Feeders and Branch Circuits in the same Conduit. - Electrician Talk - Professional Electrical Contractors Forum
Like Tree1Likes
  • 1 Post By Navyguy
Old 02-17-2019, 11:48 AM   #1
Rewards Points: 20
Default Feeders and Branch Circuits in the same Conduit.
Is there an NEC article that requires Branch circuits and feeders to be in different conduits? Specifically I'm wondering about two panel tubs that are nipple together and do I need a separate nipple for the feeders and for the branch circuits
Dizzykidd is offline   Reply With Quote
Old 02-17-2019, 11:57 AM   #2
Rewards Points: 449
It's fine, just watch your derating.
Old 02-17-2019, 12:39 PM   #3
Rewards Points: 3,858
Can you use a panel as a raceway in the NEC? We are not allowed to up here. If we had two panels nippled together (not sure why we would even), you could not pass through one panel to get to the breakers on the other panel.
That is why you see things like this up here...
Cheers
John
Old 02-17-2019, 12:47 PM   #4
Rewards Points: 16,780
No useally not unless it is speced in the prints and just be aware of derating that will get ya if you are not aware of that.
That part is in NEC but for CEC it dont allowed for some reason ( unless someone in CEC side post the code number for it )
Old 02-17-2019, 01:11 PM   #5
Rewards Points: 449
Cheers
John
Yes, you can provided there is adequate space, which is very hard to fillup, so yes.
As for your picture, that wouldn't work well here. Because of derating requirements it doesn't make sense to put that many circuits into the same raceway.
If we needed circuits from 2 different panels to enter the same raceway, we would typically use a small trough to do it. But that is more of a commercial thing, no need in resi.
Navyguy (02-17-2019)
Old 02-17-2019, 01:31 PM   #6
MTW
MTW's Avatar
Rewards Points: 7,908
Unless you're Chicken Steve.
Old 02-17-2019, 01:32 PM   #7
MTW
MTW's Avatar
Cheers
John
Are those new FPE breakers?
Old 02-17-2019, 01:56 PM   #8
That is a new install circa +/-2006 I think. FPE panels have not been available since about 2009 or so in Canada. They are still, by far, the most popular residential panel in Ontario for anything that was installed prior to +/- 2009.
On almost every residential job I go to, there is a FPE panel installed. Breakers (except for the AFCI) are plenty available. If you install a new AFCI circuit you need to install a deadfront or AFCI receptacle since AFCI breakers are not available.
Cheers
John
MTW likes this.
Old 02-17-2019, 05:22 PM   #9
EJPHI's Avatar
Rewards Points: 338
For nipples of which <2' lengths of conduit are one type, you don't have much concern with derating like you do with raceway.
I think fill also gets relaxed a bit but I am not too sure being just an engineer.
Accessory Building Spark Master Residential Electrical Forum 14 09-17-2017 12:31 PM
Branch neutrals are all burnt on neutral bar dham206 General Electrical Discussion 26 07-21-2017 11:29 PM
UF cable cover requirements WronGun Residential Electrical Forum 76 07-21-2017 08:23 PM
Voltage drop on feeders especially the grounded conductor Arrow3030 NEC Code Forum 13 09-28-2016 06:54 AM
Multiple Voltages in the same conduit Aegis Canadian Electrical Forum 14 06-07-2016 05:21 PM