Outside 30 Amp Breaker 20 Amp Duplex Receptacle - Electrician Talk - Professional Electrical Contractors Forum
Like Tree15Likes
  • 1 Post By Dennis Alwon
  • 7 Post By Forge Boyz
  • 1 Post By HackWork
  • 2 Post By Forge Boyz
  • 3 Post By MTW
  • 1 Post By Jlarson
Old 06-04-2019, 02:10 PM   #1
AWW
AWW's Avatar
Rewards Points: 42
Unhappy Outside 30 Amp Breaker 20 Amp Duplex Receptacle
I'm a retired Industrial Electrician.
I was asked to check a non-working outside receptacle at my church that someone at the church installed about a month ago. The reason it wasn't working was because the neutral wire for the receptacle was landed on the neutral bus instead of the neutral-load-screw on the GFCI CB. And a neutral from a different outside receptacle WAS landed on the neutral-load-screw of the 30a GFCI CB. It apparently never worked as the GFCI CB will not turn on in this condition; it trips instantly. [Who wired this? ] I'm still trying to figure out how all that happened.
Now the reason I'm posting is this; I also found this circuit has a single 120 volt, 20 amp duplex-receptacle fed with 10 AWG protected by the 30 amp GFCI CB.
The intended loads are two cord and plug connected fan's for inflating those big jumpy-house / water-slide type outdoor attractions. I haven't received the information on the motor load's yet but...
I interpret Table 210-21(B)(3) to mean when you have receptacle fed by 10 AWG protected by a 30a CB the receptacle is supposed to rated at 30a. Meaning a 20a single or duplex receptacle is not allowed.
I believe the solution would require changing the receptacle to a 30a single outlet (which won't allow the fan's to plug in) or change the circuit breaker to a 20a GFCI and add another circuit for the second motor if needed. Again I don't know the exact load yet, I'm waiting on someone to send me a picture of the motor label and plug type.
Am I correct or is there something that allows this that I've missed?
AWW is offline   Reply With Quote
Old 06-04-2019, 02:49 PM   #2
Rewards Points: 1,162
You are correct. I would change the breaker to a 20 amp. If the receptacles that are outside already have gfci receptacles then no need for a 20 amp gfci breaker just a 20 amp breaker.
micromind likes this.
I can't help it if I'm lucky
Old 06-04-2019, 06:32 PM   #3
AWW
AWW's Avatar
Rewards Points: 42
Thank you Dennis! Since my first post I learned that the fan's are 12a each so I will changed the breaker to a 20a and run another 20a circuit because we have two fan's that need to run at the same time (12a each).
Old 06-04-2019, 06:38 PM   #4
Rewards Points: 427
This is where we were hoping you would go on to say that you referred them to a licensed, insured, and legitimate electrical contractor.
Old 06-04-2019, 06:58 PM   #5
Rewards Points: 46
So you are saying that once you retire you lose all your knowledge? Can't a guy volunteer at his church? He correctly identified the problem, he just came here to make sure he was on the right track. It's not Harry homeowner who doesn't have a clue.
Sent from my XT1650 using Tapatalk
Old 06-04-2019, 07:16 PM   #6
Rewards Points: 427
What does knowledge have to do with my statement?
No, he can't when it comes to this. And he shouldn't be.
The only reason why the church has this problem in the first place is because they spent too much money on stone work and golden chalices, and nothing on electrical work when they brought in the last unlicensed, uninsured, and illegitimate electrician.
It's funny that when I say I break the most mundane and insignificant code everyone is all by-the-book with me. But when I suggest that the electrical work performed on a place of public accommodation of possibly hundreds of people should done by a legitimate contractor with a license and insurance I am now wrong.
CTshockhazard likes this.
Old 06-04-2019, 07:56 PM   #7
Rewards Points: 46
Knowledge has to do with the fact that he is qualified and capable to do the job correctly. To me that is the biggest issue. He's been in the field for years. How is this any different than an EC's employee who doesn't have his master's showing up to work on it? He knew what to do, it's just not an area he worked with much in his job. How is this different from lots of the rest of us that get outside of our usual work and come here to ask questions?
For every Joel Osteen type mega church that are simply moneymaking schemes, there are a hundred small community churches operating on a shoestring budget. Whether or not you believe they are right, they still do a lot of good in their community. Of course they are glad for volunteer help. Why not use your skills for your church? There are lots of other nonreligious places that use volunteer help. Should all eletricians refuse to do charity work for them?
micromind and MTW like this.
Old 06-04-2019, 08:06 PM   #8
MTW
MTW's Avatar
Rewards Points: 7,908
A license is a permission slip from the government that allows you to make your living. It says nothing about ones abilities or qualifications.
micromind, AWW and 460 Delta like this.
Old 06-05-2019, 07:36 AM   #9
Sentimental Mental
CTshockhazard's Avatar
Rewards Points: 1,400
Well, maybe churches on a shoestring budget should'nt be concerned with providing cord and plug connected fan's for inflating those big jumpy-house / water-slide type outdoor attractions.
Just to be absolutely clear...
I didn't say anything about nothing to noone.
Old 06-07-2019, 08:07 PM   #10
Jlarson's Avatar
Rewards Points: 3,968
Hey man, Jesus was a huge fan of bounce houses.
Tags
30 amp branch circuit, gfci., individual receptacle