The 2020 NEC now requires surge Protection for all dwelling units services
230.67*Surge Protection.
230.67(A)*Surge-Protective Device.
All services supplying dwelling units shall be provided with a surge-protective device (SPD).
230.67(B)*Location.
The SPD shall be an integral part of the service equipment or shall be located immediately adjacent thereto.
Exception:*The SPD shall not be required to be located in the service equipment as required in (B) if located at each next level distribution equipment downstream toward the load.
230.67(C)*Type.
The SPD shall be a Type 1 or Type 2 SPD.
230.67(D)*Replacement.
Where service equipment is replaced, all of the requirements of this section shall apply.
They say I shot a man named Gray and took his wife to Italy
She inherited a million bucks and when she died it came to me
I can't help it if I'm lucky
Dennis Alwon is offline   Reply With Quote
Sponsored Links
Advertisement
Old 10-02-2019, 02:54 PM   #2
HackWork's Avatar
Rewards Points: 1,683
Who sets the standard for what "surge protection" is?
Does the standard Eaton Ultra Mike Holmes edition count?
Could you use some cheap $10 crap device like what power strips have in them?
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
HackWork is online now   Reply With Quote
Old 10-02-2019, 03:06 PM   #3
I believe the Eaton surge suppressor is a type 2 so it would be okay.
Sponsored Links
Advertisement
Old 10-02-2019, 03:18 PM   #4
HackWork's Avatar
Oh, I missed that part about type 1 & 2. Thanks.
Old 10-02-2019, 03:26 PM   #5
MikeFL's Avatar
Rewards Points: 846
I'd be curious to know who introduced the proposal to require that.
Was it the SPD industry?
The insurance industry?
Or POCO industry?
Anyone wanna guess?
Anyone want to take the time to look it up?
telsa likes this.
Michael Gookin, President
GPS Timers
(833) GPS-TIME
MikeFL is offline   Reply With Quote
Old 10-02-2019, 06:43 PM   #6
MTW
Rewards Points: 11,526
And people here wonder why some of us have total disdain for the NEC when it's now abundantly clear that it's completely in the pocket of the manufacturers.
micromind, telsa and 460 Delta like this.
MTW is online now   Reply With Quote
Old 10-02-2019, 06:46 PM   #7
HackWork's Avatar
Or POCO industry?
Anyone wanna guess?
I don't want to get into another big argument over this with the resident brainwashees, but I think it is safe to say that a reasonable, intelligent, aware electrician would think that codes like this are implemented due to pressure from the manufacturers for their own gains.
Old 10-02-2019, 07:00 PM   #8
Chief Flunky
Rewards Points: 354
The device in the $10 power strip is the same one used in industrial equipment and utilities install on every fifth pole. It’s a block of metal oxides, mostly zinc. It is sintered which means it is heated just enough so it sticks together. It comes in all shapes and sizes and it is very cheap. The only difference between say a Cooper Ultrasil UHS0306 and a WAlmart power strop is the one from Walmart has a fuse, it is thinner so it starts acting at 150 V instead of 3000 V, and it is about the diameter of a nickel instead of a silver dollar.
Guaranteed these things will be down to $10 by 2021. As to value...haha. Google arrester works and read about lead length. It protects the panel, not the TV. Whole house surge protectors are a scam.
Sent from my iPhone using Tapatalk
paulengr is online now   Reply With Quote
Old 10-02-2019, 07:15 PM   #9
joe-nwt's Avatar
Rewards Points: 1,908
Even if they come down to $10, you still need a 2P breaker and 2 spaces to utilize one.
drsparky likes this.
joe-nwt is online now   Reply With Quote
Old 10-02-2019, 07:28 PM   #10
Hackenschmidt
splatz's Avatar
Rewards Points: 2,484
Square D makes surge protectors that install like a breaker, no leads. I like the idea but having seen the failure mode, I'd rather have the SPD outside of the panel in a sturdy metal box.
Bird dog and MikeFL like this.
This too shall pass.
splatz is online now   Reply With Quote
Old 10-02-2019, 07:54 PM   #11
Bilge Rat
Rewards Points: 3,360
I'm going to place most of the blame for this idiotic requirement on AFCIs.
My reasoning is that as far as I know, the breaker manufacturers were the first ones to purchase a code requirement as an investment and expect (and receive) a tidy return on it.
Next, it was the torque tool manufacturers, now it is the surge suppressor manufacturers.
Who will it be next?
MTW and telsa like this.
micromind is online now   Reply With Quote
The Following 2 Users Say Thank You to micromind For This Useful Post:
460 Delta (10-04-2019), telsa (10-04-2019)
Old 10-02-2019, 08:02 PM   #12
MTW
Nonsense. Forced use of a product never results in a price reduction. A cartel of manufacturers make AFCIs and the prices between them are virtually the same, almost to the penny.
telsa and Kevin_Essiambre like this.
Old 10-02-2019, 08:04 PM   #13
MTW
The same big companies that make AFCI's make surge suppressors. How convenient.
micromind, telsa and CoolWill like this.
Old 10-02-2019, 08:19 PM   #14
RSE Master Electrician
Incognito's Avatar
Rewards Points: 954
I bet Mike Holmes is in on it too!
JoeSparky and Kevin_Essiambre like this.
2018 Canadian Electrical Code
Incognito is offline   Reply With Quote
Old 10-02-2019, 08:28 PM   #15
HackWork's Avatar
Hyperbole doesn’t serve anyone.
While we know that Mike Holmes is not in on it, he certainly will be making a lot more money due to this code change.
Old 10-02-2019, 08:33 PM   #16
MTW
I hope this will cause more people to jump ship from the NEC-brainwashed bandwagon.
micromind likes this.
Old 10-02-2019, 08:43 PM   #17
Bird dog's Avatar
Rewards Points: 2,186
And it will have to be explained to customers basically all bets are off for a direct or close to direct strike IMO.
EARTH FIRST! We'll strip-mine the other planets later.
Popcorn munching forum observer
"The supreme art of war is to subdue the enemy without fighting." Sun Tzu
Bird dog is online now   Reply With Quote
Old 10-02-2019, 08:43 PM   #18
These units are not $10.... They are $60-120 depending. Siemens make a dp 20 amp breaker that is both a circuit breaker and a whole house surge suppressor. GE used to make them so I assume other have it
Here is the siemens unit
https://www.amazon.com/Siemens-QSA20.../dp/B0052MG5K0
Old 10-02-2019, 09:18 PM   #19
Can't Remember
Rewards Points: 1,440
The square D units take a couple of spaces just like a breaker. Works for me. The 2020 doesn't come into effect until at least 2021, though I need to deal with it in mass and maine most likely. Oh well, I'll hit the code update early on.
nrp3 is offline   Reply With Quote
Old 10-02-2019, 09:26 PM   #20
Incognito's Avatar
Rewards Points: 954
Hyperbole doesn’️t serve anyone.
Sure it does. It lightens the crusty mood, it’s humour.
I do agree with you and others though on this new code being brought in only to help people make money. There is no safety value at all.
Thread Tools
Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2020 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2020 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com