Old 12-08-2018, 09:28 PM   #21
Rewards Points: 84
Originally Posted by 847Videos View Post
He has the nameplate info available
I agree with everything else
The nameplate amps is only used for sizing overloads. Use the tables for wire size and overcurrent protection.
Mulder is offline   Reply With Quote
Old 12-08-2018, 09:34 PM   #22
847Videos's Avatar
Rewards Points: 96
Default Breaker and wire size help
I would design the circuit for the specified load looking at the nameplate. Because thatís the load Iím trying to serve.
But common sense says, design the circuit with whatever wonít cause it to burn and have us looking like a holes...
Maybe design it off the charts and pick the better of the two.... The NEC is meant to be minimal standards... Therefore I agree with you.
#8 or #6
Iíd go with a #6 for better heat dissipation
Overload values off the name plate, because the goal/interest here is to protect the motor.
Breaker is short ckt protection for the feeders, and able to take the lock rotor amps at start up...
Grounding is very important on motors as well as the unit vibrates and if anything gets wacky, we want the breaker to trip.
Still think, compressors should be 3 phase if the property has it
847Videos is offline   Reply With Quote
Old 12-08-2018, 09:42 PM   #23
Cow
Rewards Points: 4,532
Read 430.6(A)1 in regards to wire and breaker sizing.
Switched likes this.
Old 12-08-2018, 09:53 PM   #24
WronGun's Avatar
Rewards Points: 646
After reading the article and other posts on this subject Iíve found a dozen different answers....
Old 12-08-2018, 09:54 PM   #25
847Videos's Avatar
Rewards Points: 96
Respect where respect is due...
1,000% Correct.
Exactly how this is done.
And just for that, I'm going to revisit Article 430 myself as it never hurts to invest in our trade.
"Other than for motors built for low speeds (less than 1200 RPM) or high torques, and for mul- tispeed motors, the values given in Table 430.247, Table 430.248, Table 430.249, and Table 430.250 shall be used to determine the ampacity of conductors or ampere ratings of switches, branch-circuit short-circuit and ground-fault pro- tection, instead of the actual current rating marked on the motor nameplate."
Old 12-08-2018, 09:55 PM   #26
Switched's Avatar
Rewards Points: 8,856
This is a confusing section for those of us that don't work with it everyday. I don't quite understand all of it either, but the explanations here make sense.
Old 12-08-2018, 09:56 PM   #27
847Videos's Avatar
Rewards Points: 96
Read the code, everything else is just an opinion...
Back it up your design with article numbers
Old 12-08-2018, 09:58 PM   #28
cabletie's Avatar
Rewards Points: 1,274
Nope only one answer. Cowís is correct.
HackWork and 847Videos like this.
Old 12-08-2018, 09:59 PM   #29
847Videos's Avatar
Rewards Points: 96
I second that, Cow is correct.
Verify with the article numbers he provided
Old 12-08-2018, 10:00 PM   #30
Switched's Avatar
So... Can I go back and edit my incorrect post? lol
847Videos likes this.
Old 12-08-2018, 10:00 PM   #31
WronGun's Avatar
Rewards Points: 646
Sure #6 on a 60 would work , but it seems #8 on a 50 would Also be acceptable.
Yes itís true I donít work on this Everyday , the nameplates Iíve used for installations in the past offered more information. Min and max breaker size , fla, etc.etc. Iíve never had to dig very deep.
Old 12-08-2018, 10:03 PM   #32
847Videos's Avatar
Rewards Points: 96
I've always used Name Plate
I have a digital copy of the code book
And from now on, I'll bring it up on my phone and design the everything except the heaters off the charts just like the code specifies....
Good time we bust out and knock the dust off our code books hu... lol
Old 12-08-2018, 10:04 PM   #33
Switched's Avatar
I thought 8 on a 50 would work, because I incorrectly thought we could use the nameplate FLA to size the breaker. The section @Cow mentioned though shows I was wrong.
Old 12-08-2018, 10:14 PM   #34
cabletie's Avatar
Iím glad I wasnít the first one in. I didnít have the time to respond when I first read it. When I did the math on a calculator I came up with #8 on a 100amp breaker. But I used 230 volts. You canít see the tables when your using an app like ElectriCalc
When I saw Cowís response I opened up the table to see the different columns. I though 230v covered it down to 208v.
Old 12-08-2018, 10:16 PM   #35
WronGun's Avatar
Rewards Points: 646
Well this has been a great lesson on motors...
Good news is I can use the existing 3/4Ē emt
Old 12-08-2018, 10:19 PM   #36
Modťrateur
Rewards Points: 16,780
It is and you will run into central air conditing system ., same way with motors as you will review art 430 and art 440 from time to time to remind yourself on the numbers.
Old 12-08-2018, 10:22 PM   #37
WronGun's Avatar
Rewards Points: 646
Im sure i will.
The last few rtuís i did had everything laid out the on plate including conductor sizes.
frenchelectrican likes this.
Old 12-09-2018, 06:58 AM   #38
Rewards Points: 3,720
Correct me if I am wrong, here is how I figure...
The HP field is 7.5, simple enough. The AMPS field on this nameplate is 31, that's the FLA, but that's not the FLC. Already confusing.
FLC is not found on the nameplate, you find the FLC for the HP in the table. (In this case, 430.28 for single phase AC motors.) The tables account for power factor and efficiency.
Wire size for CCC's is based on the FLC. (If the load is continuous, the 80% rule / 1.25 multiplier applies as usual.)
The OCPD size can exceed the usual max, the max OCPD allowed is calculated from FLC and a multiplier from 430.52. The lookup in 430.52 depends on the type of motor. (I am not clear other than consulting the manufacturer how you walk up to a motor and know which type it is.)
Overloads may be built into the starter or dual element fuses in the disconnect. Overloads are sized from FLA and a multiplier per 430.32. For motors > 1hp, the multiplier is
* 1.25 for motors with SF > 1.15, OR, temperature rise 40įC or less
* 1.15 otherwise
SF is clearly marked on the nameplate, not sure about temperature rise.
To NEMA and NEC, it would be super, super helpful if you f***ing f***s could use the EXACT SAME TERMS AND LABELS.
Old 12-09-2018, 07:03 AM   #39
Rewards Points: 421
I am glad that some of you got it, because I don't have a clue what is going on.
Old 12-09-2018, 07:22 AM   #40
WronGun's Avatar
Rewards Points: 646
Ok ... I feel a little better now knowing my head isnít the only one that is spinning.
Is this Electrician correct on wire sizing? grover1134 General Electrical Discussion 10 11-05-2018 07:15 PM
Heating Loads and Wire Size darren79 Canadian Electrical Forum 2 01-20-2017 07:33 PM
60 amp double pull breaker on 12, 14 gauge wire. Gamble Residential Electrical Forum 7 09-24-2016 05:35 PM
Is this overkill? MTW NEC Code Forum 81 03-20-2016 09:26 PM
Help with this a/c breaker sizing TechieBecky Canadian Electrical Forum 73 02-27-2016 06:26 PM