grounding - Electrician Talk - Professional Electrical Contractors Forum
Old 04-08-2013, 10:32 PM   #1
Default grounding
a 400 amp feed from hydro , 2 seperate 2 inch pvc runs along outside of building, one run feeds 200 amp panel A other run feeds 200 amp panel B ...... 4-3/0 conductors and 1, #3 green ...question is ... what is the proper way to ground the system , there is no water meter in the building.
phill is offline   Reply With Quote
Old 04-08-2013, 10:39 PM   #2
Maple_Syrup25's Avatar
Rewards Points: 780
does the building have steel pounded into the ground?
Maple_Syrup25 is offline   Reply With Quote
Old 04-08-2013, 10:52 PM   #3
you say toss in a ground plate okay great i get that ... my question is do i run seperate ground conductors from each panel to the plate or do i use a ground plate for each panel and seperate ground conductors to each plate??
Old 04-08-2013, 11:07 PM   #4
Rewards Points: 780
ok, how close are these panels A and B, are there disconnects ahead of the panels, do the panels have main breakers? why not 400a wire with splitter etc
Old 04-08-2013, 11:15 PM   #5
400 amp feed by hydro... two seperate meters feeding two seperate 200 amp panels... 2 inch pvc conduit ran outside on the building feed the panels so there is no unfused wire in the building so no switches... panels are 200 amp c/w 200 amp mains.... there is nothing in the CEC detailing how to ground two seperate panels coming from the same source... if there was a water meter i would run a main ground from each panel to the water meter and clamp one ground to the street side and then crimp the other ground to it... so if i pound ground rods does the same principle apply or do i pound ground rods for each panel isolating the grounds ?? lol confused yet ?
Old 04-08-2013, 11:24 PM   #6
Rewards Points: 780
what do you mean when you say unfused wire in building? so where are they fused/protected? I can get a 100% answer for you tomorrow haha i know a guy who got 96% on his c of q, he is a code teacher now!
Old 04-08-2013, 11:28 PM   #7
you are not permitted to run unfused wire inside a building if the panel feeds ran thru the building you would have to add two ,200 amp fused disconnects so running them surface outside the building meets code requirements and conductors feed the 200 amp main in the panels
Old 04-08-2013, 11:36 PM   #8
Rewards Points: 780
i know you cant run more than a few feet inside. you aint answering my questions right, its late i give up sorry man
Old 04-08-2013, 11:42 PM   #9
If the two panel feed separate occupancies in the building, use two ground plates. The grounds for two systems only need to be tied together where they are in the same occupancy. Is that the question?
xlink is offline   Reply With Quote
Old 04-08-2013, 11:47 PM   #10
AlbertaBeef's Avatar
Rewards Points: 554
This sounds a lot like a question for school. What year are you in?
AlbertaBeef is offline   Reply With Quote
Old 04-08-2013, 11:54 PM   #11
I quit counting.
You are right, it looks like a school question. I missed that. Thanks.
Old 04-08-2013, 11:57 PM   #12
i pounded 4 ground rods, 2 for each panel but the inspector says its wrong he wants me to run a bond between the 2 sets of ground rods and in my experience that would create a ground loop ... there is nothing in the cec detailing this ...
Old 04-08-2013, 11:58 PM   #13
my 15th year lolol
The Following User Says Thank You to phill For This Useful Post:
xlink (04-09-2013)
Old 04-09-2013, 12:01 AM   #14
I'm going to stick with my first answer.
Old 04-09-2013, 12:05 AM   #15
If the two panels come from the same service, they share the same neutral so the grounds are tied together.
Old 04-09-2013, 12:06 AM   #16
i agree with you and i did that... inspector says its wrong ... what would you do if there was a water meter in the building?? run two seperate ground conductors to the street side of the meter ...
Old 04-09-2013, 12:14 AM   #17
Yes. Been there done that after discussing with an inspector.
Old 04-09-2013, 12:15 AM   #18
thanks i appreciate your input
Old 04-09-2013, 12:18 AM   #19
FWIW, I've done duplexes with separate ground plates not tied together, too.
Good luck.
Old 04-19-2013, 11:34 PM   #20
Rewards Points: 254
A duplex meter base serving 2 buildings requires one ground system.The main ground goes directly to the neutral bar in the duplex meter base.The neutral is to be only bonded once and that is at the base.Your individual panel bonding is done through separate conductors back to lugs in the meter can.The combination panels should have the neutral bonding screws removed also.
crosport is offline   Reply With Quote
grounding SparkyMcSparkerson General Electrical Discussion 5 02-23-2013 11:03 AM
Grounding Voltech NEC Code Forum 8 10-05-2011 06:50 PM
Grounding Voltech Other Codes and Standards 2 10-04-2011 10:47 PM
Replacing non-grounding receptacles with grounding Gamit General Electrical Discussion 31 01-10-2011 11:34 PM
Grounding jdeihs NEC Code Forum 3 08-24-2008 01:30 AM