Motor Feeder Conductor Temperature Rating - Electrician Talk - Professional Electrical Contractors Forum
Like Tree1Likes
  • 1 Post By Incognito
Old 04-19-2019, 11:33 AM   #1
Default Motor Feeder Conductor Temperature Rating
I was looking at some cable sizing for an Industrial MCC and i looking at the MCC Details, Allen Bradley 2100 MCC, it says
"MCCs are rated for use with 75 C (167 F) cable. Cable must be sized by using a 75 C (167 F) column in NEC Table 310.15 (B) (16) (NFPA 70-2017). The temperature rating of the lugs is not relevant."
Although that is for NEC, but i am presuming CEC would be the same.
Just searching i ran into the discussion below which seems to suggest that if the motor is Class A, then 90C table is acceptable.
electriciantalk.com/f31/motor-feed-conductor-temperature-rating-82729/
My understanding is that all sizing needs to be done per the 75C table, as that's what the MCC design suggests, but wondering if that is not necessary or covered somehow differently in code.
arbitarytwist is offline   Reply With Quote
Old 04-19-2019, 01:35 PM   #2
RSE Master Electrician
Incognito's Avatar
Rewards Points: 752
Only the first 1.2 meters of conductor connected to the MCC would have to be rated at 75 degrees, not the whole length from MCC to the motor. 4-006(5)
Same goes for the conductor connected to the motor. If the motor is a class “A” motor and 90 degree rated conductors are used, only the fist 1.2 m of conductor connected to the motor is permitted to be rated at 90 degrees. 28-104(2)+(3)
Wiring from junction box to junction box that is not connected to any equipment can have it’s ampacity rated at the temperature rating of the conductor. 4-006 is only for wires connected to equipment.
Kevin_Essiambre likes this.
2018 Ontario Electrical Code
Incognito is online now   Reply With Quote
Old 04-19-2019, 07:08 PM   #3
Same goes for the conductor connected to the motor. If the motor is a class A motor and 90 degree rated conductors are used, only the fist 1.2 m of conductor connected to the motor is permitted to be rated at 90 degrees. 28-104(2)+(3)
Wiring from junction box to junction box that is not connected to any equipment can have its ampacity rated at the temperature rating of the conductor. 4-006 is only for wires connected to equipment.
So in that case its 75C if you go direct from MCC to Motor Class A or not if the MCC is "rated for 75C"
Old 04-19-2019, 07:41 PM   #4
Incognito's Avatar
Rewards Points: 752
Yes.
Non-continuous breaker rating/ CSA pratice tool Mcarthur00 Canadian Electrical Forum 6 10-02-2017 01:28 PM
Non-continuous breaker rating/ CSA pratice tool Mcarthur00 New Member Introductions 2 10-01-2017 11:43 AM
Temperature Rating KeithAnBr New Member Introductions 7 11-16-2016 04:48 PM
Current Rating for Sub-Panel and Feeders swimmer NEC Code Forum 11 09-22-2016 12:41 PM