EVSE GFCI redux - 2017 nec TIA 625.54 - Electrician Talk - Professional Electrical Contractors Forum
Like Tree15Likes
Old 11-28-2019, 01:06 PM   #1
Rewards Points: 777
Default EVSE GFCI redux - 2017 nec TIA 625.54
My local inspector provided me with the attached TIA, going into effect around here in February/March 2020, which states:
625.54 Ground-Fault Circuit-Interrupter Protection for Personnel. All single-phase receptacles installed for the connection of electric vehicle charging that are rated 150 volts to ground or less, and 50 amperes or less shall have ground-fault circuit-interrupter protection for personnel. [emphasis added]
This applies to receptacles only, not to hard-wired installations.
The problem is that every brand of EV charger (EVSE) that I install, both hard-wired and plug-in models, has GFCI built in. Over a number of experiments so far, when plugged into a circuit protected by a (pricey) GFCI breaker, they do not function. They REQUIRE NO GFCI.
So now what???
TIA_70_17_2.pdf
mikewillnot is offline   Reply With Quote
Old 11-28-2019, 08:46 PM   #2
Rewards Points: 1,683
What if it's not for an electric vehicle? You are just installing an outlet for an RV or welder, right?
As for vehicle chargers not working with GFCI protection, I never knew that. Why don't they work? How do they know? What happens in commercial buildings with GFP mains? Sounds fishy.
Old 11-28-2019, 10:47 PM   #3
MTW
Rewards Points: 11,526
Only one month to go before this travesty is adopted in Massachusetts.
Old 11-29-2019, 12:04 AM   #4
Awg-Dawg's Avatar
Rewards Points: 726
That’s a poorly written requirement.
The way it reads, if you have a 125/250v receptacle, it would need protection.
If you had a 250v receptacle, you wouldn’t.
I feel sorry for people who don't drink, when they wake up in the morning, that's the best they will feel all day.
Awg-Dawg is offline   Reply With Quote
Old 11-29-2019, 06:45 AM   #5
CoolWill's Avatar
Rewards Points: 654
250 V is still "150 V to ground or less".
Service Call and splatz like this.
Old 11-29-2019, 08:46 AM   #6
Awg-Dawg's Avatar
Rewards Points: 726
The circuit voltage could be, but the voltage rating if the receptacle isn’t.
It says “receptacle” rating not circuit rating.
Old 11-29-2019, 09:03 AM   #7
Rewards Points: 2,484
Of course a receptacle has a voltage rating, but does a receptacle have a voltage-to-ground rating?
This too shall pass.
Old 11-29-2019, 09:05 AM   #8
Awg-Dawg's Avatar
Rewards Points: 726
The whole thing was terribly written, the next code cycle changes it to say circuit.
The Following User Says Thank You to Awg-Dawg For This Useful Post:
splatz (11-29-2019)
Old 11-29-2019, 09:15 AM   #9
As a receptacle rated 250V single phase, that means that it is rated under 150V to ground.
Old 11-29-2019, 09:33 AM   #10
Rewards Points: 792
I do not have the 2020 code yet but I believe it applies to all receptacles 50 amps or less and 150 volts to ground ( earth ). Ground, grounding, and grounded are sometimes interchanged. I like to use the term Earth and Neutral depending on the situation. Or White and Green depending on who I am talking with.
As I said before, we have to protect the general people from their own stupidity. We as electricians know what we can or should do when it comes to electric equipment. But the millennial who just bought his new TESLA has no idea of what electricity can do. I believe the " thing on the wall" is only a power port and the charger is part of the car. Things get abused by the user and could pose a danger down the road.
If you think about it, every industry is putting " safety measures" into their codes. We have AFCI & GFCI. Cars now have back up alarms and cameras, They are mandating CO and gas detectors. Houses need re-enforced hurricane strapping. Bicycle helmets. Red fire caulk when in most cases regular thermal caulk will do.
kb1jb1 is online now   Reply With Quote
Old 11-29-2019, 09:35 AM   #11
Rewards Points: 777
Most of the replies above are off topic, in a way. I'm concerned about the GFCI problem, and the requirement to put 2 in series, which usually doesn't work.
Old 11-29-2019, 09:39 AM   #12
My reply was right on topic.
Can you please explain how/why it doesn't work?
Old 11-29-2019, 10:05 AM   #13
Awg-Dawg's Avatar
Rewards Points: 726
A 480v receptacle would apply also then wouldn’t it?
Old 11-29-2019, 10:11 AM   #14
No, because that is 277V to ground.
micromind likes this.
Old 11-29-2019, 10:16 AM   #15
I don't see it that way.
For example, a NEMA 6-50R is RATED for 250V irrespective of the voltage to ground; the rating doesn't mention to 150V to ground. If it so happens that it's installed with 240V coming from the usual residential split phase supply, then 150V to ground. If it happens to be supplied by, say, the high leg of a high leg delta, and one of the other legs, with no neutral, then it is not operating at <150V to ground.
Old 11-29-2019, 10:23 AM   #16
Awg-Dawg's Avatar
Rewards Points: 726
How can a 250v receptacle be 150v or less and not a 480v?
They are both over 150v.
Old 11-29-2019, 10:25 AM   #17
And then it wouldn't need GFCI protection.
Old 11-29-2019, 10:27 AM   #18
A nominal 250v feed is 125V to ground, which is less than 150V.
A nominal 480V feed is 277V to ground, which is more than 150A.
Int he super odd situation that splatz mentioned, then it wouldn't apply and GFCI protection wouldn't be required.
Old 11-29-2019, 10:33 AM   #19
Awg-Dawg's Avatar
Rewards Points: 726
I understand what you’re saying, it’s just the wording doesn’t agree with it.
You’re saying circuit voltage , the wording is saying receptacle voltage.
Old 11-29-2019, 10:35 AM   #20
It's the same both ways.
Test that receptacle to ground and you will get less than 150v. The nominal voltage will also be less than 150V.