Soffit receptacle - rule for circuit - Electrician Talk - Professional Electrical Contractors Forum
Like Tree1Likes
  • 1 Post By Incognito
Old 05-17-2019, 09:51 PM   #1
Rewards Points: 297
Default Soffit receptacle - rule for circuit
Hi all, been going through the code , and maybe it’s staring me in the face, but I can’t find specifics on circuit requirements for soffit receptacles. I found specifics for covers, depending on the location. Some older handbooks I have state they can either be off outside receptacle circuit,....or....off any lighting circuit inside. However as mentioned, I can’t see this referenced anywhere.
Judoka is online now   Reply With Quote
Old 05-17-2019, 10:30 PM   #2
RSE Master Electrician
Incognito's Avatar
Rewards Points: 954
There is no code. They can be off any circuit you want, with some exceptions of course. If it is above 2.5 meters from the ground it also does not have to be GFI protected.
99cents likes this.
2018 Canadian Electrical Code
Old 05-18-2019, 01:16 PM   #3
Rewards Points: 3,096
Was doing a service call for a customer last week anyhow looked up at the soffit receptacle and saw a heat tape plugged in for the gutter they didn't change out the receptacle to a gfci damn competition
Old 05-19-2019, 02:47 PM   #4
Beam Me Up Scotty
Kevin_Essiambre's Avatar
Rewards Points: 480
You can take it off of most of the circuits in a building, with the exceptions of the dedicated receptacles.
Remember that it will have to be GFCI protected if installed under 2.5M from the ground, and it will have to be AFCI protected if installed on a dwelling unit.
The last home I did soffit receptacles on, we had an AFCI circuit for the outdoor receptacles. We came off of the load side of the front door GFCI, went to the switch, then to the 3 soffit receptacles. With this way, you don't have to climb a ladder to replace or reset the GFCI.
Vote Kevin for Moderator!
Old 05-21-2019, 02:49 PM   #5
Rewards Points: 212
Yeah, as others mentioned the GFCI for anything 2.5m above grade or below is the only requirement for a general-purpose receptacle. §26-722
Beyond that, if it's outdoors it'll need a coverplate intended for wet locations (not extra-duty just normal). §26-708
& AFCI §26-656
bob_says_hello is offline   Reply With Quote
Soffit receptacle 99cents Canadian Electrical Forum 63 06-15-2020 02:38 PM
CEC vs. NEC Receptacle Spacing rkstjarz Canadian Electrical Forum 35 02-28-2018 10:53 AM
adding a ground papaotis Residential Electrical Forum 71 05-22-2017 11:54 AM
208V receptacle and 120V receptacle ejon1801 General Electrical Discussion 15 03-12-2017 03:17 PM
Melted split receptacle tabs otif Residential Electrical Forum 21 10-26-2016 09:07 PM