Old 03-18-2017, 03:15 PM   #1
Rewards Points: 52
Default Canadian limitations on Romex
NEC says 60deg rating max for NMD90. I am wondering if there are any equivalent limitations under the CEC.
As long as the breaker and device is rated (and labeled) at 75deg it is my understanding that we can use the ampacity under the 75deg column in table 2.
of course if it is not labeled, 60 deg max as per 4-006(2)(a)
Specifically running 3c8 romex for a range outlet on a 50amp breaker. (short run volt drop not an issue)
RCSpades is offline   Reply With Quote
Old 03-18-2017, 04:25 PM   #2
Beam Me Up Scotty
Kevin_Essiambre's Avatar
Rewards Points: 156
I've always been taught and told to use 3c #6 for a 50 amp breaker. Anything over 40 amps we use #6.
Just my 2 cents.
electricguy and Byte like this.
Old 03-18-2017, 04:26 PM   #3
Safety Pin Member
PlugsAndLights's Avatar
Rewards Points: 2,880
If it's marked 75 your ok using the 75 column.
I don't have the link handy, but if you search "2015 bcsa el code change
training manual", you'll find excellent examples around p 38. It's pdf
and worth downloading.
P&L
Old 03-18-2017, 04:42 PM   #4
Rewards Points: 2,972
P&L
https://www.safetyauthority.ca/sites...al_v.3.5_0.pdf
PlugsAndLights likes this.
Old 03-18-2017, 05:50 PM   #5
spinninwheels's Avatar
Rewards Points: 1,103
How big is your range? Can't get by with a 40A breaker?
life is a wild adventure or nothing - helen keller
spinninwheels is offline   Reply With Quote
Old 03-18-2017, 11:15 PM   #6
Rewards Points: 52
yeah the safety authority sheet is a good one. thanks. I actually could get by with a 40A I think. Might do it just for the cost savings, but everything looks like the 75deg column is fine under the CEC.
Old 03-19-2017, 03:52 AM   #7
Rewards Points: 66
My understanding as per 4-006 was unless the receptacle and breaker are marked as rated for higher than 60 degrees you're required to use that column. Assuming it's smaller than #1 and sub 100A...
Sent from my SM-G930W8 using Tapatalk
Jmcstevenson is offline   Reply With Quote
Old 03-19-2017, 09:50 AM   #8
Rewards Points: 7,520
Check the temp rating on the receptacle. Most receptacles are NOT marked for termination temp so as per 4-006 we have to use the 60 degree column.
They increased the ampacities in the 60 degree column in 2015 because of this rule.
Old 03-19-2017, 02:28 PM   #9
Rewards Points: 1,018
A chain is only as good as it's weakest link, makes no sense to over rate the wire.
Old 03-22-2017, 08:31 AM   #10
Byte's Avatar
Rewards Points: 934
Isn't NMD90 rated at 90C? Thought that is what the 90 in NMD90 stood for?
Byte is offline   Reply With Quote
Old 03-22-2017, 08:45 AM   #11
Safety Pin Member
Yes, but the new rules focus on the fact that the equipment the wire
attaches too must have an equal or higher rating, otherwise the lowest
rating must be used when it comes to the table temp column. Bit of
a simplification, but that's the gist.
See the link given by @electricguy for details.
P&L
spinninwheels likes this.
Old 03-22-2017, 09:57 AM   #12
Safety Pin Member
My receptacles are an in store brand called Vista.
14-30R's, 14-50R's and 6-30R's are all marked AL-CU 75degC.
P&L
Old 03-22-2017, 10:21 AM   #13
Rewards Points: 1,360
Yes. As far as the NEC goes, the 90 degree rating can be used for derating purposes, but the ampacity has to be selected from the 60 degree column.
The Following User Says Thank You to RePhase277 For This Useful Post:
Byte (03-22-2017)
Old 03-22-2017, 01:36 PM   #14
Just to make it a little more confusing, 4-006 only applies to the first 1.2 meters of wire connected to breaker, fuse or equipment. Wire ran from j-box to j-box can be rated at it's rated temp. 4-006(4)
Byte (03-22-2017)
Old 03-22-2017, 02:22 PM   #15
They are asking many questions on this code in the new 2015 C of Q test. Some questions say "connected to a breaker" but don't specify temp, some questions say "Connected to equip rated at 75 degrees, and some questions say "wire ran from j-box to j-box".
Old 03-22-2017, 11:58 PM   #16
Byte's Avatar
Rewards Points: 934
In some ways I am happy to be retired...not just tired
electricguy likes this.
Romex in Channel : Wood Cabinet onilozay General Electrical Discussion 11 12-28-2016 04:29 AM
Romex in conduit Incubus311 General Electrical Discussion 38 12-27-2016 06:16 PM
Romex in PVC ben franklin General Electrical Discussion 135 07-31-2016 08:59 PM