Motor switch/starter ratings - Electrician Talk - Professional Electrical Contractors Forum
Like Tree13Likes
  • 7 Post By 460 Delta
  • 3 Post By Forge Boyz
  • 1 Post By micromind
  • 2 Post By 460 Delta
Old 04-21-2019, 07:53 AM   #1
L_S
Rewards Points: 30
Default Motor switch/starter ratings
Got a used 5HP single phase 208v air compressor to hook-up, and the pressure switch on the unit is only rated 2HP 240V / 1.5HP 120V for single-phase. So I need to find a heavier duty pressure switch or add a motor starter.
Curious that motors are available in both 200V and 230V designs but the switches and starters only seem to have 120, 240, 480, 600V ratings. So I assume a pressure switch rated for 5HP at 240V is also suitable for 5HP at 208V? Probably splitting hairs, the FLC table currents in 430.248 for a 5HP is only a couple amps difference each between 230, 208, 200V.
L_S is offline   Reply With Quote
Old 04-21-2019, 08:46 AM   #2
Peewee0413's Avatar
Rewards Points: 254
Take a couple pictures.
Old 04-21-2019, 09:04 AM   #3
460 Delta's Avatar
Rewards Points: 1,966
Those pressure switches should only be used for pilot duty only. I don’t ever trust them for contactor duty. The surface area of those contacts are tiny and a DP contactor, IEC contactor, or NEMA starter is cheap insurance in my opinion.
Overkill Is Underrated
The Following User Says Thank You to 460 Delta For This Useful Post:
John Valdes (04-21-2019)
Old 04-21-2019, 01:09 PM   #4
Rewards Points: 58
Is it a true 5hp motor? Compressor manufacturers like to exaggerate. What is the full load amperage on the motor?
Sent from my Moto Z (2) using Tapatalk
Old 04-21-2019, 01:51 PM   #5
Rewards Points: 3,412
I don't use very many IEC starters so I don't know about their ratings but I do use a ton of NEMA starters.
Most, if not all, NEMA starters have HP ratings for 200 and 230 volts. I don't know about other manufacturers but the HP tables in the Allen Bradley book list the ratings as motor voltage, not system voltage.
Single phase motors are not listed at 200 volts, I imagine because;
1) As far as I know, no one makes single phase motors in 200 volts.
2) Only an idiot would specify a large single phase motor on a 208 3 system. But yes, it happens all the time.........
Old 04-21-2019, 02:23 PM   #6
L_S
Rewards Points: 30
Actual motor;
Actual pressure switch;
Example of a starter I was considering, and then realized they aren't putting 200/208V ratings on it;
Maybe go with the 7.5HP @ 240V version of that starter..
Yes I know that motor is more suited for a 240V nominal system. The site only has a 120/208 single-phase service, they got a good deal on the compressor and are willing to chance it's longevity running at the lower end of voltage spec.
Old 04-21-2019, 05:31 PM   #7
Peewee0413's Avatar
Rewards Points: 254
You can buy pressure switches on mcmaster Carr that are cheaper than a contactor and enclosure.
Old 04-21-2019, 09:01 PM   #8
Originally Posted by L_S View Post
Actual motor;
That's a 'definite purpose' contractor. It's made mainly for HVAC.
Hermetic HVAC compressors come up to speed quickly so the time spent with more than full-load current is less. Thus, this type of contractor has smaller contacts than other types.
If it is used for something that takes longer to start, the contacts will heat up and eventually burn up because of the longer time spent in high current.
I wouldn't use that type of contractor at its HP ratings, I would go at least one HP step higher and if it starts and stops often, I'd go double the HP.
Even then, it won't hold up as well as a NEMA starter.
One thing to remember about electrical stuff and motor control in particular.....you almost always get what you pay for.
L_S likes this.
Old 04-22-2019, 05:39 AM   #9
460 Delta's Avatar
The motor already has built in overload protection so the additional overloads are unnecessary. Grab a heavy DP contactor or a good used NEMA 2 starter and remove and save the overloads for another project. Or use my method, hit Ebay and buy a good used combo starter of your brand choice and pull in all three phases for the replacement motor in the future.
micromind and L_S like this.
Old 04-23-2019, 12:09 AM   #10
L_S
Rewards Points: 30
That's what I ended up grabbing and using this morning, a 40A / [email protected] 2-Pole Definite-Purpose contactor. Kinda wish I would have gotten a "real" motor starter now that I read your info... Next time!
Question for inspector(s) ie. temp ratings UnlimitedCurrent NEC Code Forum 5 09-22-2018 01:05 PM
Termination Temperature Ratings brian john General Electrical Discussion 16 05-12-2018 08:38 AM
Service feeder ratings for residential newbie44 Canadian Electrical Forum 15 02-01-2018 08:22 PM
CSA not recognizing NEMA ratings?? [email protected] Canadian Electrical Forum 3 02-11-2016 10:14 AM