Is this a code compliant install? - Electrician Talk - Professional Electrical Contractors Forum
Like Tree9Likes
  • 5 Post By Kevin_Essiambre
  • 2 Post By B-Nabs
  • 2 Post By Funksparky
Old 05-13-2019, 11:53 AM   #1
Rewards Points: 238
Default Is this a code compliant install?
Using teck90 copper indoors from the main panel to the garage into the back of a 6x6 box. From the box use EMT about 10-12 feet to a car charger receptacle but not splicing in the box. I want to just remove the Teck casing and casing around the conductors and push the wires through the conduit.
I know that if the T90 wires within the Teck are not labelled, it may be an issue with inspection. I could use a plastic box to avoid using a bonding lug.
What say you all?
newbie44 is offline   Reply With Quote
Old 05-13-2019, 01:18 PM   #2
Beam Me Up Scotty
Kevin_Essiambre's Avatar
Rewards Points: 198
Why not just teck cable all the way?
Old 05-13-2019, 09:39 PM   #3
Rewards Points: 3,884
What say you all?
Teck has XLPE RW90 insulation on the wires. What labels are you thinking of? The neutral being identified? Use a piece of heat shrink on both ends, just don't cover up all of the ratings on the wire itself. I've taken miles of armour off and ran the wires inside a piece of pipe, such as some lighting, and I've never had any issues..
Are you concerned with mechanical protection? Run a piece of rigid and run the teck through it?
Old 05-14-2019, 02:33 AM   #4
Watt Pusher
B-Nabs's Avatar
Rewards Points: 468
You're not supposed to strip cable and run the conductors in place of building wire if those inner conductors don't have markings on them indicating voltage & temperature etc, however if you're just stripping part of a cable to continue it in a raceway without a splice, I've never heard of there being an issue with it.
glen1971 and Kevin_Essiambre like this.
Old 05-16-2019, 03:08 AM   #5
Conductor Protector
Funksparky's Avatar
Rewards Points: 52
Sometimes coming through a wall and then turning could look pretty ugly with teck or ACWU. I have used a box, come through the back and then stripped off enough armour to continue down a pipe a ways with no issues. I think it’s fine but I have spliced the bare bonding conductor onto a piece of green RW90.
Funksparky is offline   Reply With Quote
Old 05-17-2019, 11:40 PM   #6
Rewards Points: 152
Yes, this installation is code compliant. There should be no issue with stripping the Teck, entering into a box and running the bare bonding conductor to your receptacle provided you wrap the ground screw on your 6X6,or whatever.
I did a feeder for a house from a garage pretty much this exact same way with no issue. I had to bring the Teck90 through a LB after it came of the ground so it would transfer to the house nicely. Duct Seal in the LB which went through to EMT to the panel.
psgama is offline   Reply With Quote
Old 05-18-2019, 12:31 AM   #7
Rewards Points: 12,599
I have run Teck or ACWU through the box without stripping it. I run it through a PVC pipe from underground and through a hole in the back of the box. It’s just cosmetic to make things look nice.
I wouldn’t have a problem stripping it back and pushing it through some EMT, though.
Guys help me please I had to quit a job bc of code bureaucracy maybe there's code aro Math123 NEC Code Forum 40 12-30-2018 02:36 PM
Code Rules Regarding Transformer Wiring Jayc316 NEC Code Forum 1 08-29-2018 08:54 PM