Can you, by NEC, install a 20a 120v receptacle fed from a panel board with "B" phase being the wild leg? If you use A or C phase you should be okay.
pencil is offline   Reply With Quote
Old 03-19-2019, 05:31 PM   #2
220/221's Avatar
Rewards Points: 4,326
Of course you can
Well....I can anyway. I don't know your skill level
Old 03-19-2019, 05:34 PM   #3
Rewards Points: 2,786
There's no reference point available in the system that's 120V to B -
AB = 240
BC = 240
BN = 208 = BG
So if you were to install a 120V 20a receptacle with B to hot and N to neutral it would be at 208V, violating the listing, the rating, and probably a lot of other things.
As you mention AN or CN is 120V as intended, that's how it's supposed to work with the high leg delta.
The more you know, the less you need.
Old 03-19-2019, 06:51 PM   #4
Rewards Points: 3,472
That is the whole reason for Delta-Hi-Leg distribution
micromind likes this.
Old 03-19-2019, 11:26 PM   #5
Rewards Points: 3,412
Think of a 120/240 3 4 wire system as a single phase system with a high leg added.
The two 120 volt legs are exactly the same as a basic 120/240 single phase system, the high leg is the only oddball.
CoolWill likes this.
Old 03-20-2019, 10:08 AM   #6
animal lover /rat bastard
wildleg's Avatar
Rewards Points: 1,038
what he said.
Old 03-20-2019, 12:33 PM   #7
Rewards Points: 24,112
Welcome aboard @pencil!
Enjoy your ride here.
A receptacle wired in the manner you mention might just take the lead out of your pencil!
Kevin_Essiambre likes this.
Old 03-22-2019, 08:45 AM   #8
German Spy
Helmut's Avatar
Rewards Points: 4,643
BN = 208 = BG
Do they make sp breakers rated for 240V?
I suppose if they did, you could fee 208V equipment from it, couldn't you?
Old 03-22-2019, 11:37 AM   #9
I can't think of a reason why it wouldn't work,
but that doesn't mean there isn't a reason
Old 03-22-2019, 12:30 PM   #10
Rewards Points: 1,481
It would "work" but you may be loading the neutral and the transformer in an unintended way
splatz and Kevin_Essiambre like this.
Old 03-22-2019, 12:45 PM   #11
just the cowboy's Avatar
Rewards Points: 652
Default Not sure
Back in the stone age when I was in school they said no it is unusable because vector wise it goes to 240 first then subtracts to 208. I have heard people on here say you could, if breaker was rated. But I don't think it would be good.
Cowboy
"DID THIS FIX IT??"
Old 03-22-2019, 05:11 PM   #12
Watt Pusher
B-Nabs's Avatar
Rewards Points: 484
Cowboy
This doesn't make sense to me, can you elaborate?
Old 03-22-2019, 05:18 PM   #13
I was trying to think ... which winding would supply the voltage?
Would it be
N-C-B = 208 - half the AC winding plus the BC winding
or
B-A-N = 208 - other half of the AC winding plus the AB winding
or
both
Old 03-22-2019, 10:16 PM   #14
Knotted Ropes Skeery
CoolWill's Avatar
Rewards Points: 1,738
The open delta 4-wire is where you will find the wonky imbalance if you use the high leg to neutral. Not sure of the exact reason, but a closed delta wouldn't have that problem if the transformer with the neutral were sized right.
Old 03-22-2019, 10:17 PM   #15
CoolWill's Avatar
Would it be
or
or
both
Yes.
Old 03-22-2019, 11:42 PM   #16
Years ago, when I was a carpenter, I had a 240 volt worm-drive skilsaw and my compressor was also 240.
I made up some clip less (yes, they were fused) and whenever I worked anywhere there was a 240 ∆, I would use the high leg and the neutral.
Never had a lick of trouble but got some flak from electricians who didn't know better.
Old 09-11-2019, 07:46 PM   #17
Rewards Points: 178
Default John R retired electrician from Fed Gov
SD was making 240 the last time i checked
John R is offline   Reply With Quote
Old 09-11-2019, 08:21 PM   #18
Fist of lightning's Avatar
What was the intended purpose or advantage of using this system back in the day . If you cannot use the b phase with a single pole braker To feed peices of equipment with
Fist of lightning is offline   Reply With Quote
Old 09-11-2019, 08:26 PM   #19
CoolWill's Avatar
1) You got 240 three phase for big motor loads
2) You got 120 V for general power
3) You got an easy place to ground the system
4) You got a nice closed delta to cancel harmonic currents
The 208 volt high leg was just a side effect. You want 240 volt three phase and 120 V single phase from a delta, well, you have to live with the 208. The physics won't have it any other way.
It really is a pretty good and stable system, especially if you have a bunch of motors.
micromind and JRaef like this.
Old 09-12-2019, 02:58 PM   #20
Rewards Points: 546
The operative issue was however, that your loads were PREDOMINANTLY 240V 3 phase, with SOME 120V loads. So think of a machine shop with lots of 3 phase machine tools all around, then a small front office, snack room and bathrooms that need 120V outlets. In some areas the utility will limit the 120V to 5% of the total load because it results in an imbalance. if your loads are predominantly single phase, they will push you to 208Y120.
micromind and CoolWill like this.
2012 Electric only Ford Transit Connect found in the wild Southeast Power Tools, Equipment and New Products 5 12-02-2018 09:48 PM
Delta Service Wild Leg on HVAC equipment sparkiez General Electrical Discussion 42 10-18-2018 02:10 PM
Tomatoes Gone Wild Dennis Alwon Off Topic (Non Trade) 20 06-20-2018 04:14 AM
load changes cause wild voltage swings ??? mikewillnot Residential Electrical Forum 9 03-23-2016 10:28 PM