ac servo drive control - Electrician Talk - Professional Electrical Contractors Forum
Old 09-18-2012, 02:24 AM   #1
Post ac servo drive control
hello dear friends.
what should i do on ac servo drive(for example tecco) control circuit
when i press emergency stop button?
i mean that should i disconnect "servo on" signal and give zero setpoint
to it then disconnect the contactor between the drive and motor?
is servo motor coast to stop(free run to stop) if i remove 3 phase main power
from the drive?
suppose that a servo motor is rotating at 1000 rmp and i give zero setpoint
to servo drive. what happen in this situation?
is the motor stopped suddenly or with deceleration time?
is the motor stopped with deceleration time if i disconnect "servo on" signal?
best regards.
seee is offline   Reply With Quote
Old 09-18-2012, 10:47 AM   #2
Rewards Points: 105
Many new drives have External Trip or Emergency Stop inputs. Most of these that use a digital input to control E-stop have a parameter setting for Regen, Coast to Stop, or Dynamic Braking. I have never heard of an application with an ac servo and output contactor. If you do a setpoint change to zero the drive will use the decel rate to stop but will only stop as fast as its Regen or Dynamic Braking will allow. If you don't have enough braking you will likely get buss overvolt faults. If you have a load acting against the motor at the time it will be able to brake faster. If you remove 3 phase supply it can only coast to stop. If you remove "servo on" it may decel or cost to stop depending on the control mode. You mention it may be a Teco servo. I don't believe I have repaired/rebuilt that brand before.
Jabberwoky is offline   Reply With Quote
Old 09-18-2012, 01:16 PM   #3
Rewards Points: 20
Whatever you do, do not use a contactor on the line or load side of the control. You are asking for trouble.
Use the digital inputs for stop and directional changes.
Stopping servo and any other motor quickly will cause the DC bus voltage to rise. You will need a way to bleed off excessive DC buss voltage on quick stop if the load is sufficient.
the controller has all the options on board to facilitate stop. But you might need a braking system should you require quick stops.
Servos are well suited for fast stopping and direction change at fast speeds. They are designed for this type of duty.
Talk to the servo vendor and discuss the need for braking. You may not need any.
Old 09-18-2012, 02:46 PM   #4
hello.
thanks for your replies.
please use the following link and download the pdf file and then please let me to
know your openion.
in some of forums most of experts have told that it is an standard way to use
a contactor in front of drive whether servo drive or vfd !
http://www.ab.com/support/abdrives/p...lays_Rev04.pdf
best regards.
Old 09-18-2012, 05:33 PM   #5
Rewards Points: 684
Originally Posted by seee View Post
hello.
know your openion.
best regards.
That document is now a little bit dated (old), the newer A-B drives now include what is called a "Safe Torque Off" input feature that makes interfacing to safety relays easier and may not always require the use of line contactors. Most of the major drive manufacturers now have that. But if you don't have a drive with that feature, then that document depicts a valid process by which to evaluate your safety design when drives are included.
I want to emphasize though that there is no universally applicable answer, each and every safety system must be evaluated on its own with respect to what the machine does and the hazards and risks associated with using and maintaining it. If you are unfamiliar with the concepts, you should consider hiring someone to do a proper safety evaluation of your machine. The consequences of getting it wrong can be catastrophic.
Is it weird how saying sentences backwards creates backwards sentences saying how weird it is?
Using AB Micro830 to control servo valve and solenoid valve. Heartnet PLCs, VFDs, Motors and Controls 4 08-08-2012 03:35 AM
Servo Sizing mutabi PLCs, VFDs, Motors and Controls 29 01-03-2012 06:02 PM
aeg servo motor drive manual shyless PLCs, VFDs, Motors and Controls 5 09-11-2011 07:31 AM
drive control problem martindag PLCs, VFDs, Motors and Controls 11 11-06-2009 07:31 PM
motor drive control conical-rotor brake motors --help sparkie UK Electrical Forum 5 02-13-2009 05:57 PM