Is it legal to have 2 loads come out of the same transformer?
Or is there a sub panel required before branching out?
Both feeds are protected by fusable discos at the machinery.
It doesn't seem right to me but I don't have my code book with me.
Sent from my SM-J327T using Tapatalk
Electrozappo is offline   Reply With Quote
Old 01-20-2018, 01:47 PM   #2
Light Bender
eddy current's Avatar
Rewards Points: 8,168
I think it is rule #2 ? https://m.youtube.com/watch?v=JmA2WYyw-_A
Old 01-20-2018, 01:57 PM   #3
Rewards Points: 116
There are a lot of variables...but, I think 240.21(C) allows for it.
Transformer Secondary Conductors. A set of conductors feeding a single load, or each set of conductors feeding separate loads, shall be permitted to be connected to a transformer secondary, without overcurrent protection at the secondary, as specified in 240.21(C)(1) through (C)(6). The provisions of 240.4(B) shall not be permitted for transformer secondary conductors.
RunningSparky is offline   Reply With Quote
Old 01-20-2018, 02:05 PM   #4
Rewards Points: 27,026
Obey the Tap Rules -- and you're good to go.
Old 01-20-2018, 09:31 PM   #5
Rewards Points: 1,912
The transformer can power multiple loads, but you must follow tap rules - NEC 240.21. If the machine disconnects are within the permissible tap distances, you are good. If not, you would need to relocate them near the transformer or add redundant disconnects near the transformer.
frenchelectrican and splatz like this.
Old 01-20-2018, 09:37 PM   #6
Rewards Points: 21,898
It been done like that quite few time with TAP rules.
That is very important to remember it and please look up in NEC 240.21 and I think there is other spot I dont recall there is other one to follow up on that.
but just becarefull with tap rules first two part is most common for taps so please read it carefully on that.
If it dont meet the tap rules then you have no choice but put a OCPD disconnet switch after the transfomer ( yes you can have multi OCPD disconnect switch after the transfomer )
Old 01-21-2018, 12:31 PM   #7
Rewards Points: 2,149
Lot of our transformers for shows have multiple sets of camlock connections for this.
Or we just "T" cam adapters until we have what we need.
Old 01-21-2018, 10:23 PM   #8
Rewards Points: 48
This is awesome to read, and to understand tap rules which so many get wrong so often
Now the next challange: tell my side job foreman we did a wrong install.
Old 01-22-2018, 08:11 AM   #9
Rewards Points: 1,360
You treat the conductors coming from transformer terminals as if they were taps... because they are. So the conductors feeding from a transformer to a disconnect must be sized to at least 1/3 of the output capacity of the transformer.
Assuming you meet the minimum requirements of the tap rules and use a the proper lugs, yes, you can come out of a transformer multiple times.
Old 01-22-2018, 12:24 PM   #10
Licensed Journeyman
nolabama's Avatar
Rewards Points: 2,028
What he said.
Sent from my Pixel XL using Tapatalk
RePhase277 likes this.
Old 01-22-2018, 07:41 PM   #11
Arrow3030's Avatar
Rewards Points: 236
Great picture ^
nolabama likes this.
Arrow3030 is offline   Reply With Quote
Old 01-23-2018, 12:27 AM   #12
Originally Posted by nolabama View Post
What he said.
I assume based on the phase colors that your pic shows a 480Y/277 V output. If so, was there a reason that the neutral doesn't connect closer to the transformers, saving wire?
Old 01-23-2018, 04:52 AM   #13
Licensed Journeyman
nolabama's Avatar
Maybe this? I honestly don't know. I know they make them up on these busses
Old 01-23-2018, 04:52 AM   #14
Licensed Journeyman
nolabama's Avatar
I know that's a different install but they are similar in design.
Old 01-23-2018, 07:21 AM   #15
Rewards Points: 3,814
What he said.
BUT those could also be parallel feeds.
or utility transformers and secondaries.
Old 01-23-2018, 01:20 PM   #16
Licensed Journeyman
nolabama's Avatar
Pretty sure they are parallel feeds. I was just wanting to show the lugs and connection to the OP.