PV rapid shutdown device location - Electrician Talk - Professional Electrical Contractors Forum
Like Tree1Likes
  • 1 Post By katwalatapan
Old 01-19-2016, 11:09 AM   #1
Rewards Points: 265
Default PV rapid shutdown device location
Hello,
I understand based on the local jurisdiction, the location of PV rapid shutdown device could be on the interior of the building or on the exterior. I would appreciate some comments on following scenario:
We're planning to install a 8 kW grid-tied PV system on a roof top of two-storey multi-unit residential building. The electrical utility meter and distribution equipment are installed inside the building in the main electrical room. We would install a PV system shutdown device on the rooftop which would activate upon loss of utility AC power and as I understand by code, another PV system shutdown device grouped with the one on the rooftop is required before the DC/AC inverter.
My query is that knowing all electrical equipment is installed inside the building, would the PV system shutdown device installed before the inverter be located inside the building or outside the building as per standard industry practice. In the end the local authority would dictate the terms, but I wanted to understand the industry practice for such scenario.
Thank you.
katwalatapan is offline   Reply With Quote
Old 01-19-2016, 03:37 PM   #2
Rewards Points: 1,224
As a former firefighter, I would prefer to see the PV shutdown in the same location as the service disconnect.
Old 01-21-2016, 10:11 AM   #3
Rewards Points: 265
thank you for the response. If the main service disconnect is located inside the building in the main electrical room along with the meter, then I suppose the shutdown device would be located inside the electrical room, unless the AHJ requires otherwise.
Old 01-21-2016, 11:50 AM   #4
backstay's Avatar
Rewards Points: 296
Location is best with the service disco. One stop shopping for the FFs. Rapid Shut Down systems must be listed. That means to me, you can't build your own shunt trip equipment. I'm not sure about the shutdown with power failure. I see where if the service is killed the wiring from the panels would be off, but all the systems I see are manual reset. That would not work if every time the power went out, you had to reset the RSD system.
Old 01-22-2016, 06:16 AM   #5
Retired Account
Rewards Points: 14,650
Backstay, is there a model/make you'd recommend....? ~CS~
Old 01-22-2016, 02:50 PM   #6
Rewards Points: 22
An option you could use is Micro inverters. I little more expensive but would take care of the rapid shut down. Just a possibility I believe.
Longterm is offline   Reply With Quote
Old 01-22-2016, 04:01 PM   #7
Rewards Points: 265
Thank you very much for the responses.
Microinverter seems like a good alternative. It would not work if AC power is not available (power outage) and an AC disconnect could be installed prior to the main panel for disconnection.
Longterm likes this.
Old 01-22-2016, 10:57 PM   #8
backstay's Avatar
Rewards Points: 296
I've only used Midnite Solar's Bird House.
Old 02-26-2016, 11:50 AM   #9
Rewards Points: 24
Another option is Solar Edge The string voltage is managed by the inverter and goes to 1V per opto in a grid failure and auto resets.
The more I learn the more I realize I don't know.
teejayshelton is offline   Reply With Quote