Make sure you install the panel horizontally.
Old 07-14-2019, 12:00 PM   #22
Rewards Points: 26
USEB and a galvanized ground plate at the garage. PVC conduit where exposed. Bends through an LB easy. Done.
Is this allowed anymore? I was under the impression with the revision of Section 10 that outbuildings etc. are no longer allowed to be fed with USEB90 and a ground plate. The only grounding point is at the service entrance, and everything else to be bonded. Because 'equipotentiality'.
Sent from my SM-G960W using Tapatalk
Mobius87 is online now   Reply With Quote
Old 07-14-2019, 12:10 PM   #23
RSE Master Electrician
Incognito's Avatar
Rewards Points: 954
The photo is correct. No longer allowed to install another ground at the outbuilding. Must run a bond with the feed
2018 Canadian Electrical Code
The Following User Says Thank You to Incognito For This Useful Post:
Mobius87 (07-14-2019)
Old 07-14-2019, 12:24 PM   #24
Rewards Points: 12,543
Nice catch. Does that kill triplex too?
Old 07-14-2019, 12:29 PM   #25
Incognito's Avatar
Rewards Points: 954
Will need to run a quadplex and add an insulated bond to it now to meet the new code.
Same method used with the old code if you used overhead to feed a building housing livestock
99cents likes this.
Old 07-14-2019, 12:46 PM   #26
CoolWill's Avatar
Rewards Points: 3,380
Why would you add a bond to quadplex?
I'm With Her! Hillary 2016
Old 07-14-2019, 12:49 PM   #27
Rewards Points: 26
He means you would use one of the insulated conductors as a bonding conductor.
Old 07-14-2019, 12:57 PM   #28
Incognito's Avatar
Rewards Points: 954
Sorry, I meant add an insulated conductor with the triplex (for a neutral) and use the supporting cable as a bond.
Or use quadplex.