over head serivce! - Electrician Talk - Professional Electrical Contractors Forum
Old 05-18-2011, 10:02 PM   #1
Rewards Points: 288
Default over head serivce!
Hi guys,I have a problem. Im looking for help.I have a 480 3phase 400amp service that comes from a 3pot bank down to a pedestal then underground to a 400amp breaker then it taps off into 4 different tenats.Problem is im looking to add 200amps for a tenant and my inspector is telling me its against code.Because it doesnt come from a padmount utility tranformer.I have done this service before in south florida and for some reason in central florida there saying it cant happen.According to florida building code I can...any suggestions how I can prove that its a legal install?..Thanks again.
knowledge29 is offline   Reply With Quote
Old 05-18-2011, 11:42 PM   #2
Rewards Points: 1,742
Without knowing all of the details, I would guess that the total connected load, with the addition of the fifth tenant, could be too much for the 400 amp service.
Old 05-19-2011, 02:20 PM   #3
Rewards Points: 25
it sounds like you have a 400amp service feeding (4) 100amp tenent service feeds. without knowing the total connected load for the facility it would be hard to determine if you could add in an additional 200amp service/panel load. you would have a better chance of checking with the utility company and see if the transformers that are on the pole and feeders are sized for the additional load. If they are then you might beable to use the tap rule and tap ahead of the 400amp service and feed the 1 tenent with a 300amp service. 100amp originiol service + 200amp new service load.
if you want to determine the total connected load then you can either get a recording meter and mesure the actual usage over a 30 day period or contact the utility and get a historical KVA usage for the facility.
tgreen is offline   Reply With Quote
Old 05-19-2011, 02:34 PM   #4
Rewards Points: 1,762
I don't think the op is talking about the load but rather the method.
I can't help it if I'm lucky
Old 05-19-2011, 03:04 PM   #5
BBQ
Salty Member
BBQ's Avatar
Depending on the job specifics the inspector may be correct.
Would your job fit exception 1?
2008 NEC
230.40 Number of Service-Entrance Conductor Sets.
Each service drop or lateral shall supply only one set of
service-entrance conductors.
Exception No. 1: A building with more than one occupancy
shall be permitted to have one set of service-entrance conductors
for each service, as defined in 230.2, run to each
occupancy or group of occupancies.
Exception No. 2: Where two to six service disconnecting
means in separate enclosures are grouped at one location
and supply separate loads from one service drop or lateral,
one set of service-entrance conductors shall be permitted to
supply each or several such service equipment enclosures.
Exception No. 3: A single-family dwelling unit and a separate
structure shall be permitted to have one set of serviceentrance
conductors run to each from a single service drop
or lateral.
Exception No. 4: A two-family dwelling or a multifamily
dwelling shall be permitted to have one set of serviceentrance
conductors installed to supply the circuits covered
in 210.25.
Exception No. 5: One set of service-entrance conductors
connected to the supply side of the normal service disconnecting
means shall be permitted to supply each or several
systems covered by 230.82(5) or 230.82(6).
Head Lamps? Fractured Tools, Equipment and New Products 44 02-26-2011 12:38 AM
Whre to buy: Hog Head accessory: MDShunk Tools, Equipment and New Products 3 04-12-2010 04:42 PM
Greetings from cheese head country! gmitts New Member Introductions 5 01-13-2010 05:57 PM
ceiling fan near a sprinkler head SuperRick General Electrical Discussion 23 07-20-2009 02:31 AM
US Plug Head. frank General Electrical Discussion 2 01-25-2009 05:27 PM