I am working on a building from the 1800s, it has what I believe to be a two-stage system. It has 3 wires with 3 fuses but one is a neutral. So from ground to A is 240V ground To B is 240V and ground to C is 0V but, from any leg to leg is 240V.
My question is if I move this machine shop to a new location will these motors that are running on 240V 2 phase run on a 208V three-phase system? I am not that good with motors. I assume I would also have to check the starters and contactors in the control system. Any advice would be greatly appreciated thank you.
Two phase system-8e43d928-fe8d-4686-9e24-7b36fbac5d6f_1533570135031.jpg   Two phase system-cabe42f5-645c-451a-8313-f0b39a8414c5_1533570184124.jpg
Robbie Rob is offline   Reply With Quote
Old 08-06-2018, 12:50 PM   #2
*believe To be a two PHASE system
Old 08-06-2018, 01:40 PM   #3
Rewards Points: 6,421
corner grounded delta.
Unless you're working in Niagara Falls, Hartford CT, Philadelphia, or the textile regions of the Carolinas, you're unlikely to see two-phase in your life.
The Following 3 Users Say Thank You to MDShunk For This Useful Post:
Grounded-B (08-10-2018), pudge565 (08-10-2018), Southeast Power (08-06-2018)
Old 08-06-2018, 01:45 PM   #4
MTW
Rewards Points: 9,936
Unless you're working in Niagara Falls, Philadelphia, or the textile regions of the Carolinas, you're unlikely to see two-phase in your life.
Most of the smaller services of that vintage serving manufacturing in my area were ungrounded delta. A few still remain.
Old 08-06-2018, 01:47 PM   #5
MTW
A time capsule machine shop. What does this place produce?
Old 08-06-2018, 01:48 PM   #6
Functionally, it makes little difference in this case. He doesn't have a two-phase system.
Southeast Power likes this.
Old 08-06-2018, 01:49 PM   #7
The lathes and punch presses are WWII vintage or newer. Not original to the building, but old enough just the same. Perfect size for the home shop guy.
Old 08-06-2018, 02:29 PM   #8
MikeFL's Avatar
Rewards Points: 456
Awesome pictures!
Michael Gookin, President
GPS Timers
(833) GPS-TIME
Old 08-06-2018, 03:51 PM   #9
460 Delta's Avatar
Rewards Points: 1,222
The answer to your question, is maybe. If the 208 star you’re going to put it on is on the hot side, say at 215 or so it should be fine. Most of those were designed at a time when 220 was the voltage of the day. Updates may be for 240 though so some testing will be necessary.
Old 08-06-2018, 06:00 PM   #10
A time capsule machine shop. [IMG class=inlineimg]https://www.electriciantalk.com/images/smilies/eek.gif[/IMG] What does this place produce?
Small metal gasket. Making the same gaskets from the 1800s still going strong
Old 08-06-2018, 06:04 PM   #11
Thank you, most of the nameplates were worn off so it’s hard to tell what they were and what they could run on. I’ll have to do a little figuring out
Old 08-06-2018, 10:48 PM   #12
Rewards Points: 74
Not True...... The university I work at (long island, NY) still has one building that has 2 phase 5 wire. I also believe there is still some in the village of Rockville center, NY which has it's own power utility.
Gary
AU Facilities is offline   Reply With Quote
Old 08-07-2018, 12:19 AM   #13
Rewards Points: 254
As MDShunk said, you don't have a "2 phase" system, you have a 240V 3 phase delta corner grounded system. Very common. In days of old it may have started out as an ungrounded delta system, because so long as it was supplying 3 phase loads, it was considered "more reliable". But over time the potential dangers of that became so apparent that the NEC required that you EITHER ground one corner, or install a "ground fault monitoring system", which meant spending money. So many people opted to just tie one phase to ground because it was cheaper that way.
If you move to a place that has 208Y120V, those old motors may not like it, or they may be fine, there's no way to tell in advance. But it's true that if they were old enough, i.e. WWII vintage, they were likely built as "220V" and can tolerate +-10%. So that makes them good down to 198V, which is 208V -5%, within a utility's allowable deviation. However if your Voltage Drop at the actual machine is already 3%, AND the utility drops 5%, you may be out of tolerance for the motors. You'll just have to do it and measure it when you get there. If it's too low, add buck-boost transformers.
Old 08-07-2018, 06:47 AM   #14
Rewards Points: 1,726
You have a corner grounded 240 volt delta, three phase system system.
Most motors, but not all, can operate on 240 or 208. As Jraef said, it can depend on the actual voltage at the machines at each location. I have seem a 240 system where the actual voltage was 219 and a 208 system where the voltage was 223.
Remember, a lower voltage will increase motor current and heat. These old motors are pre NEMA standard, so replacements could be a challenge and rebuilds expensive. It could be cheap insurance to add a boost transformer to have a 240 volt system.
just the cowboy and splatz like this.
Old 08-08-2018, 04:30 AM   #15
Gary
I didn't make a statement that could be responded to with true or false. I said "unlikely", but thanks for playing along. The places I listed are historically places where you're likely to still find two-phase. In the rest of the country, it's quite unlikely. It's neat that you have a building still served with this vintage system.
Old 08-09-2018, 11:23 AM   #16
Rewards Points: 74
My apologies...... And not really that neat, it's a pain in the ass because most don't know much about it. We have managed to get rid of all the loads and are down to one left, the old freight elevator.
Old 08-09-2018, 07:20 PM   #17
Rewards Points: 21,856
Just of few of us left is still famuair with old school true two phase system I already dealt 3, 4 and 5 wire system it kinda a big headache if you are not aware how it set up. ( too many guys end up hook up wrong phase and blow the fuse pretty fast is most common one )
Math and finding a circuits phase on a 3 phase system Arrow3030 Off Topic (Non Trade) 35 01-21-2018 08:14 PM
Electrical Theory question.. phase balancing Jmp2016 General Electrical Discussion 8 10-11-2017 01:40 PM
Multi wire circuit 3 phase system Dash Dingo General Electrical Discussion 12 09-23-2017 06:54 PM
Customer needs 30 Hp 3 phase Specialty compressor system. nownojin PLCs, VFDs, Motors and Controls 27 02-16-2017 08:14 AM
can anyone explain why in a 3 phase system, any 2 phase can share a neutral? mike883 General Electrical Discussion 27 05-09-2016 08:46 AM