Protect control cabinets from problematic power sources - Electrician Talk - Professional Electrical Contractors Forum
Like Tree10Likes
Old 04-02-2019, 10:55 AM   #1
Rewards Points: 16
Default Protect control cabinets from problematic power sources
We have about half a dozen PLC/CNC machines in our facility, with various voltages and current loads. For discussion purposes, we can assume they are all the same.
480v 3phase input, 60a circuit breaker, 60hz
These cabinets house PLC controls and VFD's. The facility has the good luck of being hit with random power outages, brownouts and even voltage spikes from outside transformers catching on fire (literally).
Yes, I understand the incoming building power "should" be regulated and steadied by the power company. Last year, a power company technician shorted out a phase while doing service work, and just the other day a transformer randomly blew up. These incidences have created problems with our machinery, burning out circuitry and other odd problems that seem related.
I have been tasked with figuring out a way to try to protect our machines in case this happens again. I have been designing a protection box, that would control a contactor to cut off power to the machine in the event of unsteady power. This should protect from brownouts, phase imbalance or loss, and voltage fluctuation.
Has anyone worked with these devices? Is this a good one, or are the better models?
Macromatic PMD575 (i can't post links)
Thanks in advance for any advice.
sparkiez likes this.
BeerMaintenance is offline   Reply With Quote
Old 04-02-2019, 02:26 PM   #2
Rewards Points: 756
ICM makes a 3ph line voltage monitor that would work for your application as well ....we used them on large heat pump compressors.
Old 04-02-2019, 02:44 PM   #3
MikeFL's Avatar
Rewards Points: 1,970
Welcome to the forums.
Just curious: Do you drink beer?
John Valdes likes this.
Michael Gookin, President
GPS Timers
(833) GPS-TIME
Old 04-02-2019, 02:55 PM   #4
Rewards Points: 16
not enough information. On or Off the job?
John Valdes and CoolWill like this.
Old 04-02-2019, 02:58 PM   #5
Rewards Points: 16
I see many brands that make them. Is there a reason ICM is better than others? Honestly leaning toward ABB right now, but they have so many models I am not sure which is best for my application.
I think in any case it's going to be a tough call between sensitivity/protection and reliability/no false trips.
Old 04-02-2019, 02:59 PM   #6
MikeFL's Avatar
Well I was curious if you're around it all day, is that really what you want when you're not at work.
Friend of mine was graveyard shift manager of a large beer distributor on the east coast. We used to get unlimited beer for $5/ case, any kind we wanted. We didn't do it all the time, but if we were going fishing or having a party, we could always count on him for at least part of the day's needs being met.
GPS Timers
(833) GPS-TIME
Old 04-02-2019, 04:37 PM   #7
Rewards Points: 16
Theres always cans/bottles that the machines reject for various reasons... 1mm too low filled, or damaged lables... employees get to fight over those They also sell to us at cost
MikeFL likes this.
Old 04-02-2019, 08:07 PM   #8
Rora's Avatar
Rewards Points: 624
Not sure about the equipment, but since you're tasked with this just understand that you're now the fall guy whether you tune it "on the safe side" and it shuts down production for a nuisance alarm, or tune it for practical reliability then anything fails which might point the finger at the supply.
Be sure to keep management involved, give your defense on the small details up front and get them to sign off on it... ultimately make sure that you're just providing the legwork for a solution, not being responsible for it.
Old 04-02-2019, 08:44 PM   #9
MikeFL's Avatar
That's outstanding advice.
Another option is to tell them what their options are and let them select what protections they want.
glen1971 and Rora like this.
GPS Timers
(833) GPS-TIME
Old 04-02-2019, 09:03 PM   #10
Rewards Points: 6,397
Do they have a sales rep.? Maybe contact him/her, and ask. Share the blame.
Old 04-02-2019, 09:15 PM   #11
Rora's Avatar
Rewards Points: 624
Even better... this also transfers the responsibility of asking the right questions onto them. If you just spec something out that they then approve, they can still claim "you didn't tell us that, it was your idea and I trusted that you made the right choice!"
They ought to vett everything you present either way, but by making it their decision puts the onus on them to make sure THEIR decision is a good one. You might still get some flak if something happens but you're a lot less likely to get fired as a scape goat.
Old 04-03-2019, 06:15 AM   #12
Rewards Points: 694
I honestly do not see the point. In real life equipment is damaged by the spike with in 1 cycle so trying to disconnect the equipment just seems to slow.
A simple phase/voltage monitoring relay should be able to shut down control power which covers some of the problems (brown outs), Ups units on the control power protect the expensive parts then a box full of surge suppressors deals with the spikes.
In florida i swear more panel space is used for suppressors and ups units than plc hardware.
Old 04-03-2019, 08:25 AM   #13
Rewards Points: 16
This is what I normally do.
I'm not worried about being 'held responsible' in the way that you guys are thinking. I don't get grief for trying... they just want solutions that generally make things better.
Speaking of filtering, do the line filters do a whole lot? I have seen them factory installed for higher end machines, like Kuka robot cabinets... but they aren't much more than RC filter circuits, correct? I could see them help with electrical noise, but I don't have that problem.
Old 04-03-2019, 08:37 AM   #14
Rewards Points: 16
This is why I am asking. I understand a phase monitor won't prevent all problems, but the vast majority of the damage I have seen has been the on/off/on/brown/off/on cycles that happen during a power failure. If the power just cuts out, that usually doesn't hurt anything, but usually it cycles a few times then quits.
In my experience with Mov's, they don't last that long, and questionable how much they actually help. Anyone have more experience with them?
Old 04-03-2019, 11:45 AM   #15
Bird dog's Avatar
Rewards Points: 830
Maybe a problem with the POCO equipment?
Old 04-03-2019, 02:30 PM   #16
Rewards Points: 3,528
Depends what is common in your area too.. I've installed lots of Omron K8AB relays for phase loss/reversal with good success.. Tie their dry contacts into a relay/contactor to drop out the control power you want to isolate or alarm, light, etc. They can be time and voltage adjusted on site.
They don't like harmonics though! Found that out after the magic smoke got let out of one.
Old 04-04-2019, 06:07 AM   #17
Rewards Points: 694
Mov's work but by the nature of there design they will fail. You have to work out if the mov failing is cheaper than replacing the hardware it is protecting.
(works great on the 480v side)
As for the problem you are describing i would go with a phase/voltage protection relay and install it in the control voltage circuit. If you use another relay and a button you can make a simple latched relay for control power.
Operator presses button to turn on control power, Any glitch will cut control power until the button is pressed again (this allows the operator to make the machine safe before restoring power)
Old 04-04-2019, 06:55 AM   #18
Rewards Points: 2,772
Everyone that uses plug in surge strips has experience with MOVs. As @gpop said, MOVs are sacrificial devices, you have to keep replacing them. Sometimes they sacrifice themselves in spectacular manner blowing apart the SPD. But they don't sound like a good fit for you.
MOVs don't start acting until the voltage is much higher than the normal supply voltage. If you buy MOV protection for 480V supply it doesn't jump in at 481V. If you have a distribution line or MV line short to your 480V supply they will jump in. They do nothing at all for brownouts, dropouts, etc. Power conditioners do that.
I know they make big power conditioners but I've only seen them in literature. I have used little power conditioners and a lot of people really swear by them.
The product brochures claim the big ones are used in medical facilities and telecom, I could see them at say an MRI clinic. They might make sense in an industrial application if the cost of the equipment wrecked and the cost of the lost production justifies it.
I am not sure what power conditioners do if you lose a phase for more than a cycle or a few cycles. If you can safely cut power (IF) I think something like the macromatic you selected is a good way to go no matter what, if you can install conditioners ahead of the equipment too, they'll have to act less often.
Old 04-05-2019, 04:19 PM   #19
Rewards Points: 1,856
IMHO you can't start throwing money at it until you have fully identified the nature of the problems first. There are solutions for most problems, but not many that will cover more than one. You can't cover every single contingency, it would cost way more than you might imagine, but you can cover most of them if you plan it wisely. I suggest renting or borrowing a recording meter / analyzer for a few weeks first to see what the most common issues are and start with those.
On a side note: Opening a contactor ahead of a machine every time there is a glitch will only serve the purpose of letting you know how MANY glitches in power take place every day, because it will be a serious annoyance and likely end up disabled in no time. It's better to accept the fact that "stuff" happens and plan for it accordingly.
Old 05-01-2019, 11:09 AM   #20
Rewards Points: 16
Thanks everyone for the input. It's all about what I expected.
I don't see it as "throwing money at it" when I am only talking about $500 worth of parts to protect a $50k cabinet.
I also know that some of the cabinets do have 'power conditioners' built into them, but they are small and passive... it appears they are basically LC filters.
I suppose it wouldnt hurt to look into MOV's for each cabinet, to add on top of my phase monitor relay, as long as I replace them on a schedule, like bi-annual.
VFD speed control from external sources icyhammer General Electrical Discussion 19 05-19-2018 06:52 AM
Generac transformer control transformer troubleshoot MTW Industrial Electrical Forum 2 03-05-2018 08:16 PM
Advice needed! Electrician and EE degree Dale333 Electrician Apprentice Forum 16 11-30-2017 05:21 PM
Septic pump control box power (resi) MTW NEC Code Forum 38 08-07-2017 11:20 PM
Control Room Power Distribution izatso General Electrical Discussion 2 07-05-2017 06:30 PM