Old 04-27-2017, 06:57 PM   #1
Senior Member
 
Cl906um's Avatar
 
Join Date: Jul 2012
Location: Upper Michigan
Posts: 1,626
Rewards Points: 1,206
Default Diesel fuel only

Kind of confused on whether I need a emergency stop that shuts all circuits to the dispenser off. I guess my question deals with article 514 in a sort off way. But I am not sure because I guess I have never come across this situation. There are no other fuels being dispensed at this site.
Cl906um is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 04-27-2017, 07:08 PM   #2
Senior Member
 
sbrn33's Avatar
 
Join Date: Mar 2007
Location: middle america
Posts: 11,468
Rewards Points: 3,336
Default

Not for me. diesel is a non explosive liquid. I normally use seal offs going in and out though just in case they change.
splatz likes this.
sbrn33 is offline   Reply With Quote
Old 04-27-2017, 07:41 PM   #3
Senior Member
 
Cl906um's Avatar
 
Join Date: Jul 2012
Location: Upper Michigan
Posts: 1,626
Rewards Points: 1,206
Default

Quote:
Originally Posted by sbrn33 View Post
Not for me. diesel is a non explosive liquid. I normally use seal offs going in and out though just in case they change.
I put an emergency stop in because the old one had it, so I figured what the heck, I'll use it again. The ahj wants it 20 feet away. I think the 20 foot minimum 100 foot max is just for classified locations to get it out of the hazardous location.
splatz likes this.
Cl906um is offline   Reply With Quote
Sponsored Links
Advertisement
 
Old 04-27-2017, 10:40 PM   #4
Senior Member
 
Join Date: Jan 2007
Location: Wilmington, NC
Posts: 12,167
Rewards Points: 14,714
Default

Quote:
Originally Posted by Cl906um View Post
I put an emergency stop in because the old one had it, so I figured what the heck, I'll use it again. The ahj wants it 20 feet away. I think the 20 foot minimum 100 foot max is just for classified locations to get it out of the hazardous location.
Last time I read 514, the E-Stop needed to be 20' away from the dispenser and no more than 100'. It is also in our (NC) Fire Code.

Typically the classified location for a flammable liquid is 20' from the dispenser to a height of 18" is C1D2 and the area w/in 2' of the dispenser being a C1D1. Since diesel is a combustible, you wouldn't have these C1D1 location from an NEC directive, but the State Fire Code may say otherwise (I believe it does in PA).
splatz and Cl906um like this.
__________________
Three vastly different enemies, but enemies who shared one common trait. ALL of them stifle free speech. All of them bully, degrade and terrorize those who hold opposing views and who peacefully express them. All of them are intolerant and demand “loyalty” to the leader. Michael Sand
hardworkingstiff is offline   Reply With Quote
Old 04-28-2017, 08:42 PM   #5
Senior Member
 
Cl906um's Avatar
 
Join Date: Jul 2012
Location: Upper Michigan
Posts: 1,626
Rewards Points: 1,206
Default

Quote:
Originally Posted by hardworkingstiff View Post
Last time I read 514, the E-Stop needed to be 20' away from the dispenser and no more than 100'. It is also in our (NC) Fire Code.

Typically the classified location for a flammable liquid is 20' from the dispenser to a height of 18" is C1D2 and the area w/in 2' of the dispenser being a C1D1. Since diesel is a combustible, you wouldn't have these C1D1 location from an NEC directive, but the State Fire Code may say otherwise (I believe it does in PA).
My point is, how much of 514 do you have to follow for an unclassified liquid dispenser? May as well be dispensing water in a pool as far as the code is concerned. No idea why he gigged me.
Cl906um is offline   Reply With Quote
Old 04-29-2017, 05:26 PM   #6
Senior Member
 
Cl906um's Avatar
 
Join Date: Jul 2012
Location: Upper Michigan
Posts: 1,626
Rewards Points: 1,206
Default

Guess I'm not the only one confused. This code section is based on fuel dispensing. The exception of flash point tells me diesel is unclassified, but tells me nothing of what to do for dispensing it.
Cl906um is offline   Reply With Quote
Old 04-29-2017, 09:28 PM   #7
Modérateur
 
frenchelectrican's Avatar
 
Join Date: Mar 2007
Location: Philippines
Posts: 8,635
Rewards Points: 16,782
Default

Quote:
Originally Posted by Cl906um View Post
Guess I'm not the only one confused. This code section is based on fuel dispensing. The exception of flash point tells me diesel is unclassified, but tells me nothing of what to do for dispensing it.
Did ya ask the state inspector or fire inspector to see what they do cover on that code related to diesel fuel dispensing.,,

I try to read the 514 but are you on 11 or 14 cycle ?
__________________
Bleu est beau.
frenchelectrican is offline   Reply With Quote
Old 04-29-2017, 10:51 PM   #8
Senior Member
 
Join Date: Jan 2007
Location: Wilmington, NC
Posts: 12,167
Rewards Points: 14,714
Default

Quote:
Originally Posted by Cl906um View Post
Guess I'm not the only one confused. This code section is based on fuel dispensing. The exception of flash point tells me diesel is unclassified, but tells me nothing of what to do for dispensing it.
I think you are on the right track here. You don't have to use sealoffs and x-proof fittings, but you still have to comply with fuel dispensing requirements because they are not based on classification but the dispensing of fuel, therefore the estops need to be installed as required.
splatz likes this.
__________________
Three vastly different enemies, but enemies who shared one common trait. ALL of them stifle free speech. All of them bully, degrade and terrorize those who hold opposing views and who peacefully express them. All of them are intolerant and demand “loyalty” to the leader. Michael Sand
hardworkingstiff is offline   Reply With Quote
Old 04-29-2017, 11:23 PM   #9
Senior Member
 
Cl906um's Avatar
 
Join Date: Jul 2012
Location: Upper Michigan
Posts: 1,626
Rewards Points: 1,206
Default

Quote:
Originally Posted by hardworkingstiff View Post
I think you are on the right track here. You don't have to use sealoffs and x-proof fittings, but you still have to comply with fuel dispensing requirements because they are not based on classification but the dispensing of fuel, therefore the estops need to be installed as required.
I put an e stop in. Just put it by the panel which is the only thing within 200'. Only thing is, it isn't 20' away. It's 10' away. Have to mount a post just to put an e stop, and risk it getting whacked by a semi with a trailer. To me it is more at risk than what I did.
Cl906um is offline   Reply With Quote
Old 04-30-2017, 08:16 AM   #10
Senior Member
 
Join Date: Jan 2007
Location: Wilmington, NC
Posts: 12,167
Rewards Points: 14,714
Default

Quote:
Originally Posted by Cl906um View Post
I put an e stop in. Just put it by the panel which is the only thing within 200'. Only thing is, it isn't 20' away. It's 10' away. Have to mount a post just to put an e stop, and risk it getting whacked by a semi with a trailer. To me it is more at risk than what I did.
I would expect the inspector's response to be something like "that's what bumperposts are for".

We do not have the option of not complying with the code because it is too difficult or inconvenient.
splatz likes this.
__________________
Three vastly different enemies, but enemies who shared one common trait. ALL of them stifle free speech. All of them bully, degrade and terrorize those who hold opposing views and who peacefully express them. All of them are intolerant and demand “loyalty” to the leader. Michael Sand
hardworkingstiff is offline   Reply With Quote
Old 04-30-2017, 08:41 AM   #11
Senior Member
 
Cl906um's Avatar
 
Join Date: Jul 2012
Location: Upper Michigan
Posts: 1,626
Rewards Points: 1,206
Default

Quote:
Originally Posted by hardworkingstiff View Post
I would expect the inspector's response to be something like "that's what bumperposts are for".

We do not have the option of not complying with the code because it is too difficult or inconvenient.
All things considered, technically,the panel would be in the hazardous area had it been classified. Seeing as how it is not, the dispenser is right next to it. It is actually an existing service that a ghost town (ex Air Force base), had a lift station at. Chicken and egg thing. So by rights, the e stop should actually take out the service lateral. Haha. This is why they should hire an engineer to design the crap. They tried to save a buck, and I come there to wire it up, and it's so full of ifs and buts. The dispenser is three feet away from the service...
Cl906um is offline   Reply With Quote
Old 04-30-2017, 08:50 AM   #12
Senior Member
 
Join Date: Jan 2007
Location: Wilmington, NC
Posts: 12,167
Rewards Points: 14,714
Default

Quote:
Originally Posted by Cl906um View Post
All things considered, technically,the panel would be in the hazardous area had it been classified......... The dispenser is three feet away from the service...
Since the panel is 3' away from the dispenser, unless it is below 18" it would not be in a classified area even if the dispenser was pumping a flammable liquid.

Table 514.3(B)(1)
__________________
Three vastly different enemies, but enemies who shared one common trait. ALL of them stifle free speech. All of them bully, degrade and terrorize those who hold opposing views and who peacefully express them. All of them are intolerant and demand “loyalty” to the leader. Michael Sand
hardworkingstiff is offline   Reply With Quote
Old 04-30-2017, 09:13 AM   #13
Senior Member
 
Cl906um's Avatar
 
Join Date: Jul 2012
Location: Upper Michigan
Posts: 1,626
Rewards Points: 1,206
Default

[QUOTE=hardworkingstiff;3894817]Since the panel is 3' away from the dispenser, unless it is below 18" it would not be in a classified area even if the dispenser was pumping a flammable liquid.

Table 514.3(B)(1)[/QUOTE
None of it is classified. Diesel pump only. It would be in the boundary of the hazardous location. I guess another gray area. The e stop is only for circuits going through the dispenser.
Cl906um is offline   Reply With Quote
Old 04-30-2017, 09:22 AM   #14
Senior Member
 
Cl906um's Avatar
 
Join Date: Jul 2012
Location: Upper Michigan
Posts: 1,626
Rewards Points: 1,206
Default

It is in my opinion that 514 should not matter whatsoever once it becomes an unclassified location. I just wish the code book would clearly state this one way or another. It would save us the not knowing part. It's the dispensing motor fuels part that irritates me.kind of puts diesel into having to deal with some of 514. Not sure the ahj can clear it up in my head. We can argue all day.

Last edited by Cl906um; 04-30-2017 at 09:27 AM.
Cl906um is offline   Reply With Quote
Old 04-30-2017, 09:34 AM   #15
Senior Member
 
Cl906um's Avatar
 
Join Date: Jul 2012
Location: Upper Michigan
Posts: 1,626
Rewards Points: 1,206
Default

Quote:
Originally Posted by frenchelectrican View Post
Did ya ask the state inspector or fire inspector to see what they do cover on that code related to diesel fuel dispensing.,,

I try to read the 514 but are you on 11 or 14 cycle ?
No. I should, you are right. I asked the field manager the number for the inspector after I told him my side of the story, and he said he would call.
Cl906um is offline   Reply With Quote
Old 04-30-2017, 12:30 PM   #16
Modérateur
 
frenchelectrican's Avatar
 
Join Date: Mar 2007
Location: Philippines
Posts: 8,635
Rewards Points: 16,782
Default

Quote:
Originally Posted by Cl906um View Post
No. I should, you are right. I asked the field manager the number for the inspector after I told him my side of the story, and he said he would call.
Fair enough on that part and let us know what the results is..

I did check my local codes reguarding on diesel fuel dispending situation and they are muted on that part due it is classifed as low hazard class not like gasoline that will tighten the code a bit.

on diesel island only there is a bit of leeway on that part but if you have both gasoline and diesel the gasoline rules trumps it all.

( dont go there with dammed propane dispending units I went thru two of them this year )
__________________
Bleu est beau.
frenchelectrican is offline   Reply With Quote
Old 04-30-2017, 01:02 PM   #17
Senior Member
 
Join Date: Jan 2007
Location: Wilmington, NC
Posts: 12,167
Rewards Points: 14,714
Default

Quote:
Originally Posted by Cl906um View Post
It is in my opinion that 514 should not matter whatsoever once it becomes an unclassified location.
I do not understand why you think this. 514 is "Motor Fuel Dispensing Facilities". Wiring in a "classified" location is a subset of this article, not a pre-requirement to this article.

It sounds to me like you just don't want to comply with this article and no one will be able to convince you otherwise. It will be interesting to see what the AHJ says. I hope you share that with us.
__________________
Three vastly different enemies, but enemies who shared one common trait. ALL of them stifle free speech. All of them bully, degrade and terrorize those who hold opposing views and who peacefully express them. All of them are intolerant and demand “loyalty” to the leader. Michael Sand
hardworkingstiff is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Long term report, Millwaukee Fuel 99cents Tools, Equipment and New Products 56 03-11-2017 11:12 PM
Fuel 18 impact more compact then fuel 12 zac Tools, Equipment and New Products 3 08-17-2016 08:54 PM
E Stop For Fuel Pumps Walnuts240 General Electrical Discussion 11 06-24-2016 06:40 PM
Milwaukee M18 vs Fuel HAL9000 Tools, Equipment and New Products 25 05-28-2016 12:46 PM
Propane vs Diesel fuel for Generators katwalatapan Canadian Electrical Forum 21 02-20-2016 01:59 AM


All times are GMT -4. The time now is 03:51 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com