Default 3 pole disconnect for single phase?
I have a really nice non-fusible ferraz shawmut disconnect that Ive have stored for a while. Its a 3 phase motor disconnect rated for 60 amps but id like to use it for a 2 pole car charger single phase. Id essentially be using only 2 of the 3 terminals. Is this code compliant?
Navyguy and splatz like this.
Old 06-06-2019, 11:53 PM   #2
Beam Me Up Scotty
Kevin_Essiambre's Avatar
Rewards Points: 134
I personally don't see an issue with it. It opens all the ungrounded conductors.
splatz and Incognito like this.
Old 06-07-2019, 12:08 AM   #3
Cow
Rewards Points: 4,404
More often than not, I can get a 3p disconnect cheaper and faster than a 2p, so a 3p gets used.
It gets done all the time.
Southeast Power (06-07-2019)
Old 06-07-2019, 12:18 AM   #4
Rewards Points: 6,463
I've seen it done quite often. As long as it opens all the energized conductors it could be a 2-pole toggle switch (depending) for all that matters.
Old 06-07-2019, 06:50 AM   #5
CoolWill's Avatar
Rewards Points: 906
Many 3 pole disconnects say in the instructions that when using them on single phase, use the two outer poles.
I'm With Her! Hillary 2016
Old 06-07-2019, 10:26 AM   #6
Rewards Points: 110
...and so long as it's an approved disconnect in an approved box.
since it's hard to make out if it is from the photo.
bob_says_hello is offline   Reply With Quote
Old 06-10-2019, 04:51 PM   #7
Rewards Points: 8
As every one else mentioned you should be good to go, however I would be mindful not to land the neutral on the unused terminal. I don't think a Neutral should be broken inside a disconnect.
glen1971 likes this.
NorthernElectricain is offline   Reply With Quote
Old 06-10-2019, 11:48 PM   #8
Rewards Points: 3,560
Me either.. And yet I see it often and for no reason..
Old 06-11-2019, 12:47 AM   #9
Rewards Points: 110
Can go either way. Provided you break all ungrounded conductors at the same time there's no problem also breaking neutral too. It's just not needed.
Some projects preferred it, in the more 3phase systems where you don't trust the neutral being solidy grounded always, but that's more edge cases than a rule.
Incognito likes this.
Old 06-11-2019, 06:14 AM   #10
CoolWill's Avatar
Rewards Points: 906
If you want something truly isolated, that's what you do.
Old 06-11-2019, 07:19 AM   #11
RSE Master Electrician
Incognito's Avatar
Rewards Points: 280
I never open the grounded conductor in a disconnect but, like others have already said, you can.
14-016 Connection of devices
Devices required by this Section shall not be connected in any grounded conductors except where
a) the devices simultaneously or previously disconnect all ungrounded conductors
2018 Ontario Electrical Code
Incognito is online now   Reply With Quote
Old 06-11-2019, 08:41 AM   #12
Cow
We really only break the neutrals when wiring fuel pumps.
That's about the only time we do it.
Old 06-11-2019, 02:50 PM   #13
After I shut the breaker off, I'll have to start disconnecting neutrals in the panel then when I change out a fixture at home then.. (sarcasm).. lol..
Old 06-11-2019, 04:11 PM   #14
CoolWill's Avatar
Rewards Points: 906
Don't you get sassy with me lady!