Default MWBC GE AFCI/GFCI tripping
Hey guys got a quick one for ya on this Sunday morning. I recently rewired a home from scratch with the laundry room and 3 full baths on the second floor all next to each other. After discussing my plan to use MWBC's with my supplier, i was told i could share neutrals with the use of GE AFCI/GFCI breakers with tie handles to achieve my goal of using 2 12/3's to hit the laundry and three bathrooms, having them all on their own 20A dedicated circuits. Problem i am having is that i can only get one half of each MWBC to hold, and whenever i put a load on the other half, breaker trips. I have traced everything back to the panel to the first box and everything looks fine. I'm now at the point of installing AFCI only breakers and putting GFCI receptacles in the laundry and bathrooms to alleviate the problem, that's my plan b. I'm heading back today to continue troubleshooting and cant shake this gut feeling that i am close to solving this problem. I need help. Any insight would be greatly appreciated. Thanks all!
electricdrummer is offline   Reply With Quote
Old 05-05-2019, 08:58 AM   #2
Mensa Player
Rewards Points: 1,801
"i was told i could share neutrals with the use of GE AFCI/GFCI breakers with tie handles to achieve my goal of using 2 12/3's to hit the laundry and three bathrooms"
Are you using 2-pole AFCI/GFCI breakers made for this purpose? Or 2 single poles with a handle tie that you installed between them?
electricdrummer (05-05-2019)
Old 05-05-2019, 09:04 AM   #3
Rewards Points: 1,010
It is not possible to share the neutral from two different circuits with AFCI/GFCI breaker. It will trip every time. Supply house guys aren't really the best source of information to understand how something works, IMO. MWBC conductors, for what you did, would have been you using the multi conductor with two neutrals in the sheath.
electricdrummer likes this.
J F Go is offline   Reply With Quote
The Following User Says Thank You to J F Go For This Useful Post:
Old 05-05-2019, 09:42 AM   #4
Gold Pliers Champion
Signal1's Avatar
Rewards Points: 2,138
He said was using the new GE breakers, which you can in fact share a neutral at least for the AFCI ones, not sure about the Dual function GFCI/AFCI.
https://www.geindustrial.com/print/node/234861
Great for retrofits, however the OP said "rewired from scratch", hmmm, I'd give everyone a neutral while I had the chance.
"He said was using the new GE breakers",
edit: I stand corrected, the OP didn't say this.
Signal1 is online now   Reply With Quote
Old 05-05-2019, 09:42 AM   #5
Rewards Points: 49
thanks hack! that's it! I will pick up 2pole breakers first thing monday morning.
Old 05-05-2019, 09:44 AM   #6
Service Call's Avatar
Rewards Points: 28
Nope. Need a 2 pole breaker. 2 singles tied together ain’t gonna work.
Old 05-05-2019, 09:46 AM   #7
Can't Remember
Rewards Points: 974
I have used a handle tie with two single pole GE AFCI breakers, but not the Dual function type. I think the Dual function is the problem. If you have a real two pole Dual function made the same way one is that we typically use on a hot tub (if there is such a thing), you'd probably be ok. I think you are going to have to go back to GFCI at the point of use, provided it's accessible.
Old 05-05-2019, 11:48 AM   #8
Rewards Points: 1,361
GE's regular combination type non gfci arc fault breakers no longer have any kind of ground fault protection. The handle tie works just fine for them. A gfci breaker depends on the neutral from each circuit to be landed on the device. They measure the current usage between hot and neutral. More then 5 mA difference and they trip. This is why one of your breakers is tripping. You need 2 pole breakers in this application.
I don't think anyone has a 2 pole dual function breaker yet. It's a day late and a dollar short for this job, but 2 12/2 home runs are only $10 more in material then 1 12/3. You are now going to spend $25 in GFCI outlets to save $10 in wire
Old 05-05-2019, 11:55 AM   #9
Mensa Player
So you guys are saying that you can use 2 standard single pole combo AFCI breakers (no GFCI) with a handle tie to power both legs of a MWBC and it will work without issue?
I know that if you touch the neutral to ground of a circuit fed with an AFCI it will trip, so I didn't think 2 of them would work with a shared neutral of a MWBC.
Old 05-05-2019, 12:13 PM   #10
GE has specifically removed any ground fault protection from their standard combo single pole arc fault breakers. MWBC or not, you don't need to land the neutral on their afci breakers
http://apps.geindustrial.com/publibr...me=DEQ-234.PDF
Old 05-05-2019, 12:19 PM   #11
Can't Remember
Rewards Points: 974
I've done this at least half a dozen times and have it in my own house with the GE AFCI breakers.
Old 05-05-2019, 02:05 PM   #12
Band Member
emtnut's Avatar
Rewards Points: 878
As Signal1 mentioned, GE took the GFP out of the their AFCI breakers. So you could use 2 single poles with a tie bar and not have a problem.
AFAIK, they didn't take the GFP out of the GFCI
BR took the GFP out of their AFCI's as well, but it's not documented (at least anywhere I can find)
So for a dual function, OP would need a 2 pole breaker.
Old 05-05-2019, 02:18 PM   #13
Now, if we can only convince them to take the AFCI protection out of AFCI breakers
Tripping AFCI fred122 Residential Electrical Forum 3 01-25-2019 09:10 PM
Breaker tripping on instantaneous ProcessAutomate07 Canadian Electrical Forum 9 11-29-2018 08:03 PM
Eaton/CH 3000a 480v GFP Tripping RyanMc General Electrical Discussion 34 03-02-2018 11:24 AM
Mitigating Arc fault breakers tripping on upstream events Gnome General Electrical Discussion 21 02-17-2018 09:18 AM
Siemens AFCI/GFCI Breaker Woes sparky80 General Electrical Discussion 19 05-04-2017 07:59 PM