At a sewage pumping station we have a stand by generator that is used to supply power to the entire station if power is lost. It is fed from a transfer switch inside a MCC. The MCC has no neutral loads, it is strictly 600 volts.
A few questions:
Does a neutral still need to be run to the generator?
If yes, then we plan to run the neutral wire to the generator and connect it to the neutral bar inside the transfer switch. Inside the generator the neutral will be floating, and the frame of the generator connected to a bonding conductor which is then connected to the MCC ground bar.
If no neutral is run to the generator, then the neutral and frame of the generator will connected together inside the generator. Do we then also need to connect this point to a ground electrode?
I want to see what you guys say. I have had conflicting answers from electrical inspectors. Some say no neutral is required, some say it is. They also say no neutral is required and no ground electrode to the generator.
lynes.nathan is offline   Reply With Quote
Old 02-02-2016, 11:48 PM   #2
Rewards Points: 621
I would have said no ground electrode at the generator as it's not a separately derived system.
RFguy is offline   Reply With Quote
Old 02-03-2016, 10:38 AM   #3
Rewards Points: 332
No neutral required, there is Neutral connection point at the Gen set:
1. 3 phases from Gen set to Transfer Switch.
2. 1 bonding (Chasis) wire from Generator set to Ground bar at Transfer switch and from transfer switch to MCC.
If still in doubt, call the Gen supplier, they are more familiar with this type of installation than the inspector, in my case was Cullen, they were very helpful.
nomadapower is offline   Reply With Quote
Old 02-03-2016, 10:44 AM   #4
Rewards Points: 332
Single line of it:
The Following 2 Users Say Thank You to nomadapower For This Useful Post:
51360 (02-03-2016), lynes.nathan (02-20-2016)
Old 02-20-2016, 03:55 PM   #5
Rewards Points: 217
The inspector is allowing us to not run a neutral and no ground electrode is required. The neutral and frame will be bonded together at the generator.
The Following User Says Thank You to lynes.nathan For This Useful Post:
nomadapower (02-20-2016)
Old 02-20-2016, 11:45 PM   #6
Rewards Points: 332
Thanks for the feed back
The Following User Says Thank You to nomadapower For This Useful Post:
lynes.nathan (02-21-2016)
Old 02-24-2016, 06:28 PM   #7
Rewards Points: 3,090
A few questions:
So, is the main service grounded? If not, i will assume there is suitable ground fault detection, as per 10-106(2)!
No problem not grounding the generator if ground fault detection is used at the main service MCC, and the ungrounded generator feeds that system. Correct?
Maybe I am not understanding how this station is supplied.
Borgi
Old 03-01-2016, 09:10 PM   #8
Rewards Points: 217
Borgi
Yes the main service is grounded. The service supplying the station is 600/347 Y.
51360 (03-01-2016)
Generator permit (red tape) carryyourbooks General Electrical Discussion 4 01-23-2016 09:34 AM
115 VAC disconnect - should I break both hot & neutral? Paul Kraemer General Electrical Discussion 11 01-22-2016 10:21 PM
Generator Installation JudyN General Electrical Discussion 4 01-21-2016 06:24 AM
Replacing oven feed because of generator install?? NJSparky Residential Electrical Forum 5 01-13-2016 10:53 PM