Breaker and wire size help - Page 4 - Electrician Talk - Professional Electrical Contractors Forum
Like Tree33Likes
Old 12-09-2018, 02:26 PM   #61
Band Member
emtnut's Avatar
Rewards Points: 638
Originally Posted by Cow View Post
I disagree, that's not what the article I posted says.
Interesting. Under CEC, motor data trumps the tables.
For your NEC, would exception #3 not apply here (under 430.6) ?
Old 12-09-2018, 03:14 PM   #62
WronGun's Avatar
Rewards Points: 644
Default Breaker and wire size help
Today I went to the building where I got to enter the neighbors adjacent unit who has the same identical compressor unit. (Which is the reason he bought his)
Installed with 10awg thhn on a 40A breaker, itís been running now for a year. Not sure if the installer was the same.
This now becomes hard for me to explain if I need to run all new pipe , wires , etc.
Pipework in these units are about 16í-18í high , 80í from panel, so its a bit of work.
847Videos likes this.
Old 12-09-2018, 03:21 PM   #63
847Videos's Avatar
Rewards Points: 96
Iíd design and install it based on the national electrical code, the Chicago code says you take ownership of what you install, so if something happens, and you find yourself in court having to justify what you did, the ďNieghborĒ hired an untrained handy man so I copied his design wonít fly
847Videos is offline   Reply With Quote
Old 12-09-2018, 03:27 PM   #64
Rewards Points: 6,625
Originally Posted by WronGun View Post
After reading the article and other posts on this subject Iíve found a dozen different answers....
That seems to be the standard in this trade. Get 10 electricians together, and get 10 different ways to do the exact same thing.
micromind and jelhill like this.
Old 12-09-2018, 03:32 PM   #65
847Videos's Avatar
Rewards Points: 96
Look at the thread, @Cow laid it out correctly
Old 12-09-2018, 03:42 PM   #66
So just for my own curiosity, did you put an amprobe on the circuit? How about a voltage reading at the load? My point being, you've got approx. 112' from the panel, what's the V/D?
Old 12-10-2018, 12:04 AM   #67
Rewards Points: 2,426
Just because it works doesn't mean it's code compliant.
On the other hand, because this installation works, it casts serious doubt on the validity of the code.......
splatz and Kevin_Essiambre like this.
Old 12-10-2018, 05:31 AM   #68
Rewards Points: 3,376
Very true. I also don't assume because it worked for someone, sometime, it will work for me, today. Motors are not perfect, it might work for that one but not another.
If you do it to the letter / by the numbers, then if there's an issue it's not on you.
micromind likes this.
Old 12-10-2018, 05:54 AM   #69
WronGun's Avatar
Rewards Points: 644
I agree, and thatís what Iím going to price it out for , but technically what can happen?
At the panel itís Protected by a 30a breaker and right before the starter itís Protected by a 30a fused disco.
The worst that can happen? it trips...2 points of protection would need to fail..... just sayin....
Old 12-10-2018, 06:11 AM   #70
Elderly Member
jelhill's Avatar
Rewards Points: 1,090
We tested it today and it only trips as it get closer to full fill
Iím curious... did you have an amp meter on the #10 feeder (line side) when you were doing you start-up tests? What actual readings were you getting? Use the stop button on the meter and record 2 or 3 tries. In addition to you being under-sized with the #10 and 30/2 breaker.... you may have a weak breaker.
jelhill is offline   Reply With Quote
Old 12-10-2018, 06:13 AM   #71
Rewards Points: 880
just adjust the pressure switch down by 20 psi and call it good to go.
Less psi = less load = less amps
Old 12-10-2018, 06:29 AM   #72
Elderly Member
jelhill's Avatar
Good point... I wonder if the customer even has a specific PSI requirement.
Old 12-10-2018, 06:42 AM   #73
WronGun's Avatar
Rewards Points: 644
Itís a very small excavation company , they are just using this to maintain the fleet
Old 12-10-2018, 09:51 AM   #74
Elderly Member
jelhill's Avatar
Then @gpop is right... try adjusting the pressure regulator.
Old 12-10-2018, 10:05 AM   #75
Elderly Member
jelhill's Avatar
Thumbs up
I am a licensed electrician. Didnít know that the electrical license means you know every possible thing in the trade. ...
This is in an industrial setting as I stated 208V
I havenít installed anything yet just checking before i do anything.
I donít have much experience hooking up compressors. The owner who is my client just took the old compressor feeds and popped them into the new compressor which has all the same specs on name plate and now called me in because itís tripping.
Both the old and new compressor have built in motor staters with a terminal for L1, L2, and ground...
You asked a very legitimate question, just look at all the (Positive) responses you got.
Old 12-10-2018, 11:29 AM   #76
Vacated
Wiresmith's Avatar
Rewards Points: 2,840
i don't have my code book with me but vfds require i think 125% wire ampacity of the vfd rating, and often you use a larger vfd than the motor for several reasons. i think in the code book in motor section it is under something like motor controlling equipment or something like that.
also the new motor may be tripping because its a different efficiency motor than the last. sounds like it had wrong wiring before though, just offering of why same spec motor and now it trips. ratings only mean so much, take current readings on the similar compressor that's running. it says right on it 31 amps.
Think like a man of action, act like a man of thought. ~Henri Louis Bergson
Old 12-10-2018, 12:00 PM   #77
sbrn33's Avatar
Rewards Points: 3,198
This is a #8 on a 60 amp breaker all day long. I know you like to run with it on this site but just do it right and be done.
I know you know what you are doing, but in this thread you definitely do not sound like it. You sound like a mechanic that just keeps replacing parts until it works. Hard to make money that way.
Old 12-10-2018, 05:28 PM   #78
Modťrateur
Rewards Points: 16,698
I agree with Sbrn and he did bring up couple very good points reguarding of the set up.
If I were you .,, I would rip the #10 chit out and run in correct size conductor and correct breaker size and be done with it and not have to worry about callback or other issue.
#10 on 208 with 30ish amp and ya are pushing the limit on voltage drop those compressor motor dont like too low a voltage so be aware of it.
Old 12-10-2018, 06:25 PM   #79
460 Delta's Avatar
Rewards Points: 562
If they have 208 VAC, I wonder why they didn't order a 3 phase motor? Is this by chance the same place that had the issue with smoking the Siemens starters?
Old 12-10-2018, 06:36 PM   #80
WronGun's Avatar
Rewards Points: 644
If they had reached out to me first , I wouldíve advised them to go with 3-phase...
Same industrial building , different tenant.
We replaced the starter on that job and also a new 3-phase compressor, all good.
I dont know why people insist on keeping these pieces of equipment that date back to the 40ís
weíve been replacing some of the tenants really old compressors, all have been 3-phase.
All the 3-phase units were installed correctly. These couple of single phase units are cutting it too close.
Is this Electrician correct on wire sizing? grover1134 General Electrical Discussion 10 11-05-2018 07:15 PM
Heating Loads and Wire Size darren79 Canadian Electrical Forum 2 01-20-2017 07:33 PM
60 amp double pull breaker on 12, 14 gauge wire. Gamble Residential Electrical Forum 7 09-24-2016 05:35 PM
Is this overkill? MTW NEC Code Forum 81 03-20-2016 09:26 PM
Help with this a/c breaker sizing TechieBecky Canadian Electrical Forum 73 02-27-2016 06:26 PM