #3
Band Member
emtnut's Avatar
Rewards Points: 420
I'd think load shedding.
What controls the contactor ?
Old 01-19-2019, 02:49 PM   #4
Rewards Points: 6
A 15 amp circuit controls the contactor. The range is 40 amps. If the range was being used and the generator kicked on how would that change the load?
Old 01-19-2019, 02:51 PM   #5
Can't Remember
Rewards Points: 608
It may have been the only large load on the generator and its either managed or dropped depending on how its wired, ie limit switch on the ATS contactor or load management board.
Old 01-19-2019, 02:56 PM   #6
Rewards Points: 1,671
You mean that they used a #14 romex, right? You didn't confirm that it was going back to a 15A breaker I assume?
As others mentioned, it is connected to the load management in the ATS.
The_Modifier and emtnut like this.
Old 01-19-2019, 03:12 PM   #7
Rewards Points: 6
The contactor was being powered by a 15 amp breaker with 14. The range circuit was being fed by a 40 amp breaker but was also connected to the contactor. I didn't see any 14 going into the ATS. Is the load management usually done at the generator or ATS? I'm not very familiar
Old 01-19-2019, 03:15 PM   #8
Band Member
emtnut's Avatar
Rewards Points: 420
The contactor may be fed from a non-gen fed circuit ... so the range can't run on generator.
Also may be from the load mgt from the ATS.
Need more details !
Old 01-19-2019, 03:18 PM   #9
Need more details !
Either this, or whoever installed it didn't know what to do. They just read that the contactor was 120V so they wired it up to 120V
Old 01-19-2019, 03:30 PM   #10
Band Member
emtnut's Avatar
Rewards Points: 420
I've seen worse
brian john likes this.
Old 01-19-2019, 04:24 PM   #11
trentonmakes's Avatar
Rewards Points: 138
Yes...we do generacs
I was told they use SMS up to 30amps
Anything above needs a contactor.
emtnut likes this.
trentonmakes is online now   Reply With Quote
Old 01-19-2019, 05:11 PM   #12
Rewards Points: 694
It all comes down to how you read it.
I read it as the contactor has 14g wires that activate the coil.
The in and out lines of the contactor are for a 40 amp stove.
So something on the 14g has the ability to turn the feed to the stove on and off. The other end of the 14g goes to the transfer switch.
Everyone is correct, it is to load shed the stove but with out basic details like coil voltage of the contactor and if the contactor is normally open or normally closed its hard to tell how its is shedding the load.
Old 01-22-2019, 05:20 PM   #13
Rewards Points: 14
sounds like a Briggs and Stratton Symphony 11 Power management. It requires a 15 amp 120 volt to signal the high voltage module (contactor) to either turn on or off from the Symphony 11 board in the transfer switch.
Mike Atlas
mike@atlas is offline   Reply With Quote
Old 01-22-2019, 08:07 PM   #14
Watt Pusher
B-Nabs's Avatar
Rewards Points: 466
Old 01-23-2019, 10:04 AM   #15
Rewards Points: 26
Generac SMMs are 50amps.
patmurphey is offline   Reply With Quote
The house with no electricity Islander General Electrical Discussion 18 01-17-2018 01:58 AM
Cracked House catsparky1 General Electrical Discussion 7 11-02-2017 10:37 AM
Detached garage for main service, house as sub. Conduit fill? mikewillnot Residential Electrical Forum 18 07-05-2016 08:45 AM