what is 230VAC single phase? - Electrician Talk - Professional Electrical Contractors Forum
Like Tree43Likes
Old 07-03-2019, 12:15 PM   #1
Rewards Points: 34
Default what is 230VAC single phase?
We have some motors that come with brakes. The motors are powered by 230VAV 3PH, but the brakes are powered by 230VAC 1PH. Our supply in the building is 230VAC 3PH and I am wondering how we can get 230VAC single phase? I know I am missing something but I am not sure if 230VAC single phase is possible without having 480VAC 3PH....
Zylonite is offline   Reply With Quote
Old 07-03-2019, 12:22 PM   #2
Rewards Points: 459
230V 3 phase is 3 hots.
230V single phase is 2 hots.
Old 07-03-2019, 12:40 PM   #3
Rewards Points: 34
yes 230VAC is LL, but is it possible to get 230V single phase from 230V 3 phase? I know it's not possible but I need to know for sure. BTW I am a student in case this question sounds stupid.
Old 07-03-2019, 12:42 PM   #4
Rewards Points: 459
Yes, it is possible. This is how:
MikeFL (07-03-2019)
Old 07-03-2019, 12:43 PM   #5
Bird dog's Avatar
Rewards Points: 1,348
Is this a homework question?
onthegravytrain likes this.
Old 07-03-2019, 12:45 PM   #6
CoolWill's Avatar
Rewards Points: 2,012
It is possible. Any two lines will give you single phase 230.
I'm With Her! Hillary 2016
Old 07-03-2019, 12:47 PM   #7
Rewards Points: 459
I think I see what you are getting hung up on.
3 phase is all 3 hots.
Single phase is 2 of those hots, or 1 of those hots and neutral.
There is no "2 phase" in this situation. Using 2 hots is single phase, and that is how you would make 230V single phase on a 3 phase 230V system.
Old 07-03-2019, 12:49 PM   #8
Rewards Points: 34
Ok makes sense. I was thinking single phase as of hot-natural to get 230v single phase from a 230v source which is not possible.
Old 07-03-2019, 01:26 PM   #9
Rewards Points: 1,514
Most residential electric hot water heaters are 230V single phase.
Kevin_Essiambre and Bcec like this.
Old 07-03-2019, 05:21 PM   #10
Rewards Points: 3,698
I'm curious, where is there 230 vac 3 phase? I've never seen that one up here..
From Fortis' Installation Guide on Standard Supply voltages:
Service Voltage Phase and Wire and Connection
120 and 240 Single-phase, 3 wire
240 and 480 Single-phase, 3 wire
120 and 208 Three-phase, 4 wire wye
277 and 480 Three-phase, 4 wire wye
347 and 600 Three-phase, 4 wire wye
2400 and 4160 Three-phase, 4 wire wye
14400 and 24940 Three-phase, 4 wire wye
Old 07-03-2019, 05:47 PM   #11
Bird dog's Avatar
3 phase floating delta, 240v only
3 phase corner grounded delta, 240v only
3 phase high leg delta (or wild leg delta), 240v, 208v, 120v
3(?) phase open delta, not sure about voltages
Old 07-03-2019, 06:42 PM   #12
Watt Pusher
B-Nabs's Avatar
Rewards Points: 466
230V is a utilization voltage used on 240V systems. Motors and other equipment are usually rated at a voltage lower than the nominal system voltage to allow for voltage drop.
Old 07-03-2019, 06:57 PM   #13
Certified Organic A-Hole
pudge565's Avatar
Rewards Points: 1,022
An open delta can be any of the "closed delta" voltages. The only difference between a closed delta and an open delta is the open delta utilizes only 2 transformers where the closed delta has 3. This reduces the total capacity of the open delta system.
The Following User Says Thank You to pudge565 For This Useful Post:
Bird dog (07-03-2019)
Old 07-03-2019, 08:06 PM   #14
908Eng's Avatar
Rewards Points: 72
As Hack already mentioned, this is as simple as hooking up two phases instead of all 3. Unless you are dealing with some kind of strange industrial facility, you likely have 208VAC, 3 phase main incoming (not 230VAC). You can always confirm with a multimeter across the phases.
Your 230VAC 3 phase motor is actually using 208V, 3 phase but most motors will happily run at a wide range of voltages.
Your 230VAC single phase brake will likely run at 208VAC which is two hots of a 3 phase system OR 240VAC which is both hots of a single phase system. The components are likely rated for a wide range of voltages.
You can sometimes see 230VAC or 240VAC 3 phase when you are using a digital phase converter (single phase to 3 phase). Not all 3 phase motors can handle this higher voltage.
The only time that I have seen a piece of equipment that would not run on 208VAC single phase was a sensitive specialty piece of dental sterilization equipment. They had to install a small autotransformer to bump it up to 230VAC.
glen1971 likes this.
CAVEAT: Information presented in this post does not constitute professional engineering advice.
908Eng is offline   Reply With Quote
Old 07-03-2019, 08:15 PM   #15
CoolWill's Avatar
So let me see if I understand. Canada never had 240 volt delta services?
Old 07-03-2019, 08:17 PM   #16
pudge565's Avatar
240V delta systems are not uncommon in the US in older facilities. They aren't typically installed new in favor of 480/277Y systems. The downsides to 240V deltas is you either have a high leg, which is unusable for single phase loads, an ungrounded system which requires ground fault indication, or you have a corner grounded system which can be dangerous for personnel not familiar with the system. The latter 2 will produce only 240V.
tmessner and 908Eng like this.
Old 07-03-2019, 09:22 PM   #17
Watt Pusher
B-Nabs's Avatar
Rewards Points: 466
We did, but they are fairly uncommon nowadays. The Poco around here does everything they can to get people to switch over to 208Y120 or 600Y347. 240 deltas can be found in some older industrial (or formerly industrial) buildings. A few years ago I did a reno to an old warehouse that involved installing ground fault detection and a 240D - 208Y120 transformer on an existing 240 delta service. Poco fought hard to change the service but the engineer was able to get it by somehow.
glen1971, 908Eng and CoolWill like this.
Old 07-03-2019, 10:58 PM   #18
Rewards Points: 3,044
I had a guy request two phase. i had to educate him, similar to this thread.
Greg
Old 07-04-2019, 12:12 AM   #19
HertzHound's Avatar
Rewards Points: 656
I don't think Ive ever seen 230V. As far as I know some motors are rated/wired at 230V to be within 10% of 208, 220, or 240 volts. If you see a rating on a motor that says 240v it can't be used on 208V or vice versa.
On another note if you see a piece of equipment that's slash rated (marked 120/208, 277/480) it needs a neutral.
glen1971 and Kevin_Essiambre like this.
“Why say lot words when few words do trick”
Old 07-04-2019, 12:36 AM   #20
The ones I listed are from our utilities' installation guide and are the only standard supply voltages.