Main Breaker for SqD QO-16M panel needed - Page 2 - Electrician Talk - Professional Electrical Contractors Forum
Like Tree16Likes
Old Yesterday, 07:56 AM   #21
Rewards Points: 190
Originally Posted by CoolWill View Post
That sounds like the QO breakers that used 4 spaces. At some point, Square D was unable to make a 100 amp breaker that worked in two spaces, so they made them span 4. I bet this breaker can be replaced by a regular QO.
I think the two space breakers are more prone to buss to breaker failure. They require a hold down.
Probably substituting a different breaker voids UL or other listing.
Connx likes this.
Willie B is online now   Reply With Quote
Old Yesterday, 08:10 AM   #22
Rewards Points: 735
Breaker hold-downs are usually dinky little pieces of plastic that will still allow you to move the breaker quite a bit. They are not required to mitigate breaker-buss connection failures.
They are only required when backfeeding a breaker to stop someone from pulling the breaker off the bus, which would leave the connection point energized. There is an exception to this rule when backfeeding a breaker for solar, since it will shutdown on it's own when removed from the bus.
Old Yesterday, 11:09 AM   #23
Beam Me Up Scotty
Kevin_Essiambre's Avatar
Rewards Points: 322
OP is in canada. So it would be CSA or ULc listing that is voided.
Also, IIRC, at least in Ontario, we do not require a hold down kit.
Connx likes this.
Old Yesterday, 11:56 AM   #24
Rewards Points: 190
I should have separated into two paragraphs. Breaker to buss failure isn't related to the hold down. More a reminder to not pull it off the buss. I've seen a few failures in the two place breakers as a main. Despite my father using them even for 200 amp services in hundreds of electric heat houses in the 60s & 70s, I haven't seen many failures in the four place. In the day they weren't using dielectric grease on the jaws. The old ones did have a pretty reliable track record.
Old Yesterday, 12:55 PM   #25
sbrn33's Avatar
Rewards Points: 3,542
Originally Posted by Southeast Power View Post
I have a milk crate full of those.
They take up both sides of the bus.
Have they been properly tested? If I have learned one thing on this site it is that you can never put a used breaker back into service. You are taking a huge chance. Think about the kids man.
Old Yesterday, 01:11 PM   #26
Beam Me Up Scotty
Rewards Points: 322
I'm sure he's got a 200 amp service he can test them with
Old Yesterday, 06:58 PM   #27
Rewards Points: 26,754
You need a Main breaker to be tested by a certified outfit.
You should be able to ask your AHJ as to which firms are acceptable.
No ordinary LEC can expect to stand muster.
You might find that converting to MLO and setting a knife-switch disconnect up the line is the way forward.
You might find that C-H retro-guts are the way forward.
I can't see your set up from my house. The decision usually turns on many factors.
Old Yesterday, 07:35 PM   #28
Rewards Points: 3,026
the QO 2 pole 100 will not line up with the hole it sits almost to the one side off centre for the main breaker opening I should add that our QO panels have always had a separate compartment for the main breaker and service conductors iirc also this 16 circuit panel has tandem breaker rejectors so cant add much to the panel , double check the buss for arcing
electricguy is online now   Reply With Quote
Old Yesterday, 08:43 PM   #29
Rewards Points: 190
Many years ago I got a call on Friday night. A plumber in his home had suffered a main breaker, (service disconnect), failure.
The installation was horrific. NM cables entered through knock outs without removing the knock out, no connector. More cables entered through the open face, no cover.
I explained this was among the worst I had seen. It needed a new panel. Manufacturer didn't offer a replacement, they did offer a new breaker with adapter terminals.
I went back to the owner, I could replace the panel, clear up numerous other hazards. He declined, all he wanted was a new breaker. Meanwhile he lived without electric heat in his garage using a 60 amp as a makeshift main.
I got the substitute parts, and installed them.
He reported me to the State Inspector, claimed the mess in the panel was my work.
I received a written reprimand from the State, and, no, I never got paid.
Kevin_Essiambre likes this.
Old Yesterday, 09:45 PM   #30
Southeast Power's Avatar
Rewards Points: 8,826
Yes.
The test was how many I could fit in a milk crate.
The answer to the test is 28.
Old Today, 01:21 AM   #31
Yes.
i had a couple of these panels in the used pile I kept the covers and threw out the panels then i get a call from an ec asking if i had the guts for one i am assuming burnt buss