I replaced 10 2X2 Fluorescent troffers with LED troffers. The LED troffers flicker while the compressor is running.
Details:
1. Flickering occurs during the entire time the compressor is running which may be a duration of 10 minutes.
2. I measured voltage drop at a fixture when the compressor was off and again while it was on. On: 119V. Off 115V
3. Spec on LED troffers says 110V -277V
4. Connected a Variac to one LED fixture and dialed down to 100V. No flicker
5. Customer said flurorescents used to flicker. There was a combination of magnetic and electronic and I'm not sure which were or were not flickering.
6. New LED troffers have 0-10V dimming but this feature is not connected.
7. Compressor and lighting circuit both come from a 208V 3-phase panel. The compressor takes 2 of these legs with a dedicated circuit. The lights share a leg - not a circuit - with the compressor. The lights are on a dedicated circuit.
Elvis is in the building
Old 04-25-2019, 10:55 AM   #2
MikeFL's Avatar
Rewards Points: 844
Can you put the lights on the leg which does not feed the compressor?
How "loaded" is the service?
Did you check all the connections in the lighting circuit back to the panel?
Michael Gookin, President
GPS Timers
(833) GPS-TIME
Old 04-25-2019, 06:15 PM   #3
daveEM's Avatar
Rewards Points: 2,382
I'm not understanding that.
I like perfect.
Old 04-25-2019, 06:19 PM   #4
Beam Me Up Scotty
Kevin_Essiambre's Avatar
Rewards Points: 410
He means that the compressor is on A & B phase, and the lights are also on either A or B phase.
daveEM likes this.
Vote Kevin for Moderator!
The Following User Says Thank You to Kevin_Essiambre For This Useful Post:
swimmer (04-25-2019)
Old 04-25-2019, 06:56 PM   #5
Swimmer
swimmer's Avatar
Rewards Points: 666
Problem occurs when nothing is running except a few computers. Also occurs when portable power tools are run. There was no heavy electrical equipment running while I was on site though I'm sure the customer has jobs that require it.
I'll change the legs the next time I go there
Old 04-25-2019, 08:01 PM   #6
Beam Me Up Scotty
Rewards Points: 410
Be careful just changing the leg that feeds the lights. If there's a common neutral on 3 circuits, you could end up overloading the neutral. You *might* have to move 3 breakers.
Tags
flicker, led, led troffer flicker, troffer
Building wide LED a19 flicker bjt809 Commercial Electrical Forum 15 04-08-2019 03:31 PM
Lights flicker when air compressor runs John M. General Electrical Discussion 15 08-12-2018 01:30 PM
Troffer in residential ceilings Hangry Canadian Electrical Forum 18 03-15-2018 11:01 PM
Frequency Interference Causing Lights to Flicker Vevolicious New Member Introductions 6 07-29-2017 02:49 PM
Lights Flicker when initial power the disposal crum2243 Residential Electrical Forum 1 09-20-2016 02:22 AM