NM in sleeve on outside of house? - Electrician Talk - Professional Electrical Contractors Forum
Like Tree8Likes
  • 1 Post By MTW
  • 1 Post By CoolWill
  • 5 Post By HackWork
  • 1 Post By HackWork
Old 04-03-2019, 09:52 PM   #1
Rewards Points: 697
Default NM in sleeve on outside of house?
Running #6 NM cable from basement up to 2nd floor attic, and then @ 150' and down into a garage, ideally avoiding splices. The easiest way up to the attic is on the outside of the house: out wall above panel, LB & PVC & LB straight up and into the attic wall. I believe that's a violation, as the outside qualifies as a wet location. It doesn't seem fair though. Inside this PVC is the least likely place to get wet, ever. I'm know I'm answering my own question; just grumbling.
mikewillnot is offline   Reply With Quote
Old 04-03-2019, 10:01 PM   #2
MTW
MTW's Avatar
Rewards Points: 7,586
I'd do it anyway. The NEC is a book of suggestions, not rules.
mikewillnot likes this.
The Following 2 Users Say Thank You to MTW For This Useful Post:
Ctsparky93 (04-03-2019), mikewillnot (04-03-2019)
Old 04-03-2019, 10:01 PM   #3
CoolWill's Avatar
Rewards Points: 1,694
I wouldn't really lose too much sleep over something like that. Burying itbin the ground would be one thing, but the type of install you suggest is pretty tame.
I'm With Her! Hillary 2016
Old 04-04-2019, 06:48 AM   #4
Rewards Points: 1,567
Why would you use #6 romex?
#6 aluminum SER cable has the same ampacity and costs a lot less.
And as an added benefit can be compliantly used inside of the exterior conduit.
ETA- or it can just be run up the wall without the conduit.
There are 2 types of electrician... Those who knowingly break code, and those who lie about it.
Old 04-04-2019, 03:38 PM   #5
Rewards Points: 524
6 romex and 6 aluminum SER are NOT the same ampacity!! 6 romex is 60 amp. 6 alum. is 50 amp.
John M. is online now   Reply With Quote
Old 04-04-2019, 03:55 PM   #6
#6 romex is not good for 60A, you are not allowed to use #6 romex if the load is going to be 60A. You can use a 60A breaker only because there is no standard 55A breaker, but the load has to be 55A or less.
If you need 60A, then you use #4 aluminum SER cable which is still much cheaper than #6 romex.
jhil302 likes this.
Old 04-05-2019, 12:17 AM   #7
Can't sign em..forget em
lighterup's Avatar
Rewards Points: 10,046
I got a red tag for sleeving NM...above ground.
It came out of the house into a 3/4" LB down about
4' of schedule 40 pvc and then I used a jake to turn into
the side of an AC disco for central air.
Inspector made me set a JB in the basement ceiling and
transfer over to thhn. Bastahd!
Old 04-12-2019, 11:09 AM   #8
Rewards Points: 24
Inspectors around here donít call that for a violation when in vertical runs from an attic down to a box. I run #6 Romex from the panel direct to the soffit and down a conduit into a hub on top of a hot tub disconnect all the time. There is no water accumulation in that event.
Horizontal runs are different because if water is in the conduit then the wire is straight up laying in the water.
Drsparky14 is offline   Reply With Quote
Old 04-12-2019, 11:21 AM   #9
Rewards Points: 1,080
Inside any raceway on the outside is subject to condensation which builds up on the inside. I agree, to some degree, with those who feel the vertical run is not an issue however a vertical run from the top of a panel could cause water dripping into the panel from the condensation.
In NC then made an amendment that allows 6'
300.9 Raceways in Wet Locations Above grade.
Where raceways are installed in wet locations
above grade, the interior of these raceways shall be
considered to be a wet location. Insulated
conductors and cables installed in raceway in wet
locations above grade shall comply with
310.10(C).
Exception: The raceway shall not be considered a
wet location if:
(1) The section of raceway routed in a wet
location above grade does not exceed 1.8 m
(6 ft) in length;
(2) Any fittings or conduit bodies are watertight
and listed for use in wet locations; and
(3) All termination points of the raceway are
only open in any of the following:
a. A dry location;
b. Equipment suitable for outdoor use; or
c. Equipment listed for use in a wet
location.
My feeling is if you sleeve the wire from a crawl space up to an exterior panel there should not be an issue. This has been done in NC for as long as I have been working here- over 40 years.
I can't help it if I'm lucky
Old 04-12-2019, 04:24 PM   #10
Sentimental Mental
CTshockhazard's Avatar
Rewards Points: 1,388
Originally Posted by Dennis Alwon View Post
...however a vertical run from the top of a panel could cause water dripping into the panel from the condensation.
If that was truly a concern, then SE/SER should have the same restriction.
In fact all cables should be prohibited from vertically run exterior raceways that enter the top of an enclosure
Wait a minute, we'd have the exact same issue with individual conductors.
At any rate, I think you can tell that I wouldn't be worried.
Either you like bacon, or you are wrong.
CTshockhazard is online now   Reply With Quote
Old 05-11-2019, 09:09 PM   #11
Rewards Points: 697
[OP] - the sleeve would be open at each end, one in the basement and the other in the attic; from the basement exit to the attic entry points, it would be outdoors. No end of the sleeve would connect to a panel or enclosure of any kind. Any condensation in the outside run would drain out onto the basement floor. there might actually be air circulation from one end to the other.
Actually, I might have run into the same situation (upcoming) with a run of SER.
The house with no electricity Islander General Electrical Discussion 18 01-17-2018 01:58 AM
Cracked House catsparky1 General Electrical Discussion 7 11-02-2017 10:37 AM
Detached garage for main service, house as sub. Conduit fill? mikewillnot Residential Electrical Forum 18 07-05-2016 08:45 AM