Grounding/Neutral Question - Electrician Talk - Professional Electrical Contractors Forum
Old 05-31-2012, 10:30 AM   #1
gappvembe's Avatar
Rewards Points: 22
Question Grounding/Neutral Question
I'm running a sub-panel to a garage. I am coming from the bottom side of the meter socket, which seems to be ok per 230.40 exception 3.
My question is about the Neutral.
Do I hook up the the Neutral to the ground bar of the disconnect/circuit breaker box, with the ground & Neutral that goes to the garage, or do I just hook up the two neutrals and isolate the ground?
*The box is PVC, so the ground terminal strip is all it goes to.
At the sub-panel in the garage where this power is going, I will be isolating the ground and neutral.
I guess my question boils down to; do I do it before this or not?
gappvembe is offline   Reply With Quote
Old 05-31-2012, 10:38 AM   #2
BBQ
Salty Member
BBQ's Avatar
The neutral from the meter socket should land on the neutral bar of the new enclosure not the 'ground bar'.
If the new enclosure does not have a neutral terminal it is not a service rated enclosure and will need to be replaced.
Assuming the new enclosure does have a neutral bar the neutral from the meter should go to as would the neutral and equipment grounding conductor of the feeder to the garage.
By the way, the exceptions allow you to go directly all the way from the meter on the home out to the garage without the need of a garage disconnect at the home. You would also be able to eliminate one conductor if you eliminate the disconnect at the house.
You would treat these service conductors at the garage just like any service.
Old 05-31-2012, 10:53 AM   #3
gappvembe's Avatar
Rewards Points: 22
This is a Square D QO-200TRNM: 60AMP Max Rainproof Type 3R Enclosure.
I replaced the Switch, with an actual breaker. I didn't feel comfortable with the wire going out to the garage, buried, with no over-current protection.
I get what you are saying with only using 3 conductors.
Thanks.
Neutral question FireInTheWire General Electrical Discussion 10 05-18-2012 12:20 AM
GFCI neutral question cfiitcb General Electrical Discussion 10 05-01-2012 09:06 PM
Shared Neutral Question Tank General Electrical Discussion 12 12-17-2010 08:48 PM
Neutral Question... sparky723 NEC Code Forum 45 11-22-2010 03:08 PM
Neutral Question micromind General Electrical Discussion 48 05-30-2009 07:08 PM