Default Emergency and exit lighting, Canada

I have two restaurants starting, small places with a few tables, mostly take out. The last one I did had exits and emergencies on the drawings. This time they have been left out.

I am not sure of building code requirements. I read somewhere that they are required for an occupancy load over 60.

Help.
99cents is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 01-18-2019, 09:02 AM   #2
Senior Member
 
CoolWill's Avatar
 
Join Date: Jan 2019
Location: SC
Posts: 2,197
Rewards Points: 2,676
Default

Quote:
Originally Posted by 99cents View Post
I have two restaurants starting, small places with a few tables, mostly take out. The last one I did had exits and emergencies on the drawings. This time they have been left out.

I am not sure of building code requirements. I read somewhere that they are required for an occupancy load over 60.

Help.
Isn't this something you could eyeball? I mean, you know where the exits are, you know where the bathrooms are, you know where the hallways are, etc.
Kevin_Essiambre likes this.
CoolWill is offline   Reply With Quote
Old 01-18-2019, 09:29 AM   #3
:-)
 
daveEM's Avatar
 
Join Date: Nov 2012
Location: Alberta
Posts: 3,670
Rewards Points: 2,382
Default

Have a look...

chrome-extension://oemmndcbldboiebfnladdacbdfmadadm/http://www.tnb.ca/en/brands/lumacell/files/3LU_Building_Code_EN.pdf

^^ weird link but seems to work for me.

I use the Brave Browser which is built on Chrome but has all the filthy Google stuff snuffed out.

Also use DuckDuckGo for the search engine which has all the Google filthy stuff snuffed out.

Liking it.
__________________
<<
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


I like perfect.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Last edited by daveEM; 01-18-2019 at 09:38 AM.
daveEM is offline   Reply With Quote
Sponsored Links
Advertisement
 
Old 01-18-2019, 09:43 AM   #4
Senior Member
 
CoolWill's Avatar
 
Join Date: Jan 2019
Location: SC
Posts: 2,197
Rewards Points: 2,676
Default

Quote:
Originally Posted by daveEM View Post
Have a look...

chrome-extension://oemmndcbldboiebfnladdacbdfmadadm/http://www.tnb.ca/en/brands/lumacell/files/3LU_Building_Code_EN.pdf

^^ weird link but seems to work for me.

I use the Brave Browser which is built on Chrome but has all the filthy Google stuff snuffed out.

Also use DuckDuckGo for the search engine which has all the Google filthy stuff snuffed out.

Liking it.
So, skimming through that, I didn't see mention of emergency lighting for restrooms. Is that not something you do in Canada? We don't require it everywhere here either. It varies from jurisdiction to jurisdiction. Usually a fire code.
CoolWill is offline   Reply With Quote
Old 01-18-2019, 09:58 AM   #5
Hackenschmidt
 
splatz's Avatar
 
Join Date: May 2015
Location: Parts Unknown
Posts: 8,507
Rewards Points: 4,412
Default

Quote:
Originally Posted by CoolWill View Post
So, skimming through that, I didn't see mention of emergency lighting for restrooms. Is that not something you do in Canada? We don't require it everywhere here either. It varies from jurisdiction to jurisdiction. Usually a fire code.
So in Canada, if you don't know enough to get out of the bathroom if the building's on fire, it's f. you, burn motherf'er?

I am all right with that, but they say Canadians are so nice, I think once you scratch the surface, they're pretty ****ing hostile.
CoolWill likes this.
__________________
Everything Should Be Made as Simple as Possible, But Not Simpler
splatz is online now   Reply With Quote
Old 01-18-2019, 10:00 AM   #6
Hackenschmidt
 
splatz's Avatar
 
Join Date: May 2015
Location: Parts Unknown
Posts: 8,507
Rewards Points: 4,412
Default

Quote:
Originally Posted by daveEM View Post
I use the Brave Browser which is built on Chrome but has all the filthy Google stuff snuffed out.
That is the opposite of a brave browser. They should call it Scaredy Browser.
__________________
Everything Should Be Made as Simple as Possible, But Not Simpler
splatz is online now   Reply With Quote
Old 01-18-2019, 10:19 AM   #7
Senior Member
 
Wardenclyffe's Avatar
 
Join Date: Jan 2019
Location: Georgia
Posts: 158
Rewards Points: 328
Default

Quote:
Originally Posted by splatz View Post
So in Canada, if you don't know enough to get out of the bathroom if the building's on fire, it's f. you, burn motherf'er?

I am all right with that, but they say Canadians are so nice, I think once you scratch the surface, they're pretty ****ing hostile.


Or like the Exchange rate,


.75 x The Exits in the States,...
Wardenclyffe is online now   Reply With Quote
Old 01-18-2019, 10:28 AM   #8
:-)
 
daveEM's Avatar
 
Join Date: Nov 2012
Location: Alberta
Posts: 3,670
Rewards Points: 2,382
Default

Quote:
Originally Posted by CoolWill View Post
So, skimming through that, I didn't see mention of emergency lighting for restrooms. Is that not something you do in Canada? We don't require it everywhere here either. It varies from jurisdiction to jurisdiction. Usually a fire code.
Yeah it doesn't seem to list them. We light em up tho. At least the larger ones I've been in.
CoolWill likes this.
__________________
<<
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


I like perfect.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
daveEM is offline   Reply With Quote
Old 01-18-2019, 11:52 AM   #9
Senior Member
 
Join Date: Aug 2018
Location: Manitoba, Canada
Posts: 129
Rewards Points: 4
Default

Who made the drawings? Was it an engineer or are they on the back of a napkin?
If engineered drawings confirm with them. May end up being a nice little extra for you...

Last edited by Kawicrash; 01-18-2019 at 11:59 AM.
Kawicrash is offline   Reply With Quote
Old 01-18-2019, 12:11 PM   #10
Band Member
 
emtnut's Avatar
 
Join Date: Mar 2015
Location: Eastern Ontario
Posts: 5,828
Rewards Points: 1,234
Default

Quote:
Originally Posted by splatz View Post
I am all right with that, but they say Canadians are so nice, I think once you scratch the surface, they're pretty ****ing hostile.
I can't speak for all the Canucks, but it doesn't really take much scratching for me
splatz and CoolWill like this.
__________________
_____________________________________
Your Mother was a hamster, and your father smells of Elderberries. ... Now go away, or I shall taunt you a second time
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
emtnut is offline   Reply With Quote
Old 01-18-2019, 07:57 PM   #11
Member
 
908Eng's Avatar
 
Join Date: Oct 2018
Location: Alberta
Posts: 41
Rewards Points: 82
Default

From the NBC (most provincial codes have nearly verbatim clauses, I have the BCBC and ABC if you want a specific reference):

3.2.7.3 Emergency Lighting
1) Emergency lighting shall be provided to an average level of illumination not
less than 10 lx at floor or tread level in
a) exits,
b) principal routes providing access to exit in open floor areas and in service rooms,
c) corridors used by the public,
d) corridors serving sleeping rooms in a treatment occupancy,
e) corridors serving sleeping rooms in a care occupancy, except corridors
serving sleeping rooms within individual suites of care occupancy,
f) corridors serving classrooms,
g) underground walkways,
h) public corridors,
i) floor areas or parts thereof where the public may congregate
i) in Group A, Division 1 occupancies, or
ii) in Group A, Division 2 and 3 occupancies having an occupant
load of 60 or more,
j) floor areas or parts thereof of daycare centres where persons are cared for, and
k) food preparation areas in commercial kitchens.


...

3.4.5.1 Exit Signs
1) Every exit door shall have an exit sign placed over or adjacent to it if the
exit serves
a) a building more than 2 storeys in building height,
b) a building having an occupant load of more than 150, or
c) a room or floor area that has a fire escape as part of a required means of egress.


In general... Emergency lighting is needed everywhere regardless of occupancy / size / etc. Exit lighting is only needed when you have more than 150 people or a 3 storey building or higher.

Hope that helps.

CAVEAT: Information presented in this post does not constitute professional engineering advice.
908Eng is offline   Reply With Quote
Old 01-19-2019, 07:57 AM   #12
Sentimental Mental
 
CTshockhazard's Avatar
 
Join Date: Aug 2009
Location: CT
Posts: 986
Rewards Points: 1,456
Default We are not alone down here.....

Quote:
Originally Posted by 908Eng View Post
From the NBC (most provincial codes have nearly verbatim clauses, I have the BCBC and ABC if you want a specific reference):

3.2.7.3 Emergency Lighting
1) Emergency lighting shall be provided to an average level of illumination not
less than 10 lx at floor or tread level in
a) exits,
b) principal routes providing access to exit in open floor areas and in service rooms,
c) corridors used by the public,
d) corridors serving sleeping rooms in a treatment occupancy,
e) corridors serving sleeping rooms in a care occupancy, except corridors
serving sleeping rooms within individual suites of care occupancy,
f) corridors serving classrooms,
g) underground walkways,
h) public corridors,
i) floor areas or parts thereof where the public may congregate
i) in Group A, Division 1 occupancies, or
ii) in Group A, Division 2 and 3 occupancies having an occupant
load of 60 or more,
j) floor areas or parts thereof of daycare centres where persons are cared for, and
k) food preparation areas in commercial kitchens.


...

3.4.5.1 Exit Signs
1) Every exit door shall have an exit sign placed over or adjacent to it if the
exit serves
a) a building more than 2 storeys in building height,
b) a building having an occupant load of more than 150, or
c) a room or floor area that has a fire escape as part of a required means of egress.


In general... Emergency lighting is needed everywhere regardless of occupancy / size / etc. Exit lighting is only needed when you have more than 150 people or a 3 storey building or higher.

Hope that helps.

CAVEAT: Information presented in this post does not constitute professional engineering advice.



I like funny codes


Who decides which paths are the principle routes?


What's the difference between c(corridors used by the public) and h(public corridors)?


How do you determine where the public may congregate, wouldn't that be everywhere?


Also, looks like you can save a li'l cash as they only require exit signs.


__________________
.
__________________________________________________

Just to be absolutely clear...
I didn't say anything about nothing to nobody.
CTshockhazard is offline   Reply With Quote
Old 01-19-2019, 08:42 AM   #13
Senior Member
 
cabletie's Avatar
 
Join Date: Feb 2011
Location: N.J.
Posts: 1,698
Rewards Points: 1,274
Default

Quote:
Originally Posted by CTshockhazard View Post




I like funny codes [IMG class=inlineimg]https://www.electriciantalk.com/images/smilies/wink.png[/IMG]


Who decides which paths are the principle routes?


What's the difference between c(corridors used by the public) and h(public corridors)?


How do you determine where the public may congregate, wouldn't that be everywhere?


Also, looks like you can save a li'l cash as they only require exit signs.


[IMG class=inlineimg]https://www.electriciantalk.com/images/smilies/vs_smirk.gif[/IMG]
Here the route, the length of the route, and how many people are going to take that route is usually on the life safety plan.
Attached Thumbnails
Emergency and exit lighting, Canada-a21dc12a-9587-44d3-9b7b-28648b981b31_1547905317626.jpg  

cabletie is offline   Reply With Quote
Old 01-19-2019, 08:59 AM   #14
Petulant Amateur
 
99cents's Avatar
 
Join Date: Aug 2012
Location: Perky Nipples, Canada
Posts: 20,756
Rewards Points: 11,879
Default

Still confused. This is a flat rate job. Extras are like pulling teeth. The default answer is “make it to code”. To have emergency lighting and no exits in a small restaurant makes no sense.

Do I need emergency lighting in bathrooms?
99cents is offline   Reply With Quote
Old 01-19-2019, 09:17 AM   #15
Senior Member
 
CoolWill's Avatar
 
Join Date: Jan 2019
Location: SC
Posts: 2,197
Rewards Points: 2,676
Default

Quote:
Originally Posted by 99cents View Post
Still confused. This is a flat rate job. Extras are like pulling teeth. The default answer is “make it to code”. To have emergency lighting and no exits in a small restaurant makes no sense.

Do I need emergency lighting in bathrooms?
I read through that document that Dave posted twice. I saw no mention of bathrooms. Here it is usually a fire code and under the authority of the fire marshal.
99cents likes this.
CoolWill is offline   Reply With Quote
Old 01-19-2019, 10:23 AM   #16
Senior Member
 
Join Date: Aug 2018
Location: Manitoba, Canada
Posts: 129
Rewards Points: 4
Default

Quote:
Originally Posted by 99cents View Post
Still confused. This is a flat rate job. Extras are like pulling teeth. The default answer is “make it to code”. To have emergency lighting and no exits in a small restaurant makes no sense.

Do I need emergency lighting in bathrooms?
What I'll sometimes do is talk to the inspector for that district, or even the chief and ask him. I know them all so that's an advantage, because it's not up to them to tell you how to do things, but if you are nice and friendly they will usually point you in the right direction. If you're off home turf things might be different however.
My brother was a city mechanical inspector for 30+ years, and I know he would often help guys out as long as you weren't an a**hole about it.
Kawicrash is offline   Reply With Quote
Old 01-19-2019, 01:09 PM   #17
Member
 
908Eng's Avatar
 
Join Date: Oct 2018
Location: Alberta
Posts: 41
Rewards Points: 82
Default

All great questions. I still battle with these frequently.

I have stopped trying to understand the reasoning for code rules a long time ago. Trying to figure out the rationale is usually fruitless (ie. public corridors vs corridors used by the public). "Don't try to find logic in stupidity" - unknown!!!

I show emergency remote heads in bathrooms but if there is any push back from the contractor on a fixed budget, I usually cave! I won't update the drawings but I also won't hold up the final occupancy. I can't find any reference that requires emergency light in a bathroom but some building inspectors require them regardless.

In my office, we frequently have projects with emergency lights and no exit signage. If the building already has exit signs, I will usually extend them. If there are exit signs anywhere, they should be everywhere. If half the building has the old red EXIT signage, we usually consult with the building inspector to determine if the new area needs RUNNING MAN or old red EXIT signage to match. Sometimes the building inspector wants the whole building upgraded to green RUNNING MAN.

If I were 99cents, I would recommend installing the economy battery packs in minimal locations until the building inspector is satisfied. Forget the exit lights unless you are in a 3 storey building (or up) or have more than 150 people total.

CAVEAT: Information presented in this post does not constitute professional engineering advice.
908Eng is offline   Reply With Quote
Old 01-19-2019, 02:34 PM   #18
Watt Pusher
 
B-Nabs's Avatar
 
Join Date: Jun 2014
Location: Port Coquitlam, Canada
Posts: 2,189
Rewards Points: 466
Default

As far as I know em lights are not required in bathrooms here, but are often shown on engineered drawings.

Sent from my SM-G920W8 using Tapatalk
__________________
Is that a real poncho or is that a Sears poncho?
B-Nabs is online now   Reply With Quote
Old 01-20-2019, 06:28 PM   #19
Senior Member
 
billyhunter's Avatar
 
Join Date: Mar 2016
Location: Ottawa
Posts: 109
Rewards Points: 218
Default

check with engineer who prepared the permit, it is a simple job, otherwise pretend you know nothing because no drawings from engineer or building permit.
billyhunter is offline   Reply With Quote
Old 01-23-2019, 09:59 PM   #20
cog
 
stuiec's Avatar
 
Join Date: Sep 2010
Location: cana-duh
Posts: 5,173
Rewards Points: 1,174
Default

Quote:
Originally Posted by splatz View Post
So in Canada, if you don't know enough to get out of the bathroom if the building's on fire, it's f. you, burn motherf'er?

I am all right with that, but they say Canadians are so nice, I think once you scratch the surface, they're pretty ****ing hostile.
Well, its a lot easier to be nice when a few of the poindexters that can't find their way out of a one exit bathroom have been burnt off.
splatz likes this.
stuiec is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Phones and Safety splatz Workplace Safety 17 12-09-2018 11:31 PM
Emergency lighting and exits, Canada 99cents Canadian Electrical Forum 14 09-04-2018 06:06 PM
Emergency and Exits fed from Night Lights? Arcflasher Commercial Electrical Forum 10 11-15-2017 08:23 PM
EM lighting Chicagospark General Electrical Discussion 23 06-27-2016 12:01 AM


All times are GMT -4. The time now is 03:32 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com