What do you guys use for 100 and 200 amp service? - Page 2 - Electrician Talk - Professional Electrical Contractors Forum
Like Tree16Likes
Old 07-01-2020, 04:57 PM   #21
Journeyman
Rewards Points: 212
4/0 rw for 200's
1/0 rw for 100's
if you look in the 2" lb it will say max 3 4/0, so when we do commercial 200's with 250's we use 2.5" lbs and 2" pipe. Although our inspector never gives us a hard time with running the additional #6 through the service conduit
I always bring an insulated green through the meter can without terminating and use the service conduit to get to the panel to ground. saves a penetration.
quick_2 is offline   Reply With Quote
Old 07-01-2020, 08:25 PM   #22
Light Bender
eddy current's Avatar
Rewards Points: 8,166
Originally Posted by quick_2 View Post
4/0 rw for 200's
1/0 rw for 100's
I assume you talking about aluminum, but why such a large conductor for 100 amps?
Kevin_Essiambre likes this.
Old 07-02-2020, 12:01 AM   #23
Rewards Points: 18
Most of my work is small town/rural, with no gas service, so 98% is 200A services.
3/0 copper RW90 with a bare #3 copper for neutral. Metal mast if I need the height, 2" PVC from meter socket to panel.
For underground from a CSTE or pole mounted meter socket, then 250MCM USEI usually.
Viggmundir is offline   Reply With Quote
Old 07-02-2020, 04:54 PM   #24
Journeyman
Rewards Points: 212
We only get deliveries once a week, and i understand its harder to get #1, so we usually buy per the reel and 1/0 works in every situation and long feeders for voltage drop too.
Old 07-02-2020, 05:54 PM   #25
Electron Pathway Engineer
The_Modifier's Avatar
Rewards Points: 766
Originally Posted by eddy current View Post
Why only up to 400 amps?
Exactly, those fools are leaving profits on the table- a real pro knows to use #14AWG.
Bird dog and Kevin_Essiambre like this.
Old 07-02-2020, 05:59 PM   #26
Bird dog's Avatar
Rewards Points: 798
and leave a taillight warranty.
Old 07-02-2020, 08:03 PM   #27
Rewards Points: 336
Originally Posted by Kevin_Essiambre View Post
I use RW90, and normally for a resi 200 amp service I'll use black 250mcm aluminum for the hots, and white 4/0 aluminum for the neutral.
Never had an issue with this combination of wires.
Only reason for the reduced neutral is because 250mcm is not stocked in white, so it saves us taping it white or painting it white.
Thanks Kevin. When you go with 2x250 and 1x4/0 aluminum, does this fit into a 2in pvc lb nicely? Or do you use 2.5in lb?
newbie44 is offline   Reply With Quote
Old 07-02-2020, 08:28 PM   #28
Beam Me Up Scotty
Kevin_Essiambre's Avatar
Rewards Points: 494
2.5" is too expensive. I've seen the 2" LB (or LL or LR) that says 3×4/0 max, but it hasn't been an issue, and our inspections were mandatory visits, so the inspector never mentioned anything...
I'll dig up some photos later, but the photos may only have 250mcm taped grey (i had grey, and its permitted) rather than the reduced neutral.
Oh, and some were back to back LB's, but as long as you make the bends correctly, they fit without an issue.
Vote Kevin for Moderator!
Old 07-02-2020, 08:42 PM   #29
Rewards Points: 336
Found this by the way bulletin 4-3-9
Old 07-02-2020, 08:51 PM   #30
Beam Me Up Scotty
Rewards Points: 494
So we could use #2 aluminum for the neutral if we wanted when using 250mcm aluminum for the hots.... interesting and good to know.
I have the bulletins, but never really bothered to read them ALL. I read them when looking up code references or to double check something.
Old 07-08-2020, 01:14 AM   #31
Magic Smoke Remover
Rewards Points: 1,976
Can't use #6 neutral here, even on 100 amp service.
From the head inspector when I fought my last failure:
"What is the smallest size service you can legally install on a single family dwelling? Right 100-amps! X .83% on the service ungrounded conductors and 70% on the service neutral. If we are going to use calculations to de-rate feeders, we need to have calculations printed and on site for inspector to document and keep with the permit records. A service neutral shall never be smaller than #4cu or #2al for a single family dwelling when rebuilt."
He doesn't know how to read the code book. Such a PITA, other times doesn't even open the panel.
Old 07-13-2020, 08:15 PM   #32
NDC
NDC's Avatar
Rewards Points: 2,580
4/0 rw for 200's
1/0 rw for 100's
how are you transitioning the 2.5" lb to 2" pvc?
NDC is online now   Reply With Quote
Old 07-13-2020, 08:16 PM   #33
NDC
NDC's Avatar
BTW every 200 amp service around here I have changed never had anything larger than a #3 neutral if fed with 3/0 copper.
Old 07-13-2020, 08:21 PM   #34
Beam Me Up Scotty
Rewards Points: 494
I'm willing to bet he uses one of these Carlon PVC reducer bushings. (Or any brand, but this info is Carlon).
Old 07-17-2020, 07:44 AM   #35
Rewards Points: 336
This client is specifying that they want copper wire not aluminum and a full 200 amps.
If I use 3/0 copper, do you think going with a #3 copper neutral will be ok with the inspector?
Old 07-17-2020, 08:57 AM   #36
Rewards Points: 336
Whats easier to work with copper 3/0 RW or copper 3/0 T90?
Old 07-17-2020, 09:35 AM   #37
Beam Me Up Scotty
Rewards Points: 494
I always like to explain to these clients that the wiring that connects the entire electrical grid is aluminum.
As for the neutral, you posted this table below in post #29
My interpretation of this would mean #3 copper is large enough for a 200 amp service regardless of if the hots are oversized.