Old 09-23-2018, 06:44 PM   #1
Default weird troubleshoot black-neutral 120v n black-black 0v
i had a troubleshoot today as subject, called hydro for service yet im confused on how it happens.
detail as following:
when main breaker is off, incoming black-black around 5v, black-neutral 123/125 respectively;
when breaker is on, one side lost voltage while the other side remain around 120.
called hydro for service, yet dont get how this happening.
any comment appreciated
mmmzhu@gmail.com is offline
Sponsored Links
Advertisement
Old 09-23-2018, 06:51 PM   #2
Rewards Points: 25,630
Please fill out your profile.
The_Modifier and Bird dog like this.
telsa is online now
Old 09-23-2018, 08:20 PM   #3
neutral member
readydave8's Avatar
Rewards Points: 568
one leg
put down your meter and find the open
Dave Ruth
readydave8 is offline
Sponsored Links
Advertisement
Old 09-23-2018, 08:45 PM   #4
Modérateur
frenchelectrican's Avatar
Rewards Points: 16,780
Are you a homeowner or EC ?
Also call the Hydro to check their side to make sure it is good to go.
That is classic open hot conductor senicearo.
If you are a homeowner just get a electrician come out and let them deal with it this part may not be a diy at all.
Bleu est beau.
frenchelectrican is offline
Old 09-23-2018, 08:48 PM   #5
John Valdes's Avatar
Rewards Points: 2,758
Please take a few minutes and fill out your profile.
@frenchelectrician will boot you soon if you don't.
John Valdes is offline
The Following 2 Users Say Thank You to John Valdes For This Useful Post:
frenchelectrican (09-23-2018), The_Modifier (09-26-2018)
Old 09-23-2018, 08:56 PM   #6
He's waiting. 100, 99, 98, 97.........Clock is running. He is very stern!
frenchelectrican and MikeFL like this.
Old 09-23-2018, 09:23 PM   #7
ok i figure it out.
im electrician.
one hot was broken, forming a capacitor equivalent circuit on this line. since its 60hz, say left side (A)of this capacitor connecting supply while right side (B)to panel, hence when measuring voltage between B and neutral, yet it shows about 120v, however if measure between B and another hot, B will be almost in phase with another hot wire, end up with only a few volt.
when connecting to load, this wire literally become open circuit hence voltage zero on load
Old 09-23-2018, 09:32 PM   #8
Modérateur
Originally Posted by [email protected] View Post
ok i figure it out.
im electrician.
Ok then please fill out the profile as I post the link below.,
http://www.electriciantalk.com/f3/at...fields-258186/
Merci.
The_Modifier likes this.
Bleu est beau.
Old 09-23-2018, 10:46 PM   #9
hi, the link doesnt work
Old 09-23-2018, 11:14 PM   #10
Modérateur
Just let ya know I got the link fixed now so you can hit it anytime ., sorry about that.,,
Bleu est beau.
Old 09-24-2018, 12:26 PM   #11
I had the wrong one too Marc. Hax caught it and let me know. You must have had the test version which is not available to the community.
Old 09-24-2018, 01:59 PM   #12
Modérateur
Ya almost there but the issue was the HTTP it was double that how my oringal one messed up and took me a second to figure out why it went wrong.
John Valdes likes this.
Bleu est beau.
Old 09-24-2018, 08:37 PM   #13
neutral member
readydave8's Avatar
Rewards Points: 568
ok i figure it out.
im electrician.
well thats nifty that now you know why readings were confusing
so did you fix it? where was it broke?
Dave Ruth
Old 09-25-2018, 12:24 PM   #14
This going no where. So I'm closing it.
OP.....This does not affect your account. So fill out your profile if you still want to participate....Thanks
The Following User Says Thank You to John Valdes For This Useful Post:
Bird dog (09-25-2018)
Closed Thread
Thread Tools
120V to ground on hot and neutral pitapacket Residential Electrical Forum 10 06-12-2016 05:27 PM
Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com