Inverter stacking - Electrician Talk - Professional Electrical Contractors Forum
Old 04-09-2015, 07:52 PM   #1
Rewards Points: 6
Default Inverter stacking
How do I wire one 4kw and one 5kw solar inverters togeather? This is a existing 4.9kw ground mount grid tie system with a Solectria inverter that is connected to a disconnect at the meter I want to add another 20 panels and a 5kw SMA sunny boy inverter, any suggestions on the best way to do this would be appreciated thanks Dan
Dan anderson is offline   Reply With Quote
Old 04-12-2015, 03:12 PM   #2
Rewards Points: 141
I see that you have years of experience and don't mean to be insulting but since your asking I have to ask some possibly very basic questions...
Is your PV system connected to the line side or the load side of the existing service and do you know the difference, especially when it comes to the NEC?
A PV system is a power generating source which is being added to the existing service through synchronization . In you case it is 70 amps at 240 volts which is determined by the 30 and 40 amp breakers you will be using on each PV circuit that you will be installing not the wattage of the inverters or panels.
If the service is 100 amps you could expose existing sub panes to 170 amps of current if not tapping the PV on to the line side of the service upstream of the main service over current protection.
To add PV after the main service over current protection or line side could require additional protection to be added or existing panels and wire to be up sized.
Rap2 is offline   Reply With Quote
Old 04-12-2015, 03:15 PM   #3
Rewards Points: 141
Sorry I meant to say load side in the last sentence....
Old 04-22-2015, 12:47 AM   #4
Rewards Points: 6
Default Dan Anderson
You are correct I do have years of electrical experience but very little on PV systems that's why I'm asking stupid questions. This PV system is connected on the load side of the meter before the first disconnecting means.
Tags
solar inverter stacking
Derate stacking Aegis Canadian Electrical Forum 28 02-12-2013 01:33 AM
DC/AC Inverter Cletis General Electrical Discussion 25 02-08-2013 10:51 PM
Inverter jsb Tools, Equipment and New Products 14 10-25-2010 08:26 PM
ac/dc inverter jjdrees Commercial Electrical Forum 14 06-29-2010 03:26 PM
Inverter BadContact Off Topic (Non Trade) 12 04-26-2010 12:08 PM