Originally Posted by HertzHound View Post
Originally Posted by Incognito View Post
@HertzHound, that’️s not the way I read it. 300.20(b) is referring to single conductors, not conductors of a multiwire cable.
The NEC is confusing. 300.3(b)(3) Say's it's allowed as long as 300.20(b) is followed. Yes 300.20(b) is for single conductors but it's 300.3(b)(3) that got you there.
(3)Nonferrous Wiring Methods.
Conductors in wiring methods with a nonmetallic or other nonmagnetic sheath, where run in different raceways, auxiliary gutters, cable trays, trenches, cables, or cords, shall comply with the provisions of 300.20(B).
I disagree. Those rules and exceptions are not meant to be used when running multi-wire cables, they are for single conductor. The CEC also has similar codes for when doing that.
@Dennis Alwon, what is your interpretation of these NEC articles? Can a circuit be split up into different multi wire cables for three way switching and are the NEC articles posted allowing it?
2018 Canadian Electrical Code
Old 06-29-2019, 08:46 PM   #22
HertzHound's Avatar
Rewards Points: 1,166
Maybe we can get Cricket to throw in an ET mug to to the correct interpretation?
“Why say lot words when few words do trick”
Old 06-29-2019, 08:52 PM   #23
Incognito's Avatar
Rewards Points: 954
Maybe we can get Cricket to throw in an ET mug to to the correct interpretation? [IMG class=inlineimg]https://www.electriciantalk.com/images/smilies/vs_OMG.gif[/IMG]
No one told me there are ET mugs!!!
CoolWill and HertzHound like this.
Old 06-29-2019, 09:45 PM   #24
Rewards Points: 21,868
So who sells 14/4 loomex?
I dont know about your area ever sell 14/4 verison loomex .,,
but I know in USA and my country they can get it pretty easy if you know where to get it. some of the big box store still carry it but cost more than just run of mill 14/3 verison is.
sometime you need a lead time if you know you will use it a bit.
Now to answer other question .,,
can run pair of NM ( loomex ) cables to the switch box or lumainaire box ?.
Yes it done pretty often in old days before the XX/3 NM or loomex is common but you really have to watch how it connected cuz there is not much clue to give out so pay attention to the travelers.
I think Dennis will agree with me with old set up. but currentaly it kinda super rare unless special situation arise.
Old 06-30-2019, 08:57 AM   #25
Incognito's Avatar
Rewards Points: 954
Of course it was done in the past before 3 wire was around. Knob and tube is still seen in older houses today but that does not mean we can wire receptacles and switches with single conductors today.
New installations must follow new code and in Canada, all conductors of a circuit (if using multi conductor cable) must be in the same cable. 12-106(1)
frenchelectrican likes this.
Old 06-30-2019, 03:23 PM   #26
Bird dog's Avatar
Rewards Points: 764
Mugs & Tee shirts.
https://www.electriciantalk.com/f17/...0/#post5104732
Mug
Shirt
Kevin_Essiambre likes this.
Old 06-30-2019, 08:17 PM   #27
Can't Remember
Rewards Points: 380
I’d buy a mug if it was available.
Old 06-30-2019, 09:50 PM   #28
HertzHound's Avatar
Maybe they can get the logo on a 20oz Yeti tumbler. Id buy some of those.
Old 07-02-2019, 11:41 PM   #29
joe-nwt's Avatar
Rewards Points: 1,000
Run a 2-wire to the first box and then to the second. That will give you a neutral in each box to satisfy the neutral requirement. Then a 3-wire between the same two boxes will give you two travellers and a switch return or a hot and 2 travellers depending on where you start your switching from.
From where you end your switching, a 2-wire to your load. Or 3 if you want to take the hot.
Or use 4 wire BX.
Old 07-03-2019, 01:08 AM   #30
Beam Me Up Scotty
Kevin_Essiambre's Avatar
Rewards Points: 250
Heck I'd like to just get the logo to print on stuff.
Old 07-03-2019, 09:05 AM   #31
Incognito's Avatar
Rewards Points: 954
Or use 4 wire BX.
You can not run separate wires. All the wires for a circuit must be contained in the same multi conductor cable. 12-106(1)
Navyguy likes this.
Old 07-03-2019, 09:26 AM   #32
Rewards Points: 1,654
Yes, the nec does allow this install as long as it is nm cable. I have tried to get it changed but the nec panel does not care about electromagnetic field's.
Of course the easiest install is using 3 wire cable between the switches and then feed one 3 way and switch leg from the other
I can't help it if I'm lucky
Old 07-03-2019, 09:35 AM   #33
Incognito's Avatar
Rewards Points: 954
I still disagree. The exemptions and codes from the NEC posted are clearly for single conductor cables.
If not, does that mean you have to cut the metal between the holes where the wire enters in the switch box as per 300.20(b) ? Seriously? This is an actual practice done in residential? Seems silly as that is really only required for currents over 200 amps which is why the rule is meant for single conductors, not nm cable.
Old 07-03-2019, 09:40 AM   #34
Rewards Points: 2,031
We use plastic boxes.
Old 07-03-2019, 09:42 AM   #35
CoolWill's Avatar
Rewards Points: 3,936
The only reason the code allows it is so that existing installs are left alone. Some inspectors love to see a new code and demand that old stuff be ripped out, so I think this was put in to prevent that.
But no real electrician would do it.
Incognito likes this.
Old 07-03-2019, 09:56 AM   #36
Incognito's Avatar
Rewards Points: 954
We can’t even use plastic straws!!!
Our code does not allow it regardless of type of box. It just seems wrong to me as this is basic stuff taught to us from first year.
Old 07-03-2019, 11:03 AM   #37
Rewards Points: 13,463
Here’s what I was really asking with my dumb question:
It’s Saturday and I don’t want to pay HD price for 3 wire. Is it okay if I cheat?
Old 07-03-2019, 11:25 AM   #38
Yes, you would if you used metal boxes. Very rarely do we encounter this...
You can disagree but you would be wrong as this was brought up at a large code meeting and it was stated as a compliant install. It used to be done alot years ago but not so much anymore.
Old 07-03-2019, 11:26 AM   #39
I agree it does seem wrong and I will never do it however it is compliant.
Old 07-03-2019, 12:34 PM   #40
Rewards Points: 17,721
What I wanna know is why would anybody wanna put in a proposal to reduce a possible method of wiring that might come in super handy one day when you are in a pinch someplace? Just because it isn't used nowadays? Afraid of radio waves while bathing in them all day long from your iPhone and wireless routers? Because real electricians use 14-3? ( and here I hear all the time real electricians don't run nm cable at all.......). So why would anybody submit a proposal to have the practice removed from the Code? Why?
Bragging rights at Mikeholt.com is why..................
JOBS GROWTH SOARS