hey I am pricing out this hot tub installation. The existing outlet on the garage is closer than 1.5m so I am going to remove it and put a blank plate on it but does the light fixture require gfci protection because its within 10ft of the pool?
newbie44 is offline   Reply With Quote
Old 05-10-2019, 12:27 AM   #2
RSE Master Electrician
Incognito's Avatar
Rewards Points: 954
Yes.
68-000
2) A pool shall be deemed to include
c) spas and hot tubs
68-066
6) Luminaires installed below, or within 3 m of, the pool surface or walls, and not suitably separated from the pool area by a fence, wall, or other permanent barrier, shall be electrically protected by a Class A ground fault circuit interrupter.
newbie44 likes this.
2018 Canadian Electrical Code
Old 05-10-2019, 07:37 AM   #3
Rewards Points: 320
Originally Posted by Incognito View Post
Yes.
68-000
68-066
Thanks! In regards to the outlet being so close (within 4 feet) would it pass if I GFCI it? I'm wondering if there is a rule to allow it because it's existing. There is no other outlet in this yard.
Old 05-10-2019, 07:42 AM   #4
Band Member
emtnut's Avatar
Rewards Points: 2,556
Did you try reading thru sec 68 ? It's a pretty small section !
If that's the only receptacle out there and you remove it, that wouldn't be good
Old 05-10-2019, 07:49 AM   #5
Rewards Points: 320
Thanks. I did read through it thoroughly, just thought maybe there was some bulletin allowing existing to stay. I think I need to remove or cap this existing one and I price to add one 10 or more feet away.
Old 05-10-2019, 07:54 AM   #6
Band Member
emtnut's Avatar
That, or have a wall built . No exceptions that I'm aware of.
newbie44 and Kevin_Essiambre like this.
newbie44 (05-10-2019)
Old 05-10-2019, 07:58 AM   #7
Rewards Points: 320
This really sucks for the homeowner because the garage was fed with nmwu 14/3. In order to gfci the light at the panel, i'm going to need a double pole gfci breaker! Honestly, the hot tub guys should have made the client aware of this issue. They do this everyday!
Old 05-10-2019, 09:47 AM   #8
Beam Me Up Scotty
Kevin_Essiambre's Avatar
Rewards Points: 470
If you can get them to move the hot tub a few feet, that would be the best soloutuon to the receptacle issue.
Vote Kevin for Moderator!
Old 05-10-2019, 01:02 PM   #9
Rewards Points: 3,096
  1. Quote:
They are more interested in their 4000.00 sale and leave it up the the Electrical contractor to tell the customer
RRF likes this.
Old 05-10-2019, 10:06 PM   #10
Dope-less Hope Fiend
Rewards Points: 824
Can you install a GFCI outlet between the switch and the fixture?
Give me your tired, your poor, your huddled masses yearning to breathe free, the wretched refuse of your teeming shore. Send these, the homeless, tempest-tossed to me, I lift my lamp beside the golden door!
Dan the electricman is offline   Reply With Quote
Old 05-11-2019, 08:29 AM   #11
Sentimental Mental
CTshockhazard's Avatar
Rewards Points: 1,716
They will often even go so far as to say that the electrical should "only be a few hundred"
I hate to see her go, but I sure love watching her walk away.
Isolated Ground Devices Eestrada94 General Electrical Discussion 16 02-07-2018 08:53 AM
i need help experience of pond pumps, or of solar powered devices? hantrongtai1 General Electrical Discussion 4 07-30-2017 09:49 AM
Contacts of control devices (HW) JasonCo General Electrical Discussion 15 10-22-2016 03:54 PM
Wiring devices for aluminum wiring. NitroTurkey Residential Electrical Forum 5 03-20-2016 06:36 PM
stocking devices joebeadg Residential Electrical Forum 31 02-20-2016 08:00 PM