Old 07-25-2019, 04:35 PM   #61
Old Grumpy Bastard
 
MechanicalDVR's Avatar
 
Join Date: Dec 2007
Location: "Old Dominion"
Posts: 59,572
Rewards Points: 1,556
Default

Quote:
Originally Posted by Incognito View Post
So what do you guys down south use to enter the top of a meter base using PVC? The threaded one from hack’s pic?

If we used that one we would have to use a metal threaded nipple with a female PVC connector
Nipple and female adapter if the inspector is a by the book guy.
Incognito likes this.
__________________
I'm as Christian as possible in the times we live in.

Always just a stallion in a china shop
MechanicalDVR is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 07-25-2019, 04:47 PM   #62
RSE Master Electrician
 
Incognito's Avatar
 
Join Date: Apr 2019
Location: Ontario, Canada
Posts: 786
Rewards Points: 888
Default

Quote:
Originally Posted by HackWork View Post
Yes, that is done everywhere.

While it is against code for the lack of listing as explained earlier, I have never heard of someone being failed for doing it.

The PVC connector is very tight in the meter hub so I will coat it with PVC cement which softens it and deforms it to fill in any crack or crevice. It is sealed super tight.
Here there is the lack of a listing and an actual code violation so inspectors will call you on it. Rarely done though because we have the glue in meter hub available
spinninwheels likes this.
__________________
2018 Canadian Electrical Code
Incognito is offline   Reply With Quote
Old 07-25-2019, 05:03 PM   #63
Senior Member
 
CoolWill's Avatar
 
Join Date: Jan 2019
Location: SC
Posts: 2,233
Rewards Points: 2,752
Default

Quote:
Originally Posted by MechanicalDVR View Post
Nipple and female adapter if the inspector is a by the book guy.
I've done literally thousands of service riser across several states using PVC straight into a meter hub. I have never seen an inspector bat an eye about it. It's only here in la-la land ET where it's an issue.
HackWork likes this.
__________________
I'm With Her! Hillary 2016
CoolWill is online now   Reply With Quote
The Following User Says Thank You to CoolWill For This Useful Post:
HackWork (07-25-2019)
Sponsored Links
Advertisement
 
Old 07-25-2019, 05:08 PM   #64
Mensa Player
 
HackWork's Avatar
 
Join Date: Oct 2009
Location: -
Posts: 33,811
Rewards Points: 795
Default

Quote:
Originally Posted by CoolWill View Post
I've done literally thousands of service riser across several states using PVC straight into a meter hub. I have never seen an inspector bat an eye about it. It's only here in la-la land ET where it's an issue.
If a normal electrician saw a rigid nipple coming out of a meter hub with a PVC female adapter on it and then PVC glued into it, he would laugh and say that a homeowner did it. 3 points of failure instead of one. Perfect example of why the electrical code should not always be followed.
MechanicalDVR likes this.
__________________
I'm trying to think, but nothing happens.
HackWork is online now   Reply With Quote
Old 07-25-2019, 05:28 PM   #65
Senior Member
 
FishinElectrcian's Avatar
 
Join Date: Jul 2019
Location: West Coast Canada
Posts: 233
Rewards Points: 60
Default

PVC to PVC is fine.. It's cast aluminum hub to PVC MA that's wrong. I only use EMT... I hate PVC on a pole, the thermal expansion and contraction is hard on the meter gear.

So there 🙂
FishinElectrcian is offline   Reply With Quote
Old 07-25-2019, 05:35 PM   #66
Mensa Player
 
HackWork's Avatar
 
Join Date: Oct 2009
Location: -
Posts: 33,811
Rewards Points: 795
Default

Quote:
Originally Posted by FishinElectrcian View Post
PVC to PVC is fine.. It's cast aluminum hub to PVC MA that's wrong.
It's not wrong, it's very right.
__________________
I'm trying to think, but nothing happens.
HackWork is online now   Reply With Quote
Old 07-25-2019, 05:46 PM   #67
Can't Remember
 
Join Date: Jan 2009
Location: New Hampshire
Posts: 9,085
Rewards Points: 14
Default

I use those offsets top and bottom of meter sockets regularly. Just makes the job easier. No different than putting a male adapter into the hub. I think this is just semantics really and while I think the listing should be changed, again it’s one of those things I’m not worried about. The utility locally does weatherproof seu connectors into the hubs by the thousands. Same issue (or not).
nrp3 is offline   Reply With Quote
Old 07-25-2019, 05:57 PM   #68
Mensa Player
 
HackWork's Avatar
 
Join Date: Oct 2009
Location: -
Posts: 33,811
Rewards Points: 795
Default

Quote:
Originally Posted by nrp3 View Post
I use those offsets top and bottom of meter sockets regularly. Just makes the job easier.
If you use the meter offset on the top, then you have to turn the meter hub 180 degrees to move it away from the back of the meter pan.

With the meter hub installed correctly, it sets the KO far enough back that you can come straight out of it like in my picture. No meter offset needed.
__________________
I'm trying to think, but nothing happens.
HackWork is online now   Reply With Quote
Old 07-25-2019, 06:27 PM   #69
cog
 
stuiec's Avatar
 
Join Date: Sep 2010
Location: cana-duh
Posts: 5,173
Rewards Points: 1,174
Default

I've never run PVC into a meter base, but are you other Canucks saying that you're running a PVC TA straight into the meter base without a hub??
stuiec is offline   Reply With Quote
Old 07-25-2019, 07:42 PM   #70
RSE Master Electrician
 
Incognito's Avatar
 
Join Date: Apr 2019
Location: Ontario, Canada
Posts: 786
Rewards Points: 888
Default

Quote:
Originally Posted by stuiec View Post
I've never run PVC into a meter base, but are you other Canucks saying that you're running a PVC TA straight into the meter base without a hub??
I have done many but always used a pvc hub that the conduit glues into. All the overhead bases I’ve used had to be done with a hub as the top hole is a big square that the hub bolts into.
__________________
2018 Canadian Electrical Code
Incognito is offline   Reply With Quote
Old 07-25-2019, 07:50 PM   #71
cog
 
stuiec's Avatar
 
Join Date: Sep 2010
Location: cana-duh
Posts: 5,173
Rewards Points: 1,174
Default

Quote:
Originally Posted by Incognito View Post
I have done many but always used a pvc hub that the conduit glues into. All the overhead bases I’ve used had to be done with a hub as the top hole is a big square that the hub bolts into.
Yeah, all the bases I've used are designed for a hub. I believe its a matter of water ingress. Just sounded like some guys are throwing a TA with a lock nut in.
stuiec is offline   Reply With Quote
Old 07-25-2019, 07:52 PM   #72
Senior Member
 
Join Date: Oct 2012
Location: Alberta Rockies
Posts: 2,725
Rewards Points: 3,808
Default

Quote:
Originally Posted by stuiec View Post
I've never run PVC into a meter base, but are you other Canucks saying that you're running a PVC TA straight into the meter base without a hub??
The entire subdivision I'm in has every meter base with 2 TA's in the bottom - one supply from underground distribution, and 1 out to an LB and then to the panel in the house. I've seen tons in other towns and cities all done the same way.. If it's wrong, they're all done wrong.
glen1971 is offline   Reply With Quote
Old 07-25-2019, 07:55 PM   #73
Can't Remember
 
Join Date: Jan 2009
Location: New Hampshire
Posts: 9,085
Rewards Points: 14
Default

I'm fine with this as long as the pvc hub is an accessory provided by the manufacturer or I don't have to spend a bunch of time finding or waiting for the proper bolt pattern to fit my meter socket. Locally, here, the utility provides the socket. However, I'm working on a 400 amp overhead. The meter socket is a different brand than usual and they gave me a another brands hub which is fine if it bolts up. Doing rigid steel this time, so what we are arguing about doesn't matter, but for the garden variety residential service, this can be a pain. If the utility doesn't care, I don't much either.
nrp3 is offline   Reply With Quote
Old 07-25-2019, 07:56 PM   #74
cog
 
stuiec's Avatar
 
Join Date: Sep 2010
Location: cana-duh
Posts: 5,173
Rewards Points: 1,174
Default

Quote:
Originally Posted by glen1971 View Post
The entire subdivision I'm in has every meter base with 2 TA's in the bottom - one supply from underground distribution, and 1 out to an LB and then to the panel in the house. I've seen tons in other towns and cities all done the same way.. If it's wrong, they're all done wrong.
ahh, there's the difference. I've only ever done overheads. No need for a hub on the underside of a base.
glen1971 likes this.
stuiec is offline   Reply With Quote
Old 07-25-2019, 08:05 PM   #75
Senior Member
 
Join Date: Oct 2012
Location: Alberta Rockies
Posts: 2,725
Rewards Points: 3,808
Default

Quote:
Originally Posted by stuiec View Post
ahh, there's the difference. I've only ever done overheads. No need for a hub on the underside of a base.
And for an overhead I've only seen PVC on some older houses.. All newer ones in most of Alberta need to be "metallic" (see copy from Fortis Guide).

The Customer shall:
 Supply and install the meter socket(s).
 Supply and install a metallic service entrance mast complete with weather head, clevis insulator and cable. The service mast or clevis insulator complete with bolt, shall be securely fastened to the building.
Note: Screw type insulators (service knobs) will not be accepted on new or
upgraded construction.
glen1971 is offline   Reply With Quote
Old 07-25-2019, 08:37 PM   #76
Band Member
 
emtnut's Avatar
 
Join Date: Mar 2015
Location: Eastern Ontario
Posts: 5,849
Rewards Points: 1,276
Default

Quote:
Originally Posted by glen1971 View Post
Note: Screw type insulators (service knobs) will not be accepted on new or
upgraded construction.
If something hits the O/H line, they want a good part of the house to come with it
glen1971 likes this.
__________________
_____________________________________
Your Mother was a hamster, and your father smells of Elderberries. ... Now go away, or I shall taunt you a second time
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
emtnut is online now   Reply With Quote
Old 07-25-2019, 11:15 PM   #77
Senior Member
 
FishinElectrcian's Avatar
 
Join Date: Jul 2019
Location: West Coast Canada
Posts: 233
Rewards Points: 60
Default

Yeah you gotta build solid, none of my masts have taken a hit yet but I have confidence they're solid. Used to have an inspector that wanted us to get a ladder and stand on the panel. Quirky ass buggers..
FishinElectrcian is offline   Reply With Quote
Old 07-25-2019, 11:33 PM   #78
Old Grumpy Bastard
 
MechanicalDVR's Avatar
 
Join Date: Dec 2007
Location: "Old Dominion"
Posts: 59,572
Rewards Points: 1,556
Default

Quote:
Originally Posted by CoolWill View Post
I've done literally thousands of service riser across several states using PVC straight into a meter hub. I have never seen an inspector bat an eye about it. It's only here in la-la land ET where it's an issue.
I've done it too in thee states and not been flagged.

I have however known a couple guys to get bitten for it. I'm not sure if there were other issues that caused the inspector to be so critical so I can't say more.
__________________
I'm as Christian as possible in the times we live in.

Always just a stallion in a china shop
MechanicalDVR is offline   Reply With Quote
Old 07-26-2019, 09:13 AM   #79
Senior Member
 
Join Date: Oct 2012
Location: Alberta Rockies
Posts: 2,725
Rewards Points: 3,808
Default

Quote:
Originally Posted by emtnut View Post
If something hits the O/H line, they want a good part of the house to come with it
I know when a tree branch fell on my overhead service it broke the wires at the splice by the weatherhead and cracked the weatherhead. The mast never moved. Stupid tree... lol
glen1971 is offline   Reply With Quote
Old 07-26-2019, 09:26 AM   #80
Member
 
Join Date: May 2019
Location: Southern Alberta
Posts: 40
Rewards Points: 16
Default

Quote:
Originally Posted by glen1971 View Post
And for an overhead I've only seen PVC on some older houses.. All newer ones in most of Alberta need to be "metallic" (see copy from Fortis Guide).



The Customer shall:

 Supply and install the meter socket(s).

 Supply and install a metallic service entrance mast complete with weather head, clevis insulator and cable. The service mast or clevis insulator complete with bolt, shall be securely fastened to the building.

Note: Screw type insulators (service knobs) will not be accepted on new or

upgraded construction.
Key word being mast. PVC is acceptable if you're not using it as an attachment point, just as a raceway. Ex. On the gable end of a house (or a two story) where you're not penetrating the roofline and are using a through bolt clevis as the attachment point.

Sent from my SM-G960W using Tapatalk
99cents likes this.
Mobius87 is online now   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



All times are GMT -4. The time now is 03:33 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com