Old 07-18-2016, 11:43 PM   #1
Rewards Points: 540
Default how you guys caculate the voltage drop of wire bigger than 4/0?
in the CEC code book , the D3 table for calculate the voltage drop is only up to 4/0, so how you guys calculate the wire bigger than that?
any inputs will be thank you
mike883 is offline   Reply With Quote
Old 07-19-2016, 12:49 AM   #2
Rewards Points: 3,070
The SouthWire App
51360 and Majewski like this.
Old 07-19-2016, 12:57 AM   #3
Rewards Points: 283
Good question. Im thinking.....maybe verify circular mil area of the 4/0....and compare as a ratio of the CMA of the larger cable. Maybe im off track here, ( example )............ but CMA of # 14 is 4110. # 8 awg is approx. 4 times that.....16,510. Not exact, but close enough to compare. If you look at 4amps in both columns....# 14 is 15.3M....and # 8 is 61.7M. Not bang on, but pretty close to 4 X. Does this make sense??
51360 likes this.
Judoka is offline   Reply With Quote
Old 07-19-2016, 07:35 AM   #4
jw0445's Avatar
Rewards Points: 1,952
Use this http://www.elec-toolbox.com/calculators/voltdrop.htm
Majewski likes this.
Old 07-19-2016, 03:15 PM   #5
Rewards Points: 3,090
Originally Posted by electricguy View Post
The SouthWire App
Be careful using apps based on the NEC. Most times you will get what you are looking for, as our code is becoming more like the NEC each cycle, but be sure to read the notes given with the app.
Edit: I couldn't find a Southwire App that used the CEC, I tried a couple. Maybe electric guy can correct me.
Many apps out there that are based on the CEC.
Borgi
emtnut likes this.
Old 07-19-2016, 08:20 PM   #6
Rewards Points: 540
The SouthWire App
thanks, but I don't like this app
Old 07-19-2016, 08:21 PM   #7
Rewards Points: 540
Originally Posted by jw0445 View Post
thanks, but I don't like this either
Old 07-19-2016, 08:21 PM   #8
Rewards Points: 540
no one knows?...................
Old 07-19-2016, 08:55 PM   #9
Band Member
emtnut's Avatar
Rewards Points: 2,492
Did they not teach you about Ω/1000' in trade school
And then Ohm's law from that ?
Majewski and PlugsAndLights like this.
Old 07-19-2016, 09:13 PM   #10
Rewards Points: 540
it doesn't work like that, for DC , you can use I=U/R no problem,
but for AC, you can't
do some research
Old 07-19-2016, 09:23 PM   #11
Band Member
emtnut's Avatar
do some research
Sorry, my bad, ... how many miles of cable are you talking about ... I will include impedance then
Old 07-19-2016, 09:39 PM   #12
billyhunter's Avatar
Rewards Points: 218
I also want to know, but nobody has such question by far.
emtnut and PlugsAndLights like this.
billyhunter is offline   Reply With Quote
Old 07-19-2016, 10:32 PM   #13
Rewards Points: 540
is it not the miles of the cable,
it is the kcmil
see below
how you guys caculate the voltage drop of wire bigger than 4/0?-qq-20160709194817.png
Old 07-19-2016, 10:47 PM   #14
Band Member
emtnut's Avatar
it is the kcmil
see below
And how many miles of cable would it take for that to be significant
Old 07-19-2016, 11:59 PM   #15
You're not far off at all.
Calculating Voltage Drop
In situations where the circuit conductors span large distances, the voltage drop is calculated. If the voltage drop is too great, the circuit conductor must be increased to maintain the current between the points. The calculations for a single-phase circuit and a three-phase circuit differ slightly.
Single-phase voltage drop calculation:
VD = [ 2 x L x R x I ]/1,000
VD% = [ VD/Source Voltage] x 100
Three-phase voltage drop calculation:
VD = [( 2 x L x R x I)/1,000] x .866
Where:
VD = Voltage drop (conductor temp of 75C) in volts
You can find formulas, like above, that you can use. But, good apps, ( you may have to buy them ), can do the math for you. Use an app that allows you to enter as many variables as needed.
For systems using wire sizes above 4/0, you may need to consult an engineered standard.
Borgi
electricguy and Judoka like this.
Old 07-21-2016, 07:28 AM   #16
Band Member
emtnut's Avatar
Since a couple of you were asking ...
Generally voltage drop with cables larger than 4/0 isn't an issue, because the runs are generally quite short (in my experience anyways).
If your running enough 750kcmil that VDrop is an issue, I'd think a transformer would be a cheaper option ! ( Assuming you've already used parallel conductors )
Anyways, manufacturer specs ALWAYS have the answer !
Here are a couple of charts, showing both AC and DC resistance values, for single and 3 phase, there are temp correction charts as well, and even reactance values for various conductor spacing.
At this level, your generally using engineered drawings, so these calcs are already done for you (at least in my experience)
If anyone is working in this, and would like the pdf, you can PM me and I can send it to you.
You may be able to find it on Anixter's website as well.
how you guys caculate the voltage drop of wire bigger than 4/0?-voltage-drop.jpg   how you guys caculate the voltage drop of wire bigger than 4/0?-dc-ac-resistance.jpg   how you guys caculate the voltage drop of wire bigger than 4/0?-reactance.jpg
The Following 2 Users Say Thank You to emtnut For This Useful Post:
Majewski (08-04-2016), spinninwheels (07-21-2016)
Old 07-21-2016, 04:08 PM   #17
Light Bender
eddy current's Avatar
Rewards Points: 8,034
Run parrallel conductors
Old 07-21-2016, 04:10 PM   #18
Light Bender
Also, check note 6 of table D3
emtnut likes this.
emtnut (07-21-2016)
Old 08-04-2016, 09:47 AM   #19
Band Member
emtnut's Avatar
Mike ... I tried to email the doc, but your account doesn't accept incoming emails ??
I found a link for you though ... https://www.anixter.com/content/dam/...ook_Sec_07.pdf
Old 08-04-2016, 10:55 AM   #20
Rewards Points: 26,832
Here, again, 883 asks questions WRT answers he already has in hand.
Stop trolling.
Just post up your point without beating around the bush.
I also must say that MOST of your queries are of interest to Electrical Engineers and kids trying to pass their exams.
They have no bearing on field practices for active electricians.
In this case, voltage drop on feeder conductors would ALWAYS be addressed by EEs.
For to even to become a concern, the feeder run would have to be mighty long -- hence a mighty bid building -- and a complex project.
Even master electricians are not allowed to weigh in on such affairs.
The EEs protect their turf.
You might find that you'll get true satisfaction only by dropping in on forums dedicated to EEs, because that is definitely where your head is at.
Indeed, hit the books, go to college,get your EE degree. It's plain that EE calculations and concerns obsess you.
emtnut likes this.
emtnut (08-04-2016)
take a look, interesting voltage drop calcultation mike883 General Electrical Discussion 14 07-18-2016 11:47 PM
Voltage Drop Mechdude General Electrical Discussion 6 07-06-2016 10:54 PM
#10 Wire for Voltage Drop Janjak Residential Electrical Forum 29 04-06-2016 03:35 PM
Voltage drop MEISENBURG General Electrical Discussion 10 03-27-2016 07:48 PM
Voltage drop and Masts HeretoHear Residential Electrical Forum 0 01-05-2016 03:27 AM