Multi Wire Branch Circuits - Electrician Talk - Professional Electrical Contractors Forum
Like Tree25Likes
Old 03-23-2020, 03:25 PM   #1
Easy's Avatar
Rewards Points: 1,282
Default Multi Wire Branch Circuits
Residential - multi wire branch circuit
Single phase 4 wire branch circuits that consist of 2 ungrounded conductors, 1 neutral and an EGC that feed two lighting circuits or 2 branch circuits for convince receptacles would require either a common trip breaker or 2 single pole breakers with a handle tie. 210.4(b)
Commercial - multi wire branch circuit
Is there any situation or code requirement that dictates the use of a common trip or “Handle Tie” to be used in commercial or industrial applications where 2 or 3 circuits are feed with a single neutral?
It’s obvious that you would shut off all 3 circuits associated with the neutral if you were working on a 3 phase multi wire branch circuit to avoid getting across the neutral but that’s common sense. I’m just conserved with how the NEC deals with it. So far I find no reference and have never seen it applied to 3 phase circuits that feed lights or plugs either 120v or 277v.
Easy is online now   Reply With Quote
Old 03-23-2020, 03:40 PM   #2
Rewards Points: 777
It applies to everything, resi and commercial, including 3 phase. You posted the article.
210.4(B) Disconnecting Means. Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.
MHElectric likes this.
Easy (03-23-2020)
Old 03-23-2020, 05:42 PM   #3
Rewards Points: 448
obvious to you but not ... .
farmantenna is offline   Reply With Quote
Old 03-23-2020, 06:37 PM   #4
Easy's Avatar
It seems quite clear when you read that but there must be more to this. In commercial and industrial applications I have never seen common trip or "handle ties" on any branch circuits that feed 120 volt plugs or lighting or 277v lighting circuits even on new installations. I guess no one is complying to the rules. 240.15 (B) (1) & (2) seems with confirm this.
Old 03-23-2020, 06:39 PM   #5
Rewards Points: 777
Originally Posted by Easy View Post
It seems quite clear when you read that but there must be more to this. In commercial and industrial applications I have never seen common trip or "handle ties" on any branch circuits that feed 120 volt plugs or lighting or 277v lighting circuits even on new installations. I guess no one is complying to the rules. 240.15 (B) (1) & (2) seems to confirm this. Scathing my head?
It is a relatively new change, I believe it was 2008. Maybe that’s why you don’t see the handle ties that often.
Old 03-23-2020, 06:57 PM   #6
Easy's Avatar
Yes this is probably why. I'm an old timer and need to keep up with the new rules. Anything that helps with safety is a good thing.
Old 03-23-2020, 07:11 PM   #7
Easy's Avatar
Here is a photo of a new panel interior that is being installed by an electrical contractor.
According to the print circuit 14,16 & 18 are designated to feed convenience outlets. I may have a hard time finding a handle tie for these breakers so it might be better to order a 3 pole 20. Thanks again for the help.
HackWork likes this.
Old 03-23-2020, 11:20 PM   #8
Rewards Points: 1,792
With LED lighting and high speed switching in electronic equipment MWBCs are almost a thing of the past.
tmessner likes this.
Old 03-23-2020, 11:48 PM   #9
MotoGP1199's Avatar
Rewards Points: 621
On the siemens P1 panels I have always used a 3 pole breaker. If those are NGB breakers this 3 pole handle tie should work https://www.cesco.com/Siemens-BQDHT3...-Pole/p1960700 but I have not used it before.
"The laws of physics will be strictly enforced."
MotoGP1199 is online now   Reply With Quote
Old 03-24-2020, 12:20 AM   #10
Rewards Points: 18,945
From a job I did some improvements on during December of last year.
I used a 3 phase load center to feed all the new circuits I installed. The top right hand side has 2 three pole breakers in there to handle two sets of cubicle furniture hookups.
If you start feeling the effects of a possible Corona infection, do not take Ibuprofen (ADVIL) to relieve pain, it increases the ability of the virus to replicate itself.
Old 03-24-2020, 07:08 AM   #11
CoolWill's Avatar
Rewards Points: 5,080
It was a stupid rule change and helped nothing. That's why the other electrical contractor ignored it.
Old 03-24-2020, 09:35 AM   #12
Easy's Avatar
Such a deal only $43.00 ....
Old 03-24-2020, 09:45 AM   #13
Easy's Avatar
Thanks for the help on this. Your makeup looks real nice in your panelboard. I could see some situations where a handle tie would be better than a common trip breaker. If you had to work on a lighting circuit just pull the handle tie, kill one breaker and then you would not have to go completely dark just to make a repair. Ha Ha... I wonder if they allow circuit breakers that are approved for switching, listed and marked SWD.
Old 03-24-2020, 11:36 AM   #14
My offspring did the panel. I taught him about looping feeders when he first came to work with me, around 6 years ago, and we were working on a real panel that had 350's that day. He volunteered to come help me while he was on a short layoff between projects at his union job. I think he thinks that on my panels I always want a loop. Those feeders are only #4's. I didn't have the heart to tell him not to do that again.............
Old 03-24-2020, 03:47 PM   #15
MotoGP1199's Avatar
Rewards Points: 621
Such a deal only $43.00 ....[IMG class=inlineimg]https://www.electriciantalk.com/images/smilies/vs_mad.gif[/IMG]
cheaper than a 3 pole breaker but absolutely ridiculous for a single handle tie.
Old 03-24-2020, 03:51 PM   #16
MTW
Rewards Points: 10,514
I still install MWBC's and I don't use multi-pole breakers on them.
Easy likes this.
Old 03-24-2020, 03:54 PM   #17
Rewards Points: 26,778
No one should be toying with 3-phase MWBC who is not trained for safety.
Dumming down our trade is not wise.
Handle ties can be created by a 3-D printer.
MTW and CoolWill like this.
Old 03-24-2020, 03:56 PM   #18
Rewards Points: 777
I use handle ties, less that I have to stock.
Old 03-24-2020, 03:59 PM   #19
MTW
I see.
Old 03-24-2020, 04:11 PM   #20
Rewards Points: 2,002
What do you do with a/c or 240 appliance circuits?
Kevin_Essiambre likes this.
I can't help it if I'm lucky