Default NMB in conduit
Today I was asked to fix a home inspection for a realtor. When I started looking at all that needed to be done, I realized that some things would pose an issue that was existing. One of the many was two #12-2 romex wires feeding a water heater and ac unit along with the feeder for the sub panel was sleeved in conduit to the main panel outside. Maybe this was allowed back in the day, but knowing that it is a violation, I would have to change for my inspection to pass. I decided to re feed the water heater from the sub panel and re run the ac circuit with THWN in flex to a disconnect to the AC. This would free up the 2" conduit for me to run my SER cable in by itself to the main panel. I ran through several ways of fixing this. Im curious what other would have done.
LLSee is offline   Reply With Quote
Old 11-15-2018, 06:25 AM   #2
Liberal Lesbian
Rewards Points: 374
What makes you think sleeving romex is a violation? And which article is it violating?
Old 11-15-2018, 07:30 AM   #3
Rewards Points: 14
@HackWork. Well I am going off Romex not being allowed in a wet location. Am I wrong in this? Believe me, I would love to leave it in there. Also having to derate the wires since there would be 6 current carrying conductors.
GroundFighter 78 likes this.
Old 11-15-2018, 07:34 AM   #4
Liberal Lesbian
Rewards Points: 374
You are correct about romex being prohibited in conduit outdoors.
The pipe is running outside? Or it goes into the back of a panel which is mounted facing outwards on an outside wall?
It's a sleeve, not a raceway. No derating.
Old 11-15-2018, 07:40 AM   #5
Rewards Points: 14
Thanks for the reply @HackWork The pipe is outside. Runs into the top of a main service panel.
Old 11-15-2018, 07:42 AM   #6
Liberal Lesbian
Rewards Points: 374
I see. Looks like you did what you had to. One other possibility would have been switching to UF cable for the part that is outdoors.
Old 11-15-2018, 07:59 AM   #7
Rewards Points: 3,029
What’s NMB?
Old 11-15-2018, 08:03 AM   #8
Liberal Lesbian
Rewards Points: 374
Whats NMB?
Romex.
NM-B = Non-Metallic type B.
Old 11-15-2018, 08:03 AM   #9
Rewards Points: 14
Good old autocorrect. Good catch @99cents
Old 11-15-2018, 10:15 AM   #10
Rewards Points: 20
The thing that caught my attention is #12 wire to the water heater. That should be #10.
Wiredindallas is offline   Reply With Quote
Old 11-15-2018, 10:18 AM   #11
Rewards Points: 14
@Wiredindallas Exactly. Whoever did this before had a 50 amp breaker on number 10 wire. They had all kinds of things going wrong
Old 11-15-2018, 10:43 AM   #12
Liberal Lesbian
Rewards Points: 374
Was the number 12 wire on a 30 amp breaker or 20 amp??
Was the number 10 wire on a 50 amp breaker powering an air-conditioner? That may be compliant.
Old 11-15-2018, 10:45 AM   #13
Rewards Points: 14
@hackeork The number 12 wire was on a 30 amp breaker feeding a water heater in the 50 amp breaker was on number 10 wire feeding a range.
Old 11-15-2018, 10:45 AM   #14
Liberal Lesbian
Rewards Points: 374
LOL, replaced it all! And charge a lot of money!
Old 11-15-2018, 10:47 AM   #15
Rewards Points: 14
That’s exactly what I’m doing Lol
HackWork likes this.
Old 11-22-2018, 12:27 PM   #16
360max's Avatar
Rewards Points: 1,234
....does the code differentiate between a conduit sleeve and a raceway, or is he still limited to the 24" in 310.15 (B)(2)?
Old 11-22-2018, 12:45 PM   #17
Rewards Points: 21,843
There is a technical violation in the wording of your post. I'm sure you ran liquid tight flexible conduit and not "Greenfield flex". So I bother with these type of things so that apprentices and a few New Yorker's won't read it and think " hey, it sounds like it's ok to use flex conduit outside from what I read at ET...."
I stand with Tucker Carlson
Old 11-24-2018, 11:58 PM   #18
360max's Avatar
Thanks for clearing that up mike, phewww
Old 12-02-2018, 09:22 AM   #19
mbednarik's Avatar
Rewards Points: 1,126
The interior of a conduit in the wet location also being a wet location did not come about until 2008 IIRC.
Old 12-02-2018, 09:24 AM   #20
mbednarik's Avatar
Romex beings limited to 60c ampacity does have 90c rated conductors and derates comes off the 90c column so he should be fine.
Suspending security camera from conduit ElectMe NEC Code Forum 8 02-19-2017 04:20 PM
Spa conduit emerging in the pad. Kaffeene General Electrical Discussion 4 12-10-2016 09:16 PM
PV conduit inside exterior wall permitted? katwalatapan Alternative Energy Forum 11 12-05-2016 12:09 PM
Getting the most from an existing U/G conduit Gaussios Residential Electrical Forum 16 04-25-2016 10:11 PM
locating conduit or LV cable behind wall or missing conduit end? lortech Structured Wiring 3 01-18-2016 12:35 PM