Arc welder accidently trips building off ECall - Electrician Talk - Professional Electrical Contractors Forum
Like Tree8Likes
  • 3 Post By joe-nwt
  • 4 Post By brian john
  • 1 Post By just the cowboy
Old 05-21-2020, 07:02 PM   #1
JCAUPS1's Avatar
Rewards Points: 34
Default Arc welder accidently trips building off ECall
A welder was called out by the company facility manager to repair a Damaged Gate-The motorized Iron gate happened to be grounded to the building ground grid. Upon welding the gate the site main tripped--The generators fired up & the welder had no idea until the facility manager ran out & stopped him.
So the welder said it was not his fault because that's where he was told to weld.
So who's fault is it?
JCAUPS1 is offline   Reply With Quote
Old 05-21-2020, 07:12 PM   #2
joe-nwt's Avatar
Rewards Points: 1,806
I would be inclined to think the site service should be inspected if welding a gate caused it to trip. Especially the grounding. I wouldn't blame the welder.
joe-nwt is online now   Reply With Quote
Old 05-21-2020, 07:23 PM   #3
Rewards Points: 3,206
It seems strange that a welder placing current on the ground (which welders do) but they set up a circuit from the welder to the equipment that is being welded and back to the welder. The current should not be tripping the main.
UNLESS there are neutrals grounded downstream from the service and the current is on those neutrals, resulting in the GFPE on the main seeing current in excess of the relay setting.
If the welder's equipment checks out I would not blame the welder for doing what welders do weld.
Old 05-22-2020, 01:49 PM   #4
just the cowboy's Avatar
Rewards Points: 504
I have seen electronics fry when welders hook up their ground wire to one end of a machine and weld at the other. Usually when two devices mounted on the machine are referencing something to ground and something to neutral. A parallel path for current to return.
But for welding on a gate I would not think so unless like said above boot legged neutral somewhere.
Cowboy
micromind likes this.
"DID THIS FIX IT??"
Old 05-22-2020, 02:09 PM   #5
stiffneck's Avatar
Rewards Points: 1,298
Did the welder use house power? Could be a combination of marginal welder equipment and a sensitive fault setting. Once in a while, an ancient Ozark/TWA ground power unit would trip a 480 distribution Ground Fault and .25 mile of "D" concourse would go dark.
In Bred Electrical Worker
Old 05-22-2020, 04:30 PM   #6
QMED's Avatar
Rewards Points: 310
Did anybody check to see what the main tripped on before resetting the breaker? I'm assuming GFP. I always had problems for one reason or another when doing GFP testing verifying single point grounds.
What type of ground fault protection circuit is it out of curiosity?
QMED is offline   Reply With Quote