I am building a 400 amp (class 320) service. Is it permissible to use 500 MCM XHHW aluminum (350 amps rated) since the load is not constant on a service?
John M. is online now   Reply With Quote
Old 04-08-2019, 04:32 PM   #2
Knotted Ropes Skeery
CoolWill's Avatar
Rewards Points: 1,820
As long as the calculated load is less than 350 amps, yes.
Old 04-08-2019, 04:41 PM   #3
Rewards Points: 2,302
Is this a residence?
I can't help it if I'm lucky
Old 04-08-2019, 04:42 PM   #4
Never mind I see it is 3 phase- probably not resi
Old 04-08-2019, 10:12 PM   #5
Rewards Points: 938
What is your over current device rating?
Old 04-08-2019, 10:26 PM   #6
Rewards Points: 26,864
You don't get to use the 90 degree value of 350 Amps... so the rating is 310 Amps.
My Poco dictates wire sizes for Services.
Down stream feeders are sized to the NEC.
Old 04-09-2019, 06:53 AM   #7
Rewards Points: 584
400 amp fuses
Old 04-09-2019, 06:55 AM   #8
Rewards Points: 584
Just talked to my inspector. He says I have to size it to the fuses,
Old 04-09-2019, 07:02 AM   #9
Rewards Points: 938
Parallel 250 kcmil al. a lot easier to work with.
Old 04-09-2019, 07:20 AM   #10
Rewards Points: 584
That is my plan, but this POCO makes us pull service to the pole and dont want paralleled conductors
Old 04-09-2019, 07:38 AM   #11
Rewards Points: 58
Like as in, you can't do it? Or they just don't like it? Sometimes they will splice a short piece of larger copper on to take parallels down to a single wire.
If it's a rule that's actually kind of dumb, because some services you aren't able to do with a single conductor.
Sent from my Moto Z (2) using Tapatalk
Old 04-09-2019, 09:09 AM   #12
Cow
Rewards Points: 5,210
Over here, I'd use 750AL XHHW and downsize the neutral to 250AL if there wasn't much neutral load.
If you have multiple service disconnects, your wire size only has to carry the load regardless of the size of the service disconnects.
But, if you only have one service disconnect, as is your case, you have to size to the rating of the OCPD or use the "round up rule" assuming your calculated load doesn't exceed the conductor rating.
Which is why I suggested 750AL, which is rated 385 amps, if I remember right, and it is allowed to feed a 400 OCPD assuming the load is under 385 amps.
micromind likes this.
Old 04-09-2019, 09:12 AM   #13
Rewards Points: 938
Yeah. Watch out for your lug size and barrels.
Old 04-09-2019, 09:15 AM   #14
Southeast Power's Avatar
Rewards Points: 9,218
400 amps gets 600AL unless they upgrade to 500 Copper.
Old 04-09-2019, 10:28 AM   #15
Rewards Points: 3,482
Here they would take parallel 250 kcmilsAL and splice a single 4/0 AL to the transformer
Southeast Power (04-09-2019)
Old 04-09-2019, 08:29 PM   #16
Cow
600AL is 340 amp conductor.
Using 600AL on a service with single main 400 amp OCPD is noncompliant even using the "round up" rule as 350 amp OCPD's are available.
A person needs to select a conductor size with an ampacity past 350 amps to be able to select the next size up 400 amp OCPD assuming the calculated load is less than the conductor ampacity.
FYI, I'm referencing 310.15(B)16, 240.4(B), and 240.6(A).
tmessner and John R like this.
Old 04-10-2019, 10:27 AM   #17
sbrn33's Avatar
Rewards Points: 3,614
I don't like you anymore...
Wire Size for 125Amp 120/208 panel ColtenK Canadian Electrical Forum 14 09-04-2018 04:07 PM
Branch circuit wire size xnuke Residential Electrical Forum 40 07-30-2018 09:21 AM
Wiring size for service disconnect Spawne32 NEC Code Forum 1 07-20-2018 03:12 PM
Wire Strippers for #18 stranded 2 conductor !Tom Tools, Equipment and New Products 22 05-04-2016 08:22 PM
Northwest Wire Size newspark80 General Electrical Discussion 23 02-18-2016 09:40 AM